Electrical Issue
Old 10-21-2010, 12:00 PM   #1
1oldbanker is offline
Junior Member
Join Date: Apr 2010
Location: Western New York State
Posts: 10
I am the owner of a 2007 Itasca Sunrise model 35L motorhome that was purchased new in Feb., 2007. On a recent trip, we were plugged into a 50 amp hookup when we lost all power. After about an hour, the power came back on. We were told by an employee that a traffic accident near the campground took out a transformer that had to be replaced. Later that day we noticed that the PowerLine Display Panel was no longer showing 50 amps but was instead blinking every 2-3 seconds between 30 and 50 amps. An employee of the campground checked the service box and determined that 50 amps were available but had no answer as to why the Display Panel continued to blink alternating between 30 and 50 amps. After unplugging from the service box, I started the generator and it showed under the service type that the GenSet was on and the 30 amp light lit up. However, the AC Line stayed at zero despite using several appliances including central AC.

After returning home, I plugged into my 50 amp box and got the same results as in the campground but now it does not blink between 30 and 50 amps. It just shows 30 amps. The GenSet continues as described above.

I have an appointment in a few days to take my new toad to a RV and truck repair service to install a tow bar and all electrical hookups so it can be towed by our RV. I have spoken with them about the problems with the PowerLine Display Panel and they will see if they can solve that issue also.

Is there anything I can do before delivering the RV to the repair center to solve my electrical problem and be assured that I have 50 amps? Working with electricity is not my cup of tea and I am quite hesitant to mess around with something I know little about. Any suggestions would be appreciated.

1Oldbanker

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-21-2010, 12:19 PM   #2
RickO is online now
Community Moderator
RickO's Avatar


Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 5,140
Welcome to the forum Oldbanker. Sounds like you've got a weird problem on your hands.

Does your 30 amp light usually come on when you running the generator? When you say "the AC Line stayed at zero despite using several appliances including central AC" are you taling about the load meter on your Powerline? Is it blank or does it actually read zero? Also, do you use a surge protector? In hind sight, it probably would have been a good idea to turn off the 50 amp breakers on the pedistal when power went down to avoid a possible brown out situation when the power came back on.

Rick

__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
  Reply With Quote
   
Old 10-21-2010, 12:28 PM   #3
RJay is offline
Community Administrator
RJay's Avatar


Newmar Owners Club
Join Date: Jan 2010
Posts: 4,593
It could be a couple of things but it sounds like the breaker that supplies power to your second air conditioner when plugged into a 50 amp service is tripped.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
  Reply With Quote
   
Old 10-21-2010, 02:39 PM   #4
movin-on is online now
Senior Member
Join Date: Jan 2008
Location: New Hampshire
Posts: 282
As long as nothing was fried when the power came back on because of a possible surge, there is an ethernet/telephone type cable plugged into the back of the board of the EMS..Unplug it for a few minutes and plug it back in...This should reset the board...Worth a try...Also buy a surge protector...Worth every penny...
__________________
  Reply With Quote
   
Old 10-22-2010, 04:12 AM   #5
1oldbanker is offline
Junior Member
Join Date: Apr 2010
Location: Western New York State
Posts: 10
Quote:
Originally Posted by RickO View Post
Welcome to the forum Oldbanker. Sounds like you've got a weird problem on your hands.

Does your 30 amp light usually come on when you running the generator? When you say "the AC Line stayed at zero despite using several appliances including central AC" are you taling about the load meter on your Powerline? Is it blank or does it actually read zero? Also, do you use a surge protector? In hind sight, it probably would have been a good idea to turn off the 50 amp breakers on the pedistal when power went down to avoid a possible brown out situation when the power came back on.

Rick
The loadmeter would always show the amount of amps being used when the generator was in use. Now only zero. Do not have surge protecter but will order one for future use.

Thanks for your thoughts.
__________________
  Reply With Quote
   
Old 10-22-2010, 04:14 AM   #6
1oldbanker is offline
Junior Member
Join Date: Apr 2010
Location: Western New York State
Posts: 10
Quote:
Originally Posted by RJay View Post
It could be a couple of things but it sounds like the breaker that supplies power to your second air conditioner when plugged into a 50 amp service is tripped.
Only one breaker for basement central air conditioner/heat pump. Both heat and air work fine.
__________________
  Reply With Quote
   
Old 10-22-2010, 04:16 AM   #7
1oldbanker is offline
Junior Member
Join Date: Apr 2010
Location: Western New York State
Posts: 10
Quote:
Originally Posted by movin-on View Post
As long as nothing was fried when the power came back on because of a possible surge, there is an ethernet/telephone type cable plugged into the back of the board of the EMS..Unplug it for a few minutes and plug it back in...This should reset the board...Worth a try...Also buy a surge protector...Worth every penny...
What is the EMS? Surge protector will be bought.

