Basement Air in 2003 Journey
Old 06-30-2010, 01:48 PM   #1
GA Cajun is offline
Member
GA Cajun's Avatar
Winnebago Owners Club
Join Date: Jun 2008
Location: Statesboro, GA
Posts: 79
Hi everyone,

I hope you guys can answer my question about my basement A/C. I've looked at some other posts, and I think I know the answer, but I want to be sure before I bring the MH in.

I had a problem with the A/C. The start relays and capacitors were fried and that fried the circuit board. I think it was low voltage at some point a few weeks back. Anyway, I got the A/C fixed and was running it on the genset yesterday. The power manager readout was showing 32 amps and the genset was running hard. Does that sound right? I think I read that it may be a capacitor problem. Does that sound right, too?

Thanks for any help you can offer.

Cajun

__________________
2002 Winnebago Journey DL 39QD
2003 Acura 3.2TL Type S & 2005 Honda Odyssey EX-L
Better half, 2 sons-13 & 11
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-30-2010, 02:28 PM   #2
smlranger is offline
Moderator Emeritus
smlranger's Avatar


Winnebago Owners Club
Freightliner Owners Club
Join Date: Sep 2004
Location: Smith Mountain Lake, Virginia
Posts: 3,440
Blog Entries: 1
Mine pulls about 26 amps on the genset with both compressors running, if that is helpful.

__________________
'02 Journey DL, 36GD, 330 CAT. '08 Explorer Toad, Blue Ox Aventa II, Air Force One Toad Brake.
Smith Mountain Lake, VA
  Reply With Quote
   
Old 06-30-2010, 02:51 PM   #3
GA Cajun is offline
Member
GA Cajun's Avatar
Winnebago Owners Club
Join Date: Jun 2008
Location: Statesboro, GA
Posts: 79
That does help a bit. If I remember correctly, mine pulled between 20 and 25 amps (can't remember exactly) before the repairs, too, but I don't remember the genset running that fast before. I'll probably bring it back in when I get a chance.
__________________
2002 Winnebago Journey DL 39QD
2003 Acura 3.2TL Type S & 2005 Honda Odyssey EX-L
Better half, 2 sons-13 & 11
  Reply With Quote
   
Old 06-30-2010, 04:54 PM   #4
Fossilhog is offline
Senior Member
Fossilhog's Avatar
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 329
Send a message via AIM to Fossilhog
Quote:
Originally Posted by GA Cajun View Post
That does help a bit. If I remember correctly, mine pulled between 20 and 25 amps (can't remember exactly) before the repairs, too, but I don't remember the genset running that fast before. I'll probably bring it back in when I get a chance.
On my 02 Adventurer, the 20 amp breaker on the generator is dedicated to the #2 compressor so on generator power I only read 17 amps at the EMS panel even with both compressors engaged. I'm surprised that you're getting that reading and not shedding power. On shore power with just the A/C and TV on I'm readiing 28-29. I put the fridge on propane. Burned out to many circuit boards and stuff....
__________________
Tim ,Retired Police Lt.
2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+ Border Collie,Trik-L-start,Hughes Autoformer
  Reply With Quote
   
Old 06-30-2010, 07:01 PM   #5
KIX is offline
KIX
Senior Member
KIX's Avatar


Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 1,639
Quote:
Originally Posted by GA Cajun View Post
Anyway, I got the A/C fixed and was running it on the genset yesterday. The power manager readout was showing 32 amps and the genset was running hard. Does that sound right? I think I read that it may be a capacitor problem. Does that sound right, too?Cajun
Cajun, Are you certain EVERYTHING was off except for the basement A/C? With both compressors running and nothing else running like battery charger, water heater, etc. you should be reading about 25 amps.
__________________
KIX
2002 Ultimate Advantage 40J-Spartan-Cummins
2004 Jeep Rubicon 2004 Subaru Forester
  Reply With Quote
   
Old 07-01-2010, 02:35 PM   #6
GA Cajun is offline
Member
GA Cajun's Avatar
Winnebago Owners Club
Join Date: Jun 2008
Location: Statesboro, GA
Posts: 79
Kix

Yes everything else was off. I had a feeling that it was pulling too much juice. I'll get it checked as soon as I can.

