Unhappy Lost leg on 50 amp service

I was in Georgia when a storm went thru. Now when I plug into a 50 amp service, the control center only recognizes 30 amps. We checked the park power and it was all there. Tried 2 other campgrounds, still only 30 amps. Is there an in-line fuse somewhere or is the control center damaged? Any assistance will be greatly appreciated.
newyorkRVr is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-13-2019, 07:49 PM   #2
Senior Member
 
richard5933's Avatar
 
Join Date: May 2019
Posts: 2,392
If you are comfortable working with electric connections, unplug your coach, turn off the generator, and then check all the connections inside your transfer switch. Might be a good idea to also check the connections all the way from the inlet to the breaker panel, as well as the power cord itself. My guess is that you'll find a loose connection in there, and hopefully it hasn't yet burned up the insulation and done any damage.
__________________
Richard
1994 Excella 25-ft (Gertie)
1999 Suburban LS 2500 w/7.4L V8
1974 GMC 4108a - Custom Coach Land Cruiser
richard5933 is offline   Reply With Quote
Old 07-13-2019, 08:00 PM   #3
Senior Member
 
Howard Burger's Avatar
 
Join Date: Mar 2019
Location: Wasilla, AK
Posts: 202
terms

What I'm seeing in your post is this: you have a 50 amp service for your unit. This means you have a male plug with four prongs: two hots, a neutral and a ground. A 2-pole 50 amp breaker controls power into the female receptacle you plug into at the pedestal. Each one of the hots is called a 'leg'.



It sounds like you now plug into a pedestal and only one 'leg' is hot in the panel in you unit. Right?



It's still a 50 amp 'leg', which means if you exceed 50 amps the breaker will trip.


The 30 amp service is only three prongs, one hot, one neutral and one ground and has a single pole 30 amp breaker.


Now,I assume you checked the pedestal with a dmm or voltage tester and found both legs are hot, right?


Now here's the tricky part. If you're not trained in electrical work, don't pull the panel cover and check your panel to see if both legs are hot. Do this: find a 240V receptacle and use the dmm or voltage tester to check both legs. One hot, one not? If you don't have a 240 V receptacle (in a house it would be for the electric range or electric dryer; I don't know what would need a 240V rec. in a class A), get someone who does electrical work to check you panel.


Now you can start troubleshooting.
__________________
2019 Outdoors 21RBS
2018 Ford F150 w/Eco & max tow pkg
2023 F250 7.3L gas; 10 speed; 3.73
Howard Burger is offline   Reply With Quote
Old 07-13-2019, 08:42 PM   #4
Senior Member
 
Join Date: Oct 2014
Location: Cypress River Manitoba
Posts: 304
Quote:
Originally Posted by newyorkRVr View Post
I was in Georgia when a storm went thru. Now when I plug into a 50 amp service, the control center only recognizes 30 amps. We checked the park power and it was all there. Tried 2 other campgrounds, still only 30 amps. Is there an in-line fuse somewhere or is the control center damaged? Any assistance will be greatly appreciated.
If all your plugs and stuff works, then I think you have 50 amps when plugged into a 4 prong 50 amp service outlet.
If the control center 'thinks' you have only 30 amps, there is a fault with the control center. On my rig, when the electric water heater circuit breaker is OFF, the control center 'thinks' we are connected to 30 amp irregardless of the fact that we are plugged into 50 amp. I guess the control center uses that particular circuit to help determine 50 amps.
There is also a fuse on the electronic board of the control center right close to the main circuit breaker panel. Might be blowed messing up the control logic.

Make sure to let us know how you make out.


Stan
The electronic board is within the main circuit breaker panel
__________________
2004 Itasca Sunrise W22 chassis GM 8.1 Allison 1000 Towing a 2007 Chevy Cobalt four wheels down.
Switchflicke is offline   Reply With Quote
Old 07-13-2019, 08:48 PM   #5
Moderator Emeritus
 
Spk64's Avatar


 
Newmar Owners Club
Join Date: Apr 2014
Location: Southern Indiana
Posts: 19,417
Verify all your breakers are turned on in your breaker panel in the coach. The sensing circuit may be tied to a breaker that was turned off or tripped.
__________________
Steve
2002 Newmar Mountain Aire 4095
Spk64 is offline   Reply With Quote
Old 07-15-2019, 09:31 AM   #6
Member
 
Join Date: Aug 2010
Location: compton md
Posts: 91
just went through this,i losy a leg on the shore power and a leg on generator, I had to use both to get it all to work. It wa the automatic transfer switch, have it tested. that's where your issue is
bad1032 is offline   Reply With Quote
Old 07-15-2019, 10:30 AM   #7
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 3,940
Probably as Switchflicke says, it is the breaker for the water heater. Switch the water heater off and on a couple of times. I would do it with the shore cord unplugged or the pedestal breakers off.
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C F53V10 Handicap Equipped
1999 Jeep Cherokee, 1991 Jeep Wrangler Renegade and 2018 Chevrolet Equinox Diesel
John Hilley is offline   Reply With Quote
Old 07-15-2019, 10:40 AM   #8
Senior Member
 
