Old 03-02-2008, 01:34 PM   #1
SteveG is offline
Senior Member
SteveG's Avatar
Join Date: Sep 2006
Location: Florida
Posts: 358
Another lesson learned! We registered at the KOA camp in Stark, Fl requesting 50 amps. We had an early afternoon appointment so had to hustle to get our 2004 36G Journey set up. So instead of checking the one panel after I initially plugged in and the Surge Guard activated power, I completed the setup and then noticed that the One Panel read 30 amps.

So I went to the office and asked the fellow who registered us if he would check our power for a problem and he turned to another guy who said, "You must have a Winnebago with a PowerLine panel?" He then went on to explain that the site I was on was wired for 50 amps with a single leg (phase). He said that RV's without PowerLine, such as a Prevost, have no problem with this single leg 50 amp setup.

Having recently read a post about incorrectly wired electrical service, I protested. He said their electrical installation passed electrical inspections and used #4 aluminum wire so the wire was designed to carry 50 amps. He offered to move us to a site with two leg power but by then we were out of time so we stayed put.

Since this was a good learning opportunity I used Don's advice from his 06/21/07 post in how to measure for 220V which would be available if two legs were used to provide 50 amps service vs. 110V if only one leg is provided. The check is easy enough. To use Don's words, "Take a volt meter and check the voltage across the 2 hot terminals in the receptacle. If it reads 220V its OK; if it reads 0 volt it's not wired correctly." And zero volts is what it measured.

Don also explained the potential problem of a single leg being used for a 50 amp service. "When the 50A service is wired incorrectly with both hots coming from the same leg (phase) from the panel, this is actually a dangerous condition which can overrate the neutral wire, as the two hots amperage will be additive to the neutral wire, and you will over-current the neutral and possibly cause it to overheat, melt and other bad things.'

So I think I have to conclude that the KOA design must have accounted for the additive amperage? Since the PowerLine panel is designed to turn on or turn off its load shedding capacity based on the presence of 220V, the design assumes that an 110V circuit would be designed as 30 amps. It also seems to me that the PowerLine panel protects the Park owner from themselves?

So next time I register at an RV Park I am going to ask the question, "Does the 50 amp circuit have a single or double leg?" Might get some interesting responses...

__________________
SteveG

'10 Phaeton 36 QSH-
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-02-2008, 01:34 PM   #2
SteveG is offline
Senior Member
SteveG's Avatar
Join Date: Sep 2006
Location: Florida
Posts: 358
Another lesson learned! We registered at the KOA camp in Stark, Fl requesting 50 amps. We had an early afternoon appointment so had to hustle to get our 2004 36G Journey set up. So instead of checking the one panel after I initially plugged in and the Surge Guard activated power, I completed the setup and then noticed that the One Panel read 30 amps.

So I went to the office and asked the fellow who registered us if he would check our power for a problem and he turned to another guy who said, "You must have a Winnebago with a PowerLine panel?" He then went on to explain that the site I was on was wired for 50 amps with a single leg (phase). He said that RV's without PowerLine, such as a Prevost, have no problem with this single leg 50 amp setup.

Having recently read a post about incorrectly wired electrical service, I protested. He said their electrical installation passed electrical inspections and used #4 aluminum wire so the wire was designed to carry 50 amps. He offered to move us to a site with two leg power but by then we were out of time so we stayed put.

Since this was a good learning opportunity I used Don's advice from his 06/21/07 post in how to measure for 220V which would be available if two legs were used to provide 50 amps service vs. 110V if only one leg is provided. The check is easy enough. To use Don's words, "Take a volt meter and check the voltage across the 2 hot terminals in the receptacle. If it reads 220V its OK; if it reads 0 volt it's not wired correctly." And zero volts is what it measured.

Don also explained the potential problem of a single leg being used for a 50 amp service. "When the 50A service is wired incorrectly with both hots coming from the same leg (phase) from the panel, this is actually a dangerous condition which can overrate the neutral wire, as the two hots amperage will be additive to the neutral wire, and you will over-current the neutral and possibly cause it to overheat, melt and other bad things.'

So I think I have to conclude that the KOA design must have accounted for the additive amperage? Since the PowerLine panel is designed to turn on or turn off its load shedding capacity based on the presence of 220V, the design assumes that an 110V circuit would be designed as 30 amps. It also seems to me that the PowerLine panel protects the Park owner from themselves?

So next time I register at an RV Park I am going to ask the question, "Does the 50 amp circuit have a single or double leg?" Might get some interesting responses...

__________________
SteveG

'10 Phaeton 36 QSH-
  Reply With Quote
   
Old 03-02-2008, 02:24 PM   #3
Hitchhiker is offline
Community Administrator
Hitchhiker's Avatar


Appalachian Campers
Join Date: Jan 2000
Location: Buladean, NC
Posts: 8,154
Actually, with a CG wired in that manner, you'll only have available half of the amount of power as you would have if it were wired as a conventional two leg circuit and may be at risk of tripping the CG's 50 amp breaker. For example, on my trailer, I have two heat pumps and each will draw about 16 amps on separate legs when running. My refrigerator will draw about 10 amps, the electric water heater draws another 10 or 11 amps. If we run an electric coffee pot and maybe turn on the microwave... I think you can see where I'm going with this.