Thanks
__________________
2002 Winnebago Journey DL 39QD
2003 Acura 3.2TL Type S & 2005 Honda Odyssey EX-L
Better half, 2 sons-13 & 11
  Reply With Quote
   
Old 07-01-2010, 03:24 PM   #7
RJay is offline
Community Administrator
RJay's Avatar


Newmar Owners Club
Join Date: Jan 2010
Posts: 4,593
cajun, do you know what the output voltage of the generator was at the time you saw 32 amps?
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
  Reply With Quote
   
Old 07-01-2010, 06:12 PM   #8
KIX is offline
KIX
Senior Member
KIX's Avatar


Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 1,639
GACajun..........sounds like RJay may have a good idea here. If your genset voltage was low it would explain a couple of things. Low voltage would cause the appliance (A/C) to use more amps AND it would cause the genset to run at higher RPM trying to produce 120volts.
Check your genset out and let us know.
__________________
KIX
2002 Ultimate Advantage 40J-Spartan-Cummins
2004 Jeep Rubicon 2004 Subaru Forester
  Reply With Quote
   
Old 07-01-2010, 07:53 PM   #9
ernieh is offline
Senior Member
Join Date: Jul 2009
Posts: 513
My coach shows 22 or 23 amps when both compressors are running.
__________________
ernieh
2003 Journey DL, 2007 Wrangler Toad
Coming soon, 2012 Phaeton 36QSH
  Reply With Quote
   
Old 07-02-2010, 09:50 AM   #10
MaverickBBD is offline
Senior Member
MaverickBBD's Avatar


Winnebago Owners Club
Freightliner Owners Club
Join Date: Aug 2006
Location: Formerly of Washington State
Posts: 878
After a start up draw of 28 to 29 amps my ac draws 25 to 26 amps. I would suspect the voltage output of your generator. Your numbers JDSR (just don't sound right).
__________________
Tom, Cheryl & Blossom(coonhound mix) Formerly of Bellingham,WA'05 Winnebago Journey 36G. FL-XC, Cat 350, aero muffler, AFE filter, 4 FSD Koni's, ultra track bell, SafeT+, FMCA397030, WIT 129107
  Reply With Quote
   
Old 07-02-2010, 10:30 AM   #11
Fossilhog is offline
Senior Member
Fossilhog's Avatar
Join Date: Feb 2006
Location: Howell, New Jersey
Posts: 329
Send a message via AIM to Fossilhog
Are you guys talking about a 30 or 50 amp setup? As I said, my Adventurer (30 amp) sheds power over a 30 amp draw and shuts down compresser #2. On generator the highest read on the ems is 17 becasue the 2nd compressor gets direct draw from the 20 amp breaker on the generator.....
__________________
Tim ,Retired Police Lt.
2002 Winnebago Adventurer+16' Trailer
Harley Road King and Heritage Classic+ Border Collie,Trik-L-start,Hughes Autoformer
  Reply With Quote
   
Old 07-03-2010, 10:36 AM   #12
GA Cajun is offline
Member
GA Cajun's Avatar
Winnebago Owners Club
Join Date: Jun 2008
Location: Statesboro, GA
Posts: 79
I have no idea what the voltage output of my generator is - yet. I'll have my RV guy check that too. Thanks for the suggestion!!
__________________
2002 Winnebago Journey DL 39QD
2003 Acura 3.2TL Type S & 2005 Honda Odyssey EX-L
Better half, 2 sons-13 & 11
  Reply With Quote
   
Old 07-03-2010, 03:30 PM   #13
KIX is offline
KIX
Senior Member
KIX's Avatar


Join Date: Dec 2006
Location: St. Augustine, FL
Posts: 1,639
Quote:
Originally Posted by GA Cajun View Post
I have no idea what the voltage output of my generator is - yet.
Cajun, It's prudent to be able to know the voltage output of your genset. There are easy ways to be able to tell at a glance. RV Upgrades, et al, sell several different plug in meters that can stay plugged into a moho receptacle. There's the Kill-a-Watt, Good Governor and a plug in analog one too. it's very easy to read the voltage at the receptacle on any of these units. The cheap ones are probably around $20.
If you know how to use a VOM (volt-ohm meter) you could read it with the VOM too. You just would have to remember to get the VOM out to take a reading.
__________________
KIX
2002 Ultimate Advantage 40J-Spartan-Cummins
2004 Jeep Rubicon 2004 Subaru Forester
  Reply With Quote
   
Old 07-06-2010, 07:02 PM   #14
GA Cajun is offline
Member
GA Cajun's Avatar
Winnebago Owners Club
Join Date: Jun 2008
Location: Statesboro, GA
Posts: 79
Kix,

Ya know, I do have one of those cheapy voltmeters that stays plugged in to a receptacle. I don't remember ever looking at it while the genset was running. I'll have to take a look next time I can get to the MH.

Thanks for the reminder.

__________________
2002 Winnebago Journey DL 39QD
2003 Acura 3.2TL Type S & 2005 Honda Odyssey EX-L
Better half, 2 sons-13 & 11
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need model number for the basement air RV 4 2 National RV Owner's Forum 5 08-26-2008 06:10 AM
Basement air question JWatkins Winnebago Industries Owner's Forum 3 06-20-2008 06:57 AM
Rear slide hydraulic leak / basement air question DragRacer Winnebago Industries Owner's Forum 19 02-20-2008 01:36 PM
Basement air & heat pump PaulC Winnebago Industries Owner's Forum 19 09-27-2007 04:46 AM
basement air discharge temps. RKL2 Winnebago Industries Owner's Forum 12 05-05-2006 08:51 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 03:01 AM.