50amp to 30amp adapter failure

Click image for larger version

Name:	ImageUploadedByiRV2 - RV Forum1469400620.052436.jpg
Views:	286
Size:	92.8 KB
ID:	134061

Anybody had a problem like this? Awoke to electricity failing and found the adapter about to catch fire. All problems were at the 30amp end of the adapter. I guess it just overheated. Had rain earlier in the day. Don't know if that contributed. I had a load (25amps) on it over 2 days.
__________________
Craig & Rayann - 2002 Winnebago Journey 32T - 2016 Jeep Wrangler Unlimited TOAD - Florence, MS
Rcdukes is offline   Reply With Quote
Old 07-24-2016, 05:05 PM   #2
Winnebago Owner
 
palehorse89's Avatar
 
Join Date: Oct 2009
Posts: 86
You were right up near max amps. for days........Max amps= heat, and over a couple of days.....melt down........
I am sure there are better quality adapters that would take the amp draw better than the ones that you had fail.......buy a good/heavy dog bone adapter........not saying the one you had was junk or cheap........but it failed.
Focus on the wire size on the new ones.......
__________________
2000 Newmar MADP 4060, 350ISC, Spartan MM, IFS 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006Ultra & 1989 Springer
palehorse89 is offline   Reply With Quote
Old 07-24-2016, 05:46 PM   #3
Winnebago Camper
 
Join Date: Aug 2015
Location: Western Colorado
Posts: 28
I have seen that exact same thing twice in the last year. I worked as an electrician for many years and the adapters are rated well above 30 amps. The problem most likely occurred from arcing as a result of a loose fit. The plug blades MUST fit tight. If the plug was lying on the ground during the rain, shorting at the connection is quite possible. As palehorse stated, a quality adapter is essential. The plug blades MUST fit tight.

What makes this situation so dangerous is that arcing DOES NOT normally trip the breaker as you are still below the rated current draw. A fire can be in full force and the breaker remains hot!! Hope this helps.
mtnmike is offline   Reply With Quote
Old 07-24-2016, 05:55 PM   #4
Winnebago Camper
 
Join Date: Jan 2009
Posts: 38
I'd bet it was the campground receptacle. We've seen 30 amp receptacles that were old, lose fitting, melted, and/or actually burnt. No way i'd try plugging into these. We've encountered this a few times and so far, have always had good luck getting park personnel to change the bad ones out.

Edited: Reread your post and see that what i wrote above wasn't the cause of your failure.

But while i'm here, what is that 2nd black cord on the right? Looks like two cords coming together before the plug.
__________________
03 Itasca Sunova, 8.1 Workhorse on a P32 chassis
Mudfrog is offline   Reply With Quote
Old 07-24-2016, 06:00 PM   #5
Winnebago Owner
 
palehorse89's Avatar
 
Join Date: Oct 2009
Posts: 86
Once a year, I polish my connections with emery cloth till shinny.......tweak the tabs till the plug in is tight........spray with a good electrical spray,not in excess, and also, go over the transfer switch's contacts.......
__________________
2000 Newmar MADP 4060, 350ISC, Spartan MM, IFS 2011 Jeep JK, M&G Braking, 2014 MTI 27' Hog Hauler, Wireless brake control, 2006Ultra & 1989 Springer
palehorse89 is offline   Reply With Quote
Old 07-24-2016, 06:01 PM   #6
Winnebago Camper
 
Rcdukes's Avatar
 
Join Date: Mar 2014
Location: Florence, MS
Posts: 18
Quote:
Originally Posted by mtnmike View Post
I have seen that exact same thing twice in the last year. I worked as an electrician for many years and the adapters are rated well above 30 amps. The problem most likely occurred from arcing as a result of a loose fit. The plug blades MUST fit tight. If the plug was lying on the ground during the rain, shorting at the connection is quite possible. As palehorse stated, a quality adapter is essential. The plug blades MUST fit tight.

What makes this situation so dangerous is that arcing DOES NOT normally trip the breaker as you are still below the rated current draw. A fire can be in full force and the breaker remains hot!! Hope this helps.

Mtnmike, you are correct. The breaker was still hot when I found it but the connection had already been severed by the melting/fire. I will monitor more closely when in high load situations. Thanks.


