Question: I have a 30 AMP 2006 Itasca Suncruiser 35U and we have a trip coming up next month to South East/Fl. Friends have offered us a nearby parking connection to their garage 15 AMP standard wall AMP. Will my EMS power panel recognize it as the 20 AMP source and will it run A/C compressor #1 (11-12 Amp) if all other appliances etc are on gas? Any thoughts/past experience here?
__________________
Pubtym
20th SOS "Green Hornet" , Viet Nam 68-69
MACVSOG
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
07-16-2007, 04:05 AM
|
#2
|
|
Senior Member
Workhorse Chassis Owner Winnebago Owners Club
Join Date: May 2006
Location: Brandon, SD
Posts: 722
|
Question: I have a 30 AMP 2006 Itasca Suncruiser 35U and we have a trip coming up next month to South East/Fl. Friends have offered us a nearby parking connection to their garage 15 AMP standard wall AMP. Will my EMS power panel recognize it as the 20 AMP source and will it run A/C compressor #1 (11-12 Amp) if all other appliances etc are on gas? Any thoughts/past experience here?
__________________
Pubtym
20th SOS "Green Hornet" , Viet Nam 68-69
MACVSOG
|
|
|
|
| |
|
07-16-2007, 04:18 AM
|
#3
|
|
Senior Member
Join Date: Nov 2002
Location: Crossville, TN USA
Posts: 909
|
When you plug in. You will have to change the EMS setting to the 20 AMP manualy. There is a switch on the EMS. It will show what you can run with 20 AMP.
__________________
Tom & Bonnie
2008 Winnebago Aspect 29H
A Class C Not a B+
|
|
|
|
| |
|
07-16-2007, 04:45 AM
|
#4
|
|
Senior Member
Join Date: Jan 2005
Location: Back at the ranch
Posts: 2,540
|
Like Tom says, the EMS has to be manually set for 20 amp service. For only 15 amp service, have a voltage tester or some way of keeping an eye on the AC voltage and reduce the load when you drop below say about 110 volts (assuming the 15 amp service breaker doesn't trip first.) Your EMS assumes you will have 20 amp service so you will need to be actively involved in monitoring the situation.
Not sure if you will be able to run the AC on 15 amp service - maybe depending on the voltage drop. We have experience with 20 amp service, but not 15.
__________________
--John
2005 Horizon 40AD, 2005 Jeep Liberty CRD
|
|
|
|
| |
|
07-16-2007, 05:07 AM
|
#5
|
|
Moderator Emeritus
Vintage RV Owners Club Texas Boomers Club Oklahoma Boomers Club Ford Super Duty Owner
Join Date: Aug 2000
Location: Cypress, TX
Posts: 11,964
|
You might make it on 1 A/C compressor on 15 amps and you might not.
Run the frig on propane, not electric, the water heater on propane and you might have to disconnect your power converter.
If the power out of the garage, it may be 20 amps instead of 15 amps.
Your friends offer might cause problems with the home owners association....better have him check into that issue.
Ken
__________________
Amateur Radio Operator|Practicing for our retirement! 2008 Cameo 35SB3 - 2002 7.3L Crew Cab Dually w/ a SCMT - Max Brake - Travel with one Miniature Schnauzer, one Standard Schnauzer and one small Timneh African Gray Parrot
|
|
|
|
| |
|
07-16-2007, 05:11 AM
|
#6
|
|
Senior Member
Join Date: Mar 2007
Location: CAPE CORAL FL
Posts: 116
|
see if the house your staying at has a washer and dryer close by i use my dryer plug when i bring bus home to load its 30amps works both airs at same time..............warning temps done here are high 90s and humid......hurricanes are coming otherwise we live in paradise.....................
__________________
07 GS Tourmaster T40b Merc 330 Allison 6 speed 04 4RNR V8 Toad Yamaha 250 Hanging on the back
|
|
|
|
| |
|
07-16-2007, 05:21 AM
|
#7
|
|
Senior Member
Workhorse Chassis Owner Winnebago Owners Club
Join Date: May 2006
Location: Brandon, SD
Posts: 722
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by John_Canfield:
Like Tom says, the EMS has to be manually set for 20 amp service. For only 15 amp service, have a voltage tester or some way of keeping an eye on the AC voltage and reduce the load when you drop below say about 110 volts (assuming the 15 amp service breaker doesn't trip first.) Your EMS assumes you will have 20 amp service so you will need to be actively involved in monitoring the situation.
Not sure if you will be able to run the AC on 15 amp service - maybe depending on the voltage drop. We have experience with 20 amp service, but not 15. </div></BLOCKQUOTE>
I use surge protector with auto disconnect for low voltage/feqs.
__________________
Pubtym
20th SOS "Green Hornet" , Viet Nam 68-69
MACVSOG
|
|
|
|
| |
|
07-16-2007, 05:24 AM
|
#8
|
|
Senior Member
Workhorse Chassis Owner Winnebago Owners Club
Join Date: May 2006
Location: Brandon, SD
Posts: 722
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by 03 CORVETTE:
see if the house your staying at has a washer and dryer close by i use my dryer plug when i bring bus home to load its 30amps works both airs at same time..............warning temps done here are high 90s and humid......hurricanes are coming otherwise we live in paradise..................... </div></BLOCKQUOTE>
I can't mentally picture connection from my RV 30 amp plug to dryer connect. Assist please with link to picture/part for connect.