I could easily be drawing 50, 60, or more amps and that single circuit wiring just isn't going to handle the loads. I have my doubts that it was actually passed by a competent, licensed building inspector who wasn't biased in favor of the CG.
__________________
'11 GMC Acadia SLT AWD
'11 GMC Sierra 1500 4x4 Extended Cab
  Reply With Quote
   
Old 03-02-2008, 02:38 PM   #4
DriVer is online now
iRV2 Marketing
DriVer's Avatar


Winnebago Owners Club
Workhorse Chassis Owner
Coastal Campers
Carolina Campers
Join Date: Jan 2000
Location: Conway, SC
Posts: 20,557
Blog Entries: 66
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by SteveG:
Another lesson learned! We registered at the KOA camp in Stark, Fl requesting 50 amps. </div></BLOCKQUOTE>Interesting! We've camped there several times in the past. I run a 50A Surge Guard and if it trips shut I usually feel comfortable with the power that I have.

I'll be sure to keep an eye on that if I camp there again. We did find a nice campground up on the 295 loop West of Jacksonville, Flamingo Lake.

Nice pull throughs and all new service equipment on unique looking pedestals that almost look like pagodas.
  Reply With Quote
   
Old 03-02-2008, 03:29 PM   #5
Hillbilly2 is offline
Senior Member
Join Date: Dec 2007
Location: Blairsville,GA
Posts: 257
Hitchhiker, you are incorrect on the assumtion that you will have only half the power with that setup, the breaker only "sees" current, not voltage. You still can have 50 amps flowing on each leg, but you will have 100 amps flowing on the neutral, which is the dangerous part in which the wire would overheat. The exception to this is if they are useing a single pole breaker and jumpering the hot over to the other side of the receptacle. The only reason that I can think of why they only have 120 volts available is they ran three conductor wire instead of four conductor to the pedestal. Usually a larger feeder cable is run through the campground (200-400 amp capacity) then is split off at each pedestal, reduced down to the needed ampacity. As for inspections, unless its just obvious, most inspectors don't have the time or are unwilling to look at the installation that close. The Power Line One panel correctly detects this condition, and keeps the wiring from being overheated.
__________________
  Reply With Quote
   
Old 03-02-2008, 03:51 PM   #6
Gary RVRoamer is offline
Community Moderator
Gary RVRoamer's Avatar


Fleetwood Owners Club
Freightliner Owners Club
Florida Cooters Club
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 9,573
If you go to enough different places and check the wiring, you will find most every possible combination on a 50A receptacle. I've seen 220V with as little as 40A or 30A per leg and I've seen 30, 50 or 50A @ 120V feeding the two hots from a single source. And I've seen a 30A and a 20A masquerading as a 50A by feeding one hot from each (just like the "cheater boxes" do when you want 50 and only have a 30A/20A hookup). That's actually not too bad - most everything works fine and there is no overload on the neutral.

My American Tradition with its Smart Energy Mgmt System will read the power situation just like the Winnebago does, reporting it as a 30A hook-up and managing the load to match.
__________________
Gary Brinck
2004 American Tradition; 2007 GMC Acadia
Homebase in the Ocala Nat'l Forest near Ocala, FL
  Reply With Quote
   
Old 03-02-2008, 04:15 PM   #7
John_Canfield is offline
Senior Member
John_Canfield's Avatar
Join Date: Jan 2005
Location: Back at the ranch
Posts: 2,540
I've seen just about everything like Gary in the above post (including an RV park in Alaska where the power was supplied by a large generator with a varying line frequency), but only one time in 30K miles of camping I found a 50 amp receptacle obviously wired wrong where there was only 30 amp indicated by my EMS.

Ironically it was near Gary's home base at Salt Springs!

Low voltage and low current are so common it's not even worth talking about
__________________
--John

2005 Horizon 40AD, 2005 Jeep Liberty CRD
  Reply With Quote
   
Old 03-02-2008, 06:00 PM   #8
Harry B is offline
Senior Member
Harry B's Avatar


Join Date: May 2006
Location: Central Florida
Posts: 620
Steve,

A single phase 50 amp service can be a legal configuration. However, if the EMS only sees one leg powered, it functions as if you have 30 amp service available and will shed loads to not exceed 30 amps as designed.

This only means that you are limited to drawing 30 amps of power on a circuit capable of supplying 50 amps. (saves on the electric bills for the campings).

You need both legs powered, to have the EMS indicate that you have 50 amps of service available, which if wired as such really means you have 100 amps available, (50 amps via each leg). Our coaches use each leg for 120 VAC at 2x 50 amps=100 amps and not 240 VAC at 50 amps, which is how 50 amp dual phase wiring is typically used. This is just something unique due to the wiring of motor homes.

A good indicator if wired properly or not would to determine if the circuit breaker at the hookup pedestal is a 50 amp single gang or 50 amp dual gang breaker. If it is a single gang breaker and it has the correct wire size feeding it, it is wired properly. On the other hand if you have a dual gang breaker and only a single leg powered, you have a problem.