Sent from my iPad using iRV2 - RV Forum
__________________
Craig & Rayann - 2002 Winnebago Journey 32T - 2016 Jeep Wrangler Unlimited TOAD - Florence, MS
Rcdukes is offline   Reply With Quote
Old 07-24-2016, 06:17 PM   #7
Winnebago Camper
 
dons2346's Avatar
 
Join Date: Dec 2010
Posts: 15
That's nasty. In looking at this, I would say that the campground has lousy maintenance when it comes to their electrical boxes.
__________________
Don
2002 Country Coach Intrigue
dons2346 is offline   Reply With Quote
Old 07-24-2016, 06:30 PM   #8
Winnebago Camper
 
Rcdukes's Avatar
 
Join Date: Mar 2014
Location: Florence, MS
Posts: 18
Quote:
Originally Posted by dons2346 View Post
That's nasty. In looking at this, I would say that the campground has lousy maintenance when it comes to their electrical boxes.

Well, It was not a campground. It was at my farm. The problem occurred not at the receptacle but at the adapter to extension cord that then ran to the receptacle. Mid-span. I had the 30amp receptacle installed back when I had a travel trailer. I will be installing a 50amp soon.


Sent from my iPad using iRV2 - RV Forum
__________________
Craig & Rayann - 2002 Winnebago Journey 32T - 2016 Jeep Wrangler Unlimited TOAD - Florence, MS
Rcdukes is offline   Reply With Quote
Old 07-24-2016, 06:38 PM   #9
Winnebago Camper
 
DrDaveMA's Avatar
 
Join Date: Jun 2007
Location: Cotuit, MA
Posts: 21
You have to watch the length of the run from the panel. 30 amp, you need at least #8 for a run up to 200', beyond that go to #6. You also have to add in the cord to your RV. Be sure ALL the connections are tight and waterproof.
__________________
Dave, Bobbi and Fenway
2005 38' FDTS Alpine Limited, 2016 Jeep Grand Cherokee Limited
Cape Cod, MA
DrDaveMA is offline   Reply With Quote
Old 07-24-2016, 09:56 PM   #10
Winnie-Wise
 
SuperGewl's Avatar
 
Join Date: Aug 2004
Location: Oregon
Posts: 477
Sorry to hear that happen. The fix for this is to apply some Dielectric grease to the prongs and at every connection wrap it in a plastic bag to keep out the moisture. You will be amazed at how little moisture it takes to cause problems at the connections.
Basically what happened is that yours shorted out.
__________________
Retired Navy Submariner
2014 Itasca Sunstar 35F; 5 Star tuned; 2014 Jeep Cherokee TrailHawk
SuperGewl is offline   Reply With Quote
Old 07-25-2016, 07:35 AM   #11
Winnebago Master
 
Join Date: Nov 2005
Posts: 1,080
Quote:
Originally Posted by dons2346 View Post
That's nasty. In looking at this, I would say that the campground has lousy maintenance when it comes to their electrical boxes.
If you look at the picture closely you'll see the damage is between the 30/50 amp adaptor connector and the OP's cord. There is no damage at the plug end of the adaptor. This failure has nothing to do with the campground or it's maintenance. It's strictly a function of the OP's equipment.
__________________
Hikerdogs
2013 Adventurer 32H
Hikerdogs is offline   Reply With Quote
Old 07-25-2016, 07:54 AM   #12
Winnebago Camper
 
DrDaveMA's Avatar
 
Join Date: Jun 2007
Location: Cotuit, MA
Posts: 21
And there is something unusual going on with the cord on the right, is that a 30/20 to 50 amp adaptor? Also the rain the OP mentioned contributed to the problem.
__________________
Dave, Bobbi and Fenway
2005 38' FDTS Alpine Limited, 2016 Jeep Grand Cherokee Limited
Cape Cod, MA
DrDaveMA is offline   Reply With Quote
Reply

Tags
ada


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Surge Guard 50amp where is the Key? boyland Electrical | Charging, Solar and Electronics 10 07-07-2017 04:38 PM
Turning off House Batteries kills 50amp!?! RickO Electrical | Charging, Solar and Electronics 36 08-23-2010 01:05 PM
30amp or 50amp?? Greybeard Electrical | Charging, Solar and Electronics 12 07-15-2008 08:57 AM
Coiled 50amp electric cable whyoder Electrical | Charging, Solar and Electronics 12 06-26-2008 09:20 AM
Trailer plug adapter Doug Sage Winnebago Travel Trailers 14 10-11-2006 08:41 AM

» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 01:01 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.