Only 1 compressor with generator
Old 07-08-2011, 12:30 PM   #1
INSPECTORBOB is offline
Member
Ford Super Duty Owner
Join Date: Jul 2010
Posts: 82
On my 2000 Itasca Suncruiser 35u, the basement air draws about 22 amps while on a/c with both compressors running, but only 1 compressor runs, drawing about 10-13 amps using the Onan 4.8 kva generator. I tried using the generator to run fully loaded running the microwave, coffee pot and portable heater, which combined pull about 30 amps, with no problem so I know that the gen is working, and so is the air, but can't get the air going on 2 compressors using the generator. Suggestions?? Thanks!

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-08-2011, 05:16 PM   #2
The General is offline
Senior Member
The General's Avatar


Ford Super Duty Owner
Fleetwood Owners Club
Join Date: Sep 2007
Location: Rancho Cordova, California
Posts: 729
Send a message via Yahoo to The General
Quote:
Originally Posted by INSPECTORBOB View Post
On my 2000 Itasca Suncruiser 35u, the basement air draws about 22 amps while on a/c with both compressors running, but only 1 compressor runs, drawing about 10-13 amps using the Onan 4.8 kva generator. I tried using the generator to run fully loaded running the microwave, coffee pot and portable heater, which combined pull about 30 amps, with no problem so I know that the gen is working, and so is the air, but can't get the air going on 2 compressors using the generator. Suggestions?? Thanks!
Bob,
I would suggest calling Winnie and fiind out if there is a safety reason why when on gen you can't run both airs. Your gen produces less power than most which are at 5.5KW.
Let us know what you find out!


Steve

__________________
  Reply With Quote
   
Old 07-08-2011, 05:32 PM   #3
Wizard is offline
Senior Member
Wizard's Avatar


Freightliner Owners Club
Winnebago Owners Club
Join Date: Mar 2007
Location: Milledgeville Ga.
Posts: 1,160
Did you check the circuit breakers on the generator itself. Most has one brealer just for #2 compressor and another that runs everything else.

Mine has a 20amp and a 30amp breaker, I tripped the 20 amp once and my #2 compressor wouldn't run.
__________________
Jerry & Patsy, Taz & Jake
2000 Winnebago Journey
2006 Ford Explorer 4X4
  Reply With Quote
   
Old 07-08-2011, 07:40 PM   #4
INSPECTORBOB is offline
Member
Ford Super Duty Owner
Join Date: Jul 2010
Posts: 82
Thanks for the suggestions. With the gen rated for 40 amps, seems it should handle both with no problems. I will check with Winnie on Monday, but was hoping to get it running for the trip home this week-end.

Wizard, I checked both the breakers, and seem to be ok. Is your generator a 40 amp also? Mine is an Emerald 5000+. Problem is I don't know if I have a problem or if this is supposed to be this way, as General suggests.

Thanks
__________________
  Reply With Quote
   
Old 07-08-2011, 08:01 PM   #5
Perry White is offline
Senior Member


Join Date: Mar 2011
Location: Milwaukee
Posts: 1,422
The gen would run both, but it's not big enough to start them. 4kw won't start a 2 1/2 ton AC. 22 amp draw is 2.6kw. ,but it would take 5.2 KW to start it.
__________________
  Reply With Quote
   
Old 07-08-2011, 09:06 PM   #6
INSPECTORBOB is offline
Member
Ford Super Duty Owner
Join Date: Jul 2010
Posts: 82
There are 2 feeds to the a/c control panel. They are labeled "1" and "2". Both are seeing 120v using the generator.
Perry, while using the generator I start out with 13 amp draw, then settle at about 10 amps. Assuming the second compressor draws the same, and it requires 200% running current to start, then it should draw about 36 amps to run #1 and start #2 at the same time, right? (10+13+13). The gen puts out 40 amps, so I am confused!
__________________
  Reply With Quote
   
Old 07-08-2011, 09:08 PM   #7
TXiceman is online now
Moderator Emeritus
TXiceman's Avatar


Vintage RV Owners Club
Texas Boomers Club
Oklahoma Boomers Club
Ford Super Duty Owner
Join Date: Aug 2000
Location: Cypress, TX
Posts: 11,976
Is the generator a 240/120 VAC unit or just 120 VAC. If it is 120 VAC, the power management system is probably keeping 1 A/C compressor off.

ken
__________________
Amateur Radio Operator|Practicing for our retirement! 2008 Cameo 35SB3 - 2002 7.3L Crew Cab Dually w/ a SCMT - Max Brake - Travel with one Miniature Schnauzer, one Standard Schnauzer and one small Timneh African Gray Parrot
  Reply With Quote
   
Old 07-11-2011, 08:38 PM   #8
David Kanoy is offline
Member
David Kanoy's Avatar
Winnebago Owners Club
Join Date: Feb 2008
Location: Supply, NC
Posts: 40
Inspectorbob,

I have a 2000 Winne Adventure 35U with basement air that came from factory with 30 amp which I converted to 50 amp.