Thanks for your thoughts.
__________________
  Reply With Quote
   
Old 10-22-2010, 09:11 AM   #8
AFChap is offline
Senior Member
AFChap's Avatar


Winnebago Owners Club
Join Date: Aug 2002
Location: ...hopefully on the road!
Posts: 3,176
An 07 Itasca with 50a should have a breaker for each main ...total of two ...and also a breaker for each ac stage ...again, two.

Re-setting the EMS board is an excellent idea too ...the board where you are reading the amps. You can gently remove it from the wall to unplug the large phone-type cable, OR you can ulplug the other end at the inverter if that is accessible. Leave it disconnected for apx 5 min before plugging it back in.

When on 50a shore power you will see no reading in the amps used window. When on 30a/20a/15a shore power OR generator you should see a reading for amps being used.
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
'03 Winnebago UA 40e / '00 Honda Odyssey toad
  Reply With Quote
   
Old 10-22-2010, 09:33 AM   #9
NO1RAINH20 is offline
Member
Winnebago Owners Club
Join Date: Apr 2008
Posts: 67
My money is on a bad ems board in the breaker box,but before you condem the board check all the lug connections on the board
__________________
  Reply With Quote
   
Old 10-23-2010, 09:19 AM   #10
1oldbanker is offline
Junior Member
Join Date: Apr 2010
Location: Western New York State
Posts: 10
Quote:
Originally Posted by NO1RAINH20 View Post
My money is on a bad ems board in the breaker box,but before you condem the board check all the lug connections on the board

I did remove the only connection behind the EMS panel that consisted of a plug with 3 wires attached. After about 15 minutes I plugged them back together with no change in results. Will continue to check everything again including unplugging the above wires for a longer period of time.

Thanks everyone for your input.

Oldbanker
__________________
  Reply With Quote
   
Old 10-23-2010, 10:54 AM   #11
wa8yxm is offline
Senior Member


Workhorse Chassis Owner
Damon Owners Club
Join Date: Mar 2009
Posts: 8,068
Many times when power is restored there is... ONE HECK OF A SURGE, standard spike supressors won't clip it.. A surge guard (Power line monitor) may cut it off in time to protect things, but it may have happned that your EMS got spiked big time.

Going to the dealer, in this case.. Which you already have scheduled, is my best suggestion.
__________________
Home is where I park it!
  Reply With Quote
   
Old 10-23-2010, 11:07 AM   #12
jackrobinryan is offline
Senior Member
jackrobinryan's Avatar
Workhorse Chassis Owner
Join Date: Oct 2006
Location: wherever
Posts: 341
I had a very similar problem on the EMS display on our '07 Adventurere.

(search on my posts from a year or so ago)

Turns out my ac to dc converter, the garbage Parallax 7455, was "bleeding AC voltage into the dc output side of the converter. (verified by voltmeter) As explained to me, the EMS board is the most sensitive 12 user aboard to this problem and will act strange when it sees this AC on it's dc supply.

Under warranty, Winnie sent a new converter to my dealer, who sent it to me and I swapped it out. Solved the problem.

Later, I decided to by an Iota 55A converter (smarter, smaller 3 stage intelligent converter) and took the Parallax out.

jack
__________________
2007 Adventurer 38T w/
sway & trac bars, Koni FSDs and SafeT+
2006 Jeep Liberty toad
  Reply With Quote
   
electrical
Old 10-23-2010, 05:03 PM   #13
pawpawboyce is offline
Senior Member
pawpawboyce's Avatar
Winnebago Owners Club
Join Date: Aug 2010
Posts: 117
Blog Entries: 4
well sir, i had a similiar problem. plugged into 50 amp, but would only read 30 and the ac comp #2 did not light up. all the breakers were checked and stayed the same. all in all, it took a new board in my information center.
i have extraride thank goodness. costs 2,400.00 and i don't have a clue if that was good or bad since i don't know anything too much about electricity. good luck.

boyce and lisa
06 meridian 39k
06 jeep limited tow

__________________
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
rv electrical stuff russ31073 Vintage RV's 5 09-02-2010 08:50 PM
Electrical issue radams MH-General Discussions & Problems 30 08-01-2010 05:59 AM
30 amp to 50 amp Electrical Upgrade mikwallace Winnebago Industries Owner's Forum 17 11-30-2009 10:17 AM
First Time Owner, Electrical Outlet Issue ATLFleetWood RV Systems & Appliances 18 09-02-2009 09:28 AM
Newmar Dutch Star-3126 Cat Electrical Issue waybuzd MH-General Discussions & Problems 4 08-19-2009 08:26 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 07:41 PM.