__________________
Pubtym
20th SOS "Green Hornet" , Viet Nam 68-69
MACVSOG
|
|
|
|
| |
|
07-16-2007, 05:27 AM
|
#9
|
|
Senior Member
Workhorse Chassis Owner Winnebago Owners Club
Join Date: May 2006
Location: Brandon, SD
Posts: 722
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Ed/Full-time:
Like rvten said you have to select it manually, but I don't think a 20 amp service will be enough to run/start even one compressor. If I remember I tried it a while ago and the startup surge is to much for the 15/20 amp service to handle. Even if it gets up and running the house wiring might not be able to handle the heat...generated by the demand.
I don't know if you noticed but even plugged into a 30 amp and the AC on max the draw is sometimes to much and the plug gets very hot at times. If I had to do it again I would change the 30 to a 50 amp service in our coach. More times then not I use the 50 to 30 adapter works better and doesn't over-heat the breaker in some RV Parks...
Good luck! </div></BLOCKQUOTE>
How about start A/C on genset...plug in to 15-20 amp...shutdown genset when compressors stabilize and expect # 2 to drop off as EMS moves to 20? Run on compressor #1.
__________________
Pubtym
20th SOS "Green Hornet" , Viet Nam 68-69
MACVSOG
|
|
|
|
| |
|
07-16-2007, 05:30 AM
|
#10
|
|
Senior Member
Workhorse Chassis Owner Winnebago Owners Club
Join Date: May 2006
Location: Brandon, SD
Posts: 722
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by TXiceman:
You might make it on 1 A/C compressor on 15 amps and you might not.
Run the frig on propane, not electric, the water heater on propane and you might have to disconnect your power converter.
If the power out of the garage, it may be 20 amps instead of 15 amps.
Your friends offer might cause problems with the home owners association....better have him check into that issue.
Ken </div></BLOCKQUOTE>
Good point about homeowners assc. It'll only be for one night...but???
__________________
Pubtym
20th SOS "Green Hornet" , Viet Nam 68-69
MACVSOG
|
|
|
|
| |
|
07-16-2007, 05:41 AM
|
#11
|
|
Senior Member
Join Date: Mar 2007
Location: CAPE CORAL FL
Posts: 116
|
[/QUOTE]
I can't mentally picture connection from my RV 30 amp plug to dryer connect. Assist please with link to picture/part for connect.[/QUOTE]if dryer connection is a 30amp three prong connection.......if you come out of rv with 50 amp plug use a 50/30 amp knockdown..........works just like at a campground...also in my town i have to get a permit to park in driveway even for overnite
__________________
07 GS Tourmaster T40b Merc 330 Allison 6 speed 04 4RNR V8 Toad Yamaha 250 Hanging on the back
|
|
|
|
| |
|
07-16-2007, 06:08 AM
|
#12
|
|
Senior Member
Workhorse Chassis Owner Winnebago Owners Club
Join Date: May 2006
Location: Brandon, SD
Posts: 722
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by 03 CORVETTE:
</div></BLOCKQUOTE>
I can't mentally picture connection from my RV 30 amp plug to dryer connect. Assist please with link to picture/part for connect.[/QUOTE]if dryer connection is a 30amp three prong connection.......if you come out of rv with 50 amp plug use a 50/30 amp knockdown..........works just like at a campground...also in my town i have to get a permit to park in driveway even for overnite[/QUOTE]I have 30 amp hardwire plug. Gotta reach the dryer plugin....I have 15-20 amp extension 50ft wire and 50 male to 30 female knockdowm..also 30 to 15 knockdown...
__________________
Pubtym
20th SOS "Green Hornet" , Viet Nam 68-69
MACVSOG
|
|
|
|
| |
|
07-16-2007, 06:43 AM
|
#13
|
|
Senior Member
Join Date: Mar 2007
Location: CAPE CORAL FL
Posts: 116
|
go get a 50 foot 30 amp from camping world and make sure the dryer plug at the house is same terminals...............
__________________
07 GS Tourmaster T40b Merc 330 Allison 6 speed 04 4RNR V8 Toad Yamaha 250 Hanging on the back
|
|
|
|
| |
|
07-16-2007, 07:00 AM
|
#14
|
|
Senior Member
Join Date: Jan 2005
Location: Back at the ranch
Posts: 2,540
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Pubtym:
--snip--
I use surge protector with auto disconnect for low voltage/feqs. </div></BLOCKQUOTE>So do I but mine will cut out on low voltage that is much lower (~102V) than I like to run. I start my power management procedure when I see the voltage sag to ~109 volts. I have encountered many marginal power situations in Canada, Alaska and state parks and never has my SurgeGuard cut out on low voltage. Running anything with an inductive load (like the AC fan & compressor) for extended periods with low voltage is very deleterious to the load.
We were even in a park outside of Denali National Park where the campground power was supplied by a large generator on the property. The voltage and line frequency was all over the place but never dramatic enough to trip the SurgeGuard. Ergo, I always keep an eye on the power at an unfamiliar campground.
__________________
--John
2005 Horizon 40AD, 2005 Jeep Liberty CRD
|
|
|
|
| |
|
 |
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|