Circuit Breaker blowing
Old 10-21-2011, 04:01 AM   #1
WendellG is offline
Junior Member
WendellG's Avatar
Workhorse Chassis Owner
Winnebago Owners Club
Join Date: Dec 2010
Posts: 14
If I run 2 portable heaters on 1500 w, or 1 and start the coffee pot, the 20 amp circuit breaker blows! Can this be fixed to not blow ??? Thanks

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-21-2011, 04:15 AM   #2
Steve N Sal is online now
Senior Member
Steve N Sal's Avatar


Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2007
Location: Michigan
Posts: 2,590
With the load your indicating with the heaters, then NO. 1500W divided by 120V = 12.5amps X the two heaters is 25 amps. Don't know what the wattage draw is on the coffee pot but it must be high enough to still exceed the amp rating of the breaker. Don't you have more then one circuit so you can divide the load? DO NOT just increase the size of the breaker rating to overcome the problem. The wire would not be sized properly to carry the load.

__________________
Steve & Sally / HiTee & Hudson Our Little Poms / Heidi & Houston Forever in our Hearts
04 NEWMAR MACA 3778 W22 / 05 PT Vert / Demco KAR KADDY SS
  Reply With Quote
   
Old 10-21-2011, 12:28 PM   #3
Dave78Chief is offline
Senior Member
Dave78Chief's Avatar


Join Date: Jun 2009
Posts: 1,069
You could have 30 (page 2) or 50 amp (page 3) service. Like Steve said, select recepticles on different load circuits
http://www.winnebagoind.com/diagram/...ire_172077.pdf

Wiring TOC for your rig: Table of Contents

Dave
__________________
Dave in Virginia
1978 Winnebago Chieftain
Dodge M400 - 440-3
  Reply With Quote
   
Old 10-21-2011, 04:45 PM   #4
George Schweikle is offline
Senior Member
George Schweikle's Avatar
Join Date: Apr 2004
Posts: 302
No. Your circuit breaker was doing what is is supposed to do. All residential circuit breakers are actually rated by Underwriters Laboratory as "Intermittent duty"; with continuous duty at 80% of handle rating. In this case, a 20 A breaker should only hold in at 16 A, but the "Hold-in, Trip-out" window begins at this point. At anything over this, there is a time / load curve that defines when the breaker will thermally trip. A 17A load takes a long time to trip, but 20A trips within 10 - 15 minutes if my work memory is accurate (short circuits cause the breaker to trip literally instantaneously).

Circuit breakers trip to protect the insulation on the wires, GFI breakers trip to protect people.

Quote:
Originally Posted by WendellG View Post
If I run 2 portable heaters on 1500 w, or 1 and start the coffee pot, the 20 amp circuit breaker blows! Can this be fixed to not blow ??? Thanks
__________________
George Schweikle
Lexington, KY
1999 Safari TREK 2830
  Reply With Quote
   
Old 10-21-2011, 05:06 PM   #5
Cougarkid is offline
Senior Member
Cougarkid's Avatar
Freightliner Owners Club
Join Date: Sep 2011
Location: Mid-Missouri
Posts: 156
A coffee maker draws a lot of amps.

If you want to see how much different things draw, just fire up your generator.
Turn on different applicances, one at a time and see how your generator reacts.
The coffee maker will surprise you.

Been there, done that.
__________________
Mike and Carla
1998 42' Overland Larado Diesel Pusher
Full-Timing in one place - for now
  Reply With Quote
   
Old 10-21-2011, 06:06 PM   #6
bachler is offline
Senior Member
Winnebago Owners Club
Join Date: Oct 2009
Posts: 659
The pre poster Nailed it;; If it is a 25 amp braker. The MAXIMUM Continous draw should be NO more then 15 amps; So many People are Idiots;; when a braker says 25 amps they Invarieable try to plug in A 25 amp load;;;; As a study load ;; it don't work that way; Use your head;; Don't plug it in. Life is good; Some will say I am to Harsh; Maybe;; It also may keep you from burning your RV. to the ground; Electrical fires in RV are all to common and most are Fatel;;
__________________
  Reply With Quote
   
