Old 04-03-2006, 04:59 PM   #1
Matt1616 is offline
Junior Member
Join Date: Mar 2005
Location: Mars, PA
Posts: 26
Good evening,

I wanted to post a question to the forum. I have an 2003 Adventurer 35U and an gettign it ready for the first road trip of the new year.

I cranked the generator and noticed although it cranked right away it was not providing power the coaches electrical system. No lights come on at all on the Powerline Remote Display Panel co-located with the thermostat and tank guages.

I plugged into shore power and everything works fine. The Remote Display lights up just as it should and everything works.

My next check was keeping the shore power plugged in and starting the generator. The Poweline system detected that the generator was running and everything seemed to work normally.

SO I dug into my black Bag and pulled out the Powerline 2000 EMS Installation and Service Manual. It states under a descriotion of the system that there are 2 components
1.The Control Module which is housed in the standrad main distribution panel, a sheet metal enclosure with removeable front paneland
2.A Display Panel which is mounted to a wall or suitable surface remotely from the distribution panel.

I read the troubleshooting guide and determined the following from TroubleShooting step VIII

Problem - All load indicators do not light and GEN SET service indicator on the Remote Display does not light with the generator running
Remedy - Check for the presence of +12Vdc at Jumper J4 pin #8 on the Control Module.

So here is my Electronics 101 question. If I use a voltmeter and discover there is no +12Vdc at J4 pin #8 then what? What might prevent having +12Vdc at that particular pin. All of my +12Vdc breakers have been reset.

Any insight you can provide would be greatly appreciated.

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-03-2006, 04:59 PM   #2
Matt1616 is offline
Junior Member
Join Date: Mar 2005
Location: Mars, PA
Posts: 26
Good evening,

I wanted to post a question to the forum. I have an 2003 Adventurer 35U and an gettign it ready for the first road trip of the new year.

I cranked the generator and noticed although it cranked right away it was not providing power the coaches electrical system. No lights come on at all on the Powerline Remote Display Panel co-located with the thermostat and tank guages.

I plugged into shore power and everything works fine. The Remote Display lights up just as it should and everything works.

My next check was keeping the shore power plugged in and starting the generator. The Poweline system detected that the generator was running and everything seemed to work normally.

SO I dug into my black Bag and pulled out the Powerline 2000 EMS Installation and Service Manual. It states under a descriotion of the system that there are 2 components
1.The Control Module which is housed in the standrad main distribution panel, a sheet metal enclosure with removeable front paneland
2.A Display Panel which is mounted to a wall or suitable surface remotely from the distribution panel.

I read the troubleshooting guide and determined the following from TroubleShooting step VIII

Problem - All load indicators do not light and GEN SET service indicator on the Remote Display does not light with the generator running
Remedy - Check for the presence of +12Vdc at Jumper J4 pin #8 on the Control Module.

So here is my Electronics 101 question. If I use a voltmeter and discover there is no +12Vdc at J4 pin #8 then what? What might prevent having +12Vdc at that particular pin. All of my +12Vdc breakers have been reset.

Any insight you can provide would be greatly appreciated.

__________________
  Reply With Quote
   
Old 04-03-2006, 05:37 PM   #3
Ed Gardiser is offline
Senior Member
Ed Gardiser's Avatar
Join Date: Feb 2006
Posts: 137
I would believe the house batteries are dead or very low on charge.
Ed Gardiser
Escondido,Ca.
04 Vectra
87 Nissan PickUp
FMCA
__________________
  Reply With Quote
   
Old 04-03-2006, 05:52 PM   #4
Matt1616 is offline
Junior Member
Join Date: Mar 2005
Location: Mars, PA
Posts: 26
Ed,

thanks for your reply. The House batteries are showing a charge or 13.7 on the power panel and other onboard +12Vdc electrical appliances are working.

Could I be getting a false reading on the power panel and the house batteries are actually low?
__________________
  Reply With Quote
   
Old 04-03-2006, 05:55 PM   #5
Cruzer is offline
Moderator Emeritus
Cruzer's Avatar


Join Date: Oct 2002
Location: Sheboygan, WI
Posts: 2,566
The EMS gets it's 12 volt signal from the "B+" feed off the generator. This signal is the one that also runs the hourmeter and is supplied from the genset when it is running.

Based upon your description I'm going to take a guess at what happened. If you had no coach power when the genset was running then it wasn't putting out any AC power. But when you plugged into shore power you had power. Then when you started the genset the "Generator" LED on the panel lit but you still were running off of shore power?

The first thing I'd check is that the two circuit breakers on the genset haven't tripped. That would cause the above scenario. If the "generator" LED never lights, then I'd check the DC fuse in the genset that feeds the B+ wire. The third possibility is that the LED did light and the genset did puit out AC but the automatic transfer switch stuck and didn't switch over. Anyway, I'd check those things in that order.
__________________
Mark & Leann Quasius
2007 Allegro Bus 42QRP - Cummins 400 ISL
2012 Jeep Wrangler Unlimited - Rubicon
  Reply With Quote
   
Old 04-03-2006, 07:20 PM   #6
AFChap is offline
Senior Member
AFChap's Avatar


Winnebago Owners Club
Join Date: Aug 2002
Location: ...hopefully on the road!
Posts: 3,176
I had the same problem once on my coach ...the transfer switch had not functioned. I had heard of others have the transfer switch stick. I smacked the box in my power compartment with my hand, heard a loud "clack!", and then everything worked like it should, and no problems since...
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
'03 Winnebago UA 40e / '00 Honda Odyssey toad
  Reply With Quote
   
Old 04-04-2006, 02:52 AM   #7
troth is offline
Senior Member
troth's Avatar


Join Date: Aug 2003
Location: NE Ohio
Posts: 1,170
Matt1616, follow Cruzer's advice and report back to us. I suspect