KanzKran's Avatar
 
Join Date: Sep 2018
Posts: 1,944
Quote:
Originally Posted by Spk64 View Post
Verify all your breakers are turned on in your breaker panel in the coach. The sensing circuit may be tied to a breaker that was turned off or tripped.
I would just add that the OP should cycle the breakers, fully 'off' then back to 'on', not just visually check. Many breakers don't show tripped status very well, and some even feel like they're still on when they're not (free-trip handles). I get calls every couple of years from DW's sister with exactly that issue. Fortunately, no site visit required for that.
KanzKran is offline   Reply With Quote
Old 07-15-2019, 10:50 AM   #9
Senior Member
 
Join Date: Apr 2017
Posts: 436
The only way the control center could assume 30A service is if one leg of the power cord were dead or the voltage between legs is 0.


Any chance a 30A to 50A dog bone adapter is connected. 50A 240VAC at the pole provides 50A to each hot leg.



If 50A service is identified when the generator is running, it would limit the issue to be from the transfer switch to the plug on the land line.


If the generator doesn't provide 50A service, problem is with the transfer switch toward coach.
Ndrorder is offline   Reply With Quote
Old 07-15-2019, 11:25 AM   #10
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2005
Location: Buxton, North Dakota
Posts: 3,940
The CT (current transformer) is in the water heater circuit. It helps determine whether 30 amp or 50 amp
__________________
2003 Winnebago Adventurer 38G F53/ V10 605 watts of Solar
1999 Winnebago Brave 35C F53V10 Handicap Equipped
1999 Jeep Cherokee, 1991 Jeep Wrangler Renegade and 2018 Chevrolet Equinox Diesel
John Hilley is offline   Reply With Quote
Old 07-15-2019, 12:24 PM   #11
Senior Member
 
Join Date: Jul 2014
Posts: 35,446
The control center decides if you have 30 amp or 50 amp service by measuring voltage between L 1 and L 2.

If it measures 0 volts, it assumes 30 amp service. If it measures 240 volts, it assumes 50 amp service.

If one of the sense lines is tied to a breaker that is off, it will measure 0 volts and assume 30 amp service.
twinboat is offline   Reply With Quote
Old 07-15-2019, 12:31 PM   #12
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
Quote:
Originally Posted by AK_Howard View Post
What I'm seeing in your post is this: you have a 50 amp service for your unit. This means you have a male plug with four prongs: two hots, a neutral and a ground. A 2-pole 50 amp breaker controls power into the female receptacle you plug into at the pedestal. Each one of the hots is called a 'leg'.

It sounds like you now plug into a pedestal and only one 'leg' is hot in the panel in you unit. Right?

It's still a 50 amp 'leg', which means if you exceed 50 amps the breaker will trip.

The 30 amp service is only three prongs, one hot, one neutral and one ground and has a single pole 30 amp breaker.

Now,I assume you checked the pedestal with a dmm or voltage tester and found both legs are hot, right?

Now here's the tricky part. If you're not trained in electrical work, don't pull the panel cover and check your panel to see if both legs are hot. Do this: find a 240V receptacle and use the dmm or voltage tester to check both legs. One hot, one not? If you don't have a 240 V receptacle (in a house it would be for the electric range or electric dryer; I don't know what would need a 240V rec. in a class A), get someone who does electrical work to check you panel.

Now you can start troubleshooting.
Some of the higher end RV's like mine do have a 240 volt dryer and even fewer have a 240 volt range.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 07-15-2019, 12:45 PM   #13
Senior Member
 
bruceisla's Avatar
 
Join Date: Oct 2012
Location: Foley AL
Posts: 7,138
So .... what happens when you use the generator?
__________________
2005 Newmar Essex 4502, 2013 Caddy SRX
1997 HR Endeavor 37, CAT, 1996 Geo Tracker
bruceisla is offline   Reply With Quote
Old 07-15-2019, 02:38 PM   #14
Senior Member
 
Join Date: Jul 2014
Posts: 35,446
Quote:
Originally Posted by bruceisla View Post
So .... what happens when you use the generator?
If your asking about Mr.D, he has a 240 volt generator.
twinboat is offline   Reply With Quote
Reply

Tags
service



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Total Amps available on each leg of 50 Amp service wagonmaster2 Newmar Owner's Forum 10 12-30-2017 04:11 PM
Fix for low voltage in one leg of 50 amp service? knightstorm RV Systems & Appliances 4 07-22-2017 06:36 AM
Kwikee Level Best 3000 Jacks - How to Service Leg Switch ChrisFSB MH-General Discussions & Problems 2 08-04-2012 10:19 PM
What is running on each leg of 50A service? wagonmaster2 Winnebago Industries Owner's Forum 23 03-01-2008 07:12 AM
Factory overloading one leg of the 50 Amp circuit JavaJelly Newmar Owner's Forum 5 11-28-2006 11:20 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:07 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.