I have an '01 National RV with an Atwood furnace problem. Fan comes on, I can hear the click of the igniter, and I can smell a small amount of propane at the exhaust. Clicks about every 15 to 20 seconds. Just no flame. Pulled the unit out, and with no propane going to it, I could see the spark. The spark looked weak to me, but I have nothing to judge that by. I checked the gas pressure by lighting all three burners on the stove and that looked good. The problem started after I set up and used the furnace a couple of mornings, then switched over to a portable tank, then flew back east for a few days. Margaret called and said the furnace didn't work. Luckely, it warmed up in Tucson and was out of heat only one morning when it was needed.

Any suggestions, comments, or leading questions?
Thanks for any help.

Harold

__________________
Once a full timer and miss the road.

'01 Nat'l RV, Tropical 33' Ford V10
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-11-2007, 02:12 PM   #2
H. Dossett is offline
Member
Join Date: Mar 2007
Location: AZ
Posts: 36
I have an '01 National RV with an Atwood furnace problem. Fan comes on, I can hear the click of the igniter, and I can smell a small amount of propane at the exhaust. Clicks about every 15 to 20 seconds. Just no flame. Pulled the unit out, and with no propane going to it, I could see the spark. The spark looked weak to me, but I have nothing to judge that by. I checked the gas pressure by lighting all three burners on the stove and that looked good. The problem started after I set up and used the furnace a couple of mornings, then switched over to a portable tank, then flew back east for a few days. Margaret called and said the furnace didn't work. Luckely, it warmed up in Tucson and was out of heat only one morning when it was needed.

Any suggestions, comments, or leading questions?
Thanks for any help.

Harold

__________________
Once a full timer and miss the road.

'01 Nat'l RV, Tropical 33' Ford V10
  Reply With Quote
   
Old 03-11-2007, 03:45 PM   #3
"007" is offline
Community Moderator
"007"'s Avatar


Nor'easters Club
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,593
H. Dossett welcome to irv2
When you switched over to the portable the line to the furnace may have air in it and needs to be cleared. Stove may work but line to furnace still has air in it.
If you keep trying to light it it may clear after a few trys.
Enjoy the forums and post often.
__________________
98KS,99MA,03-KS-3740 W-22 & 6 Ford's 3 V-10's
VISIT the NEWMAR QUICK TIPS & EASYMODS1&2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS
  Reply With Quote
   
Old 03-11-2007, 11:32 PM   #4
RV Wizard is offline
Community Moderator
RV Wizard's Avatar


Gulf Streamers Club
Country Coach Owners Club
Appalachian Campers
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 8,235
Harold, welcome to iarv2.com. We are glad to have you join us here. Have you gotten the furnace retarted? You may want to try it off the main tank and if it works from there check the fittings and valve on the portable tank feeding the system. GOod luck and keep us posted.
__________________

Mike, Certified Master RV Technician
Amy, RV Merchandiser; Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser w/ Banks & 2 toads
  Reply With Quote
   
Old 03-12-2007, 07:02 AM   #5
H. Dossett is offline
Member
Join Date: Mar 2007
Location: AZ
Posts: 36
A little more info:

The furnace worked for two or three days after I switched to the portable tank.

I have ordered the RV Repair and maintenance manual. After 5 years on the road, I need it more and more!

What should the Electrode to ground gap be. It did not look fouled up or anything and the burner looks clean enough. The gap is about 3/16".

What are the chances of the control board being bad with the symtoms listed?
__________________
Once a full timer and miss the road.

'01 Nat'l RV, Tropical 33' Ford V10
  Reply With Quote
   
Old 03-12-2007, 07:44 AM   #6
RV Wizard is offline
Community Moderator
RV Wizard's Avatar


Gulf Streamers Club
Country Coach Owners Club
Appalachian Campers
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 8,235
The gap is right at 3/16". One thing you will want to be sure to check is that the burner is clean and especially at where the electrode is. Also check to be sure the gas fuel pressure is 11" water colum. Be sure the blower wheels and vents are clean and no pest have built a nest in them. If you have a volt meter or 12 test probe be sure you are getting good 12 (13 volt) at the gas valve and control board. The gas valve will only be opened for a short time while the igniter starts sparking. Let us know what you find.
__________________

Mike, Certified Master RV Technician
Amy, RV Merchandiser; Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser w/ Banks & 2 toads
  Reply With Quote
   
Old 03-13-2007, 01:44 AM   #7
H. Dossett is offline
Member
Join Date: Mar 2007
Location: AZ
Posts: 36
Hi again.

Another update on the furnace.

Pulled out the control board this morning and dusted it off with a small paint brush. (had to act like I was doing something useful.) Put it back in and turned it on and lo and behold, it fired up. Fast and loud, 'bout had a heart attack, standing next to it with the cover off. Ran the thermostat down and it turned off just like it should. Could not get it to relight after that.

Any suggestions?

Harold
__________________
Once a full timer and miss the road.

'01 Nat'l RV, Tropical 33' Ford V10
  Reply With Quote
   
Old 03-13-2007, 10:32 PM   #8
RV Wizard is offline
Community Moderator
RV Wizard's Avatar


Gulf Streamers Club
Country Coach Owners Club
Appalachian Campers
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 8,235
Harold, Do you have and know how to use a multimeter? The unit needs to be properly diagnosed as we can only guess and offer things to check. According to Dinasour, 80% of board problems were loose conections. Have you checked the gas pressure with a monometer? I would start there just to be sure it is right; if so then make sure the igniter is sparking and at the same time the gas valve opens after the unit has gone through about a 7 second purge period. Good luck and let us know what you find by continuing this topic on the RV Syatems and Appliance section down the main page of the forum.

__________________

Mike, Certified Master RV Technician
Amy, RV Merchandiser; Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser w/ Banks & 2 toads
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Atwood furnace Max Hubrich RV Systems & Appliances 1 02-14-2009 12:48 AM
Atwood Furnace Scubadave 5th Wheel Discussion 3 12-14-2007 11:15 AM
Atwood furnace H. Dossett RV Systems & Appliances 4 03-31-2007 10:29 AM
Atwood furnace New Member Check-In 4 12-31-1969 06:00 PM
Atwood furnace New Member Check-In 7 12-31-1969 06:00 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 02:04 AM.