Old 10-22-2011, 02:03 AM   #7
WendellG is offline
Junior Member
WendellG's Avatar
Workhorse Chassis Owner
Winnebago Owners Club
Join Date: Dec 2010
Posts: 14
Thanks guys, it is a 20 amp breaker. Is there a safe way to fix this?
__________________
  Reply With Quote
   
Old 10-22-2011, 02:28 AM   #8
Journey39n is offline
Member
Journey39n's Avatar
Join Date: Jul 2010
Location: back in the Pacific NW for the summer
Posts: 75
I would say there is no 'safe' way to fix this, if all are on the same breaker.

In our coach, there are three breakers that split the various outlets, front, middle, rear. In the cold spells during winter last year, to save propane, we had three 1500w heaters, that were all running, on thermostats, cycling on and off, but I'm sure there were times they would all run at the same time.

Only tripped one breaker once, front heater was on, and we tried to use an electric frypan. So we learned not to run the heater on that circuit while cooking.
__________________
2010 Journey 39n - 2010 Jeep Wrangler - living aboard, traveling in the Pacific NW
  Reply With Quote
   
Old 10-22-2011, 03:54 AM   #9
Steve N Sal is online now
Senior Member
Steve N Sal's Avatar


Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2007
Location: Michigan
Posts: 2,590
Fixing it is as I mentioned before. You have to split the load up. You have determined it was a 20A breaker. There should be more breakers in the panel and there should be a panel label with circuits identified on that label. If not, purchase a plug in voltage tester, turn the breakers off one at a time and now see what receptacles are not working. Make yourself a list of these recptacles or a diagram of their location and keep it in safe keeping for future problems. Now that you have identified what breakers control what, if you need a heater in the bedroom/bath area plug it in there. If you need one in the living area plug another in that area, remembering that they MUST be on different circuits. Now if you want to use the coffee pot and it turns out to be on one of these circuits, then you will have to unplug the heater at that location. Same goes for the other heater, if it's in that bath area and the wife wants to use a hair dryer or curling iron then that heater will probably have to be unplugged. It's all a matter of balance. Failed to mention that it's also a good time to identify these circuits on the panel label which is usually attached to the inside part of the door when you open it. If there is not one there you can easily make yourself one and attach it with some tape. In addition you also probably have some receptacles in your storage bay area. You will want to know what circuits they are on as well. "Whew" hope this helps you out.
__________________
Steve & Sally / HiTee & Hudson Our Little Poms / Heidi & Houston Forever in our Hearts
04 NEWMAR MACA 3778 W22 / 05 PT Vert / Demco KAR KADDY SS
  Reply With Quote
   
Old 10-22-2011, 10:40 AM   #10
wa8yxm is offline
Senior Member


Workhorse Chassis Owner
Damon Owners Club
Join Date: Mar 2009
Posts: 8,060
1500 watts/120 volts = 12.5 amps

Times 2 = 25 amps

you are already 5 amps over the rating of the breaker and it should blow at, as I recall 17 long term..

So, no, there is no cure

now if you have one 1500 watt on one breaker and another on another (As i do it) and the coffee maker (often in the thousand watt range) is sharing a circuit let's see what the math says

2500 watts / 120 volts =20.833333 amps Again your 20 amp breaker should make a very quick CLICK

Your options are to use a stove top coffee maker, or a smaller (less wattage) coffee maker or to add a circuit.

In my motor home there are 3 20 amp outlets (2 of 'em on 15 amp breakers) each outlet has a breaker to it's lonesome

One (Factory installed) feeds my Progressive Dynamics 9180 with charge wizard Therotical max draw is right around 10 amps which is why i changed it to a 15 amp breaker... The other two I added, one in the bedroom one in the living room. they are fed with 12ga wire off a 15 and 20 amp breaker in the box.. Eventually they will both have 20 amp breakers.