On my unit, before the 50 amp conversion, one leg of the genset was wired directly to the A/C compressor #2. The genset would run both compressors with no problem as long as no other large loads were on.

If you are comfortable with using a VOM, check the voltage on #2 compressor at the basement A/C power connection board with genset running. This power connection is at the lower left bottom of the A/C unit behind a removable metal plate.

Hope this helps,

David
__________________
2000 Winnebago 35U, Ford Triton V10, F53 Chassis. Toad: 2000 Honda Odyssey (296K Miles)
Home Made Trac Bar, Firestone Ride Rites, 5 Star Performance Tune
  Reply With Quote
   
Old 07-13-2011, 05:51 PM   #9
dirko is offline
Senior Member


Ford Super Duty Owner
Join Date: Dec 2002
Posts: 467
Hi Ho: I think WI kind of let people down by not pointing out that the second stage works on a separate winding on the generator. It doesn't register on the one-place because the wire doesn't go through the current sense torroid. The reason is that it is actually out-of-phase with the other stuff.

Anyway, be sure the 20 amp breaker on the generator is set and then be sure you have 120 v. on the second stage when the generator is running.

Dirk
__________________
  Reply With Quote
   
Old 07-14-2011, 05:53 AM   #10
Wizard is offline
Senior Member
Wizard's Avatar


Freightliner Owners Club
Winnebago Owners Club
Join Date: Mar 2007
Location: Milledgeville Ga.
Posts: 1,160
Actually mine is a 6.5kw. It has two breakers on the genny. The 30 amp breaker powers the AC unit and compressor #1, The 20amp breaker powers #2 compressor.

Its fairly east to overload one of the genny breakers by trying to use other devices such as coffee pot as the 20amp breaker also feeds the recepticals in the front of the coach.
__________________
Jerry & Patsy, Taz & Jake
2000 Winnebago Journey
2006 Ford Explorer 4X4
  Reply With Quote
   
Old 07-15-2011, 02:54 PM   #11
dirko is offline
Senior Member


Ford Super Duty Owner
Join Date: Dec 2002
Posts: 467
Hi Ho: Good point Wizard. I can understand why they didn't route the 20 amp through the current sense torroid because it would be out-of-phase with the 30 amp and actually subtract. However, I think you could run the wire through backwards from the 30 amp. and make it work. I've been meaning to try this out but just haven't got around to it.

What do you think?

Dirk
__________________
  Reply With Quote
   
Old 07-15-2011, 05:52 PM   #12
Wizard is offline
Senior Member
Wizard's Avatar


Freightliner Owners Club
Winnebago Owners Club
Join Date: Mar 2007
Location: Milledgeville Ga.
Posts: 1,160
Actually on mine and I think most Winnebagos, when the generator is running, there is no amp reading as the EMS switches over to 50amp mode.
__________________
Jerry & Patsy, Taz & Jake
2000 Winnebago Journey
2006 Ford Explorer 4X4
  Reply With Quote
   
Old 07-15-2011, 06:31 PM   #13
dirko is offline
Senior Member


Ford Super Duty Owner
Join Date: Dec 2002
Posts: 467
Hi Ho: That is probasbly true of the diesel coaches that usually have larger diesel generators. Most of the gas coaches that I've seen stay at 30 amps of the display. If you really had 30 + 20 amps that would be 6000 watts which is more than the generator is rated for.

Anyway we see the current just fine for the 30 amp winding, nothing for the 20 amp.

Is it worth putting the wire through the sense torroid in the wrong direction?

Dirk
__________________
  Reply With Quote
   
Old 07-15-2011, 08:29 PM   #14
FDchief is offline
Senior Member
FDchief's Avatar


Workhorse Chassis Owner
Join Date: Oct 2002
Location: Truckee, CA
Posts: 468
Quote:
Originally Posted by dirko
Hi Ho: I think WI kind of let people down by not pointing out that the second stage works on a separate winding on the generator. It doesn't register on the one-place because the wire doesn't go through the current sense torroid. The reason is that it is actually out-of-phase with the other stuff.

Anyway, be sure the 20 amp breaker on the generator is set and then be sure you have 120 v. on the second stage when the generator is running.

Dirk
Yep, that's how mine is wired.

__________________
Greg & Lynn
'03 33V Itasca Suncruiser / Workhorse Chassis
Jeep GC Overland in Tow
  Reply With Quote
   
Reply

Tags
compressor, generator


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Remote generator start not working, please help ShapeShifter Monaco Owner's Forum 18 11-23-2010 01:47 PM
Running the generator while on shore power? Magumba Winnebago Industries Owner's Forum 9 01-14-2010 08:03 PM
Onan Generator Quits On Start With No Load Birddog Pilot Alpine Coach Forum 26 08-11-2008 10:49 AM
Generator only putting out a few volts AC TallPaul RV Systems & Appliances 7 12-25-2007 02:57 PM
Generator Coolant Level OldForester Alpine Coach Forum 8 10-25-2007 05:56 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 09:30 PM.