I am just not sure if electrical code requires a different plug for single phase 50 amp service or not.
__________________
Harry
2005 Itasca Horizon 40KD
2006 Honda CR-V
  Reply With Quote
   
Old 03-02-2008, 06:13 PM   #9
Hillbilly2 is offline
Senior Member
Join Date: Dec 2007
Location: Blairsville,GA
Posts: 257
Actually it is not considered "Dual Phase" even if it's derived from a three phase system. It is still single phase even with both "hots" present. There is a thing called two phase, but it is as rare as hens teeth, and has not been used in this country for a long time. Most rural campgrounds are single phase 120/240. Yes, there are some real creative power systems out there!
__________________
  Reply With Quote
   
Old 03-03-2008, 05:09 AM   #10
Pusherman is offline
Senior Member
Pusherman's Avatar


Commercial Member
Join Date: Oct 2006
Location: Rochester NY
Posts: 1,825
Assuming the KOA in question ran 2 hot lines to each side of the RV receptacle, but both lines ran to a single 50A breaker (single pole) the setup would be 'safe' but I'm not sure it's legal. In this case, the amperage would be limited to 50A max, which would not overrate the neutral line.

The One-Place panel reads voltage to determine whether it's a 50A or 30A service. If it reads 220V across both legs, then it allows 50A. In the case above, the device only senses 120V and limits to 30A usage by shutting down devices, as if it were plugged into a 120V 30A shore service.

When wired correctly, a 50A service is actually a 220V service, even though the motorhome only uses 120V devices, and yes, you have 100A load capacity in this situation. These services are always 'fused' with a 50A double pole breaker which guarantees you're getting power from both legs of the panel, which are 180d out of phase with each other, which cancels on the neutral amperage, thus not overrating the neutral line.
Note, this assumes the pedestal's source is truly 220V power from 2 separate legs of the main power supply.

The test I described in Steve's original post still applies.
__________________
Don Pophal -Caledonia RV Center - Rochester, NY
'07 Winnebago Journey 34H - CAT C7, Koni's, MCU's, SS Bell Crank
'07 HHR Toad, SMI AFO, Blue OX
  Reply With Quote
   
Old 03-03-2008, 04:01 PM   #11
SteveG is offline
Senior Member
SteveG's Avatar
Join Date: Sep 2006
Location: Florida
Posts: 358
We returned today from the KOA-Stark no worst for the wear and a lot better educated. Thanks to all for your replies. We watched the One Panel shed the loads as needed and we had a pleasant stay.

Since the Power Line One Panel protects our Motorhomes from a single phase wiring by limiting the amperage to 30 amps, what happens to the MHs that do not have the Power Line One Panel? As their current draws exceeds 30 amps possible exceeding 50 amps is the Motor Home at risk or just the camp wiring?
__________________
SteveG

'10 Phaeton 36 QSH-
  Reply With Quote
   
Old 03-03-2008, 04:51 PM   #12
Hillbilly2 is offline
Senior Member
Join Date: Dec 2007
Location: Blairsville,GA
Posts: 257
If the breaker at the pedestal is a single pole it will just trip, resulting in power loss to the MH. If it is a two pole, the power cord on the MH will start heating up, depending on the overall load. Prolonged overloading could damage the pedastal receptacle, plug on the cord and/or the distribution panel in the MH. Full load would likely be only temporary, most people would not have everything on at one time, at least not for an extended period of time.
__________________
  Reply With Quote
   
Old 03-03-2008, 09:20 PM   #13
Jackm is offline
Senior Member
Jackm's Avatar
Workhorse Chassis Owner
Join Date: Nov 2005
Posts: 621
Hillbilly2,

Your responses suggest that you know more about electrical systems than most. I hope you keep contributing to this forum. Thanks.

Jack
__________________
2004 Winnebago Brave 34D with the usual add-ons
  Reply With Quote
   
Old 03-05-2008, 05:19 AM   #14
SteveG is offline
Senior Member
SteveG's Avatar
Join Date: Sep 2006
Location: Florida
Posts: 358
Trying to understand the RV electrical system I found the following paragraph from Progresive Industries Surge Guard:

"RV wiring is different than the wiring found in homes. The neutral and ground wires are isolated in an RV. In a home they are tied together at the service panel. The reason, homes have a bonded ground system and RVs do not. Therefore never bond the neutral and ground together for any reason. This will create a ground fault condition and may result in electrical shock and/or fire hazard."

Why are home and RV power supply circuits designed differently?

__________________
SteveG

'10 Phaeton 36 QSH-
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Getting 50 amps to a 30 amp RV bjbkkb RV Systems & Appliances 5 03-15-2008 07:20 PM
110 electric power...15 amp circuit breakers Cocoa Loco RV Systems & Appliances 4 01-03-2007 05:48 AM
Factory overloading one leg of the 50 Amp circuit JavaJelly Newmar Owner's Forum 5 11-28-2006 11:20 AM
Max amps on 50 amp circuit? eandy MH-General Discussions & Problems 12 07-25-2006 10:51 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 07:25 PM.