These are for space heaters.. One more space heater line is a 15 amp (Originally the washing machine/dryer line but I did not opt for them.. rig still came wired, so I "retasked" by means of a 20 amp capable appliance type extension cord with 15 amp plug and outlet.
__________________
Home is where I park it!
  Reply With Quote
   
Old 10-22-2011, 07:26 PM   #11
Party Barge is offline
Senior Member
Join Date: May 2006
Posts: 169
WendellG,
Our Horizon seems to also have many of the plugs in the galley area and micowave on the same 20 amp breaker. On 30 amps site, you have to watch everything you turn on and off, with a 50 amp site, using two space heater, coffee maker, microwave will blow the breaker.

We have a heat pump which we use in conjunction with one space heater, and using the vinyl vent covers help control the heat. I installed a rope lite in my water inlet bay that I turn on during freezing weather.

I have been considering a stand alone circuit which would run from the rv park pedistal 15 amp gfi into the rv and to a new dedicated out let for a space heater. This would allow for a little more flexiibility during cold periods.
My expreince has been that when Its 15degr. or lower the rv is just hard to keep warm with out using the propane heater.
__________________
Bob and Bev

06 Itasca 40' Horizon KD
  Reply With Quote
   
Old 10-22-2011, 09:28 PM   #12
Jerry J is offline
Senior Member
Jerry J's Avatar
Winnebago Owners Club
Freightliner Owners Club
Join Date: Dec 2000
Location: N Id
Posts: 359
Quote:
Originally Posted by Party Barge View Post
WendellG,
Our Horizon seems to also have many of the plugs in the galley area and micowave on the same 20 amp breaker. <<<<<<<<<
Our Vectra has a 15amp circuit breaker for the microwave. The plugins are separate circuits.
__________________
Jerry J.
2008 Winnebago Vectra 40TD
2007 Honda CRV
  Reply With Quote
   
Old 10-23-2011, 01:22 PM   #13
wa8yxm is offline
Senior Member


Workhorse Chassis Owner
Damon Owners Club
Join Date: Mar 2009
Posts: 8,060
My RV (Damon Intruder) has one breaker JUST for the microwave, One feeds all televisions and such, One feeds the GFCI outlets (kitchen, bath, dining table, patio) one the bedrooom outlets and fridge, one the Washer/Dryer box One for the water heater and two for the air conditioners (one each) (I think that's all from teh factory)..

I have added 2 circuits (30 amp) for feeding power back to the house via a proper inlet and transfer panel or for daisy chaining to another RV. Two 20 capable (one is) for space heaters and such.

Lots of breakers and room for at least one more.
__________________
Home is where I park it!
  Reply With Quote
   
Old 10-24-2011, 08:41 AM   #14
bachler is offline
Senior Member
Winnebago Owners Club
Join Date: Oct 2009
Posts: 659
Posters Please Be extremley Care full When plugging Electric heaters in;; A lot of wire In the RV industery is 14or even 16 Gage; When I hear some one Putting a larger breaker in. I get the chills.;;And I ask my self WHY don't they just put a gun to there head and pull the Trigger..Over the winter months We all read of familys Burning to death in Trailer houses, The cause. "ELECTRIAL short" Before you plug an electric heater in. "DO YOUR HOME WORK" We can all tell of tarrible stories;; It's not allways the other guy.. Please I may seem Harsh; Be carefull.. Life is good. IN Any home If an Electrial Circuit is needed for a Electrial heater, electrial water tank, Bathroom ,hair dryers ETC , It will allways be a dedecated circuit, Nothing else on it EXCEPT;; Because there is a plug inlet, that does not mean something can be plugged in.. Be carefull.. life is good

__________________
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Resetting the Service light 4x4crazy Cummins Engines 6 03-01-2011 08:26 PM
circuit breaker panel JBroadaway Winnebago Industries Owner's Forum 0 01-22-2011 08:22 PM
Circuit Breaker Wingnut57 5th Wheel Discussion 4 03-25-2010 05:51 PM
Failed Circuit Breaker gjstacy Alpine Coach Forum 5 09-02-2009 10:14 AM
Circuit Breaker Question Sallys Mom 5th Wheel Discussion 5 07-19-2005 06:12 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 11:36 AM.