In big round numbers in crayon.
An 4k Onan running a single 13.5k btu a/c unit will be running at 30% load when the compressor is cycling only, otherwise about 15%. According to Onan this unit consumes about 0.5 gal / hour at 50% load, at no load it's about 0.3 gal / hour.
Since the ratio between compressor run time and fan only is entirely dependent on temp and thermostat setting it's impossible to determine your use.
If you 'guess-timate' that the generator will be running at an average of 25% load for 8 hours a day it would look something like this;
8 hours x 0.4 gal / hour = 3.2 gal / day.
Most units have generator fuel line set at 1/3rd level of tank, so 69 gal x .66 = ~45 gallons useable by the generator.
45 gallons / 3.2 (gal per day) = 14 days.
YMMV.
I know in my case (based on the generators Hobbs meter) it will run for ~80 hours before the fuel level drops too far and it starves out.