Quote:
Originally Posted by scottma
I installed the battery today. I ran the generator and the Dimensions charger quickly moved from bulk charge to acceptance charge and was at 14.1 volts 20 amps when I turned it off and put the coach away. So........I did not let it charge long enough to go into float mode. Is that a problem or will it just pick up where it left off next time I plug in our run the generator? Do the house batteries get charged from the alternator also?
|
No and yes. You should let the battery go up to float, give or take (according to temp) +14.4 VDC. the alternator
should charge both batteries while the engine is running. I don't know what the total Amp Hours (AH) rating on that house battery is but if it's over 400 amp hours, the dimensions charger will have to be reset to the higher AH. That's a smal switch located on the right side of the charger/inverter. I think the switch positions are 1:AGM under 400AH 2:AGM over 400AH, 3:wet cell under 400AH and 4:wet cell over 400AH. I'm not sure about these, you had better check your operating instructions for the details.
The charger/inverter will start over on a new cycle when you run the generator again. No big deal, it'll go thru the whole cycle and do nothing damaging.
I just reread your OP. I don't know what to do about a Gel Cell battery. You should check with the manufacturer of the charger/inverter. I would guess (just a guess) you should treat that puppy like an AGM. That would be charging it at a lower max voltage. Someone out there will be posting here and set us straight.