On any A/C system if the evaporator blower fails to come on, the refrigerant pressure will drop to the point where it will trip the low pressure safety preventing the evaporator from freezing and the protecting the compressor as well. Depending on the unit, that safety may automatically reset itself once the pressure begins to naturally rise during the 'off' time at which point the system will try and start again. If this process of autostart doesn't happen, then the system is further protected by a lock out relay where once the low pressure switch is activated, it uses that relay to prevent another attempted auto start. The relay can be manually reset by waiting for the pressure to naturally rise during the off cycle, then cycle the systems power off then on (that resets the relay) and try to start the system again. The long and the short of it is that the system is protecting itself because the furnace blower does not work. In the A/C mode that blower is enabled from a fan relay somewhere in the system. I suspect the relay is bad, but here's how you can check. With the A/C and heat off, turn on your blower only if you have that setting available at the thermostat. If no blower, the relay is bad. In the heat mode, the furnace does not use that relay and instead uses a blower fan switch that's enabled by heating time or temperature. However, if THAT does not bring in the blower, then the blower motor itself may be the culprit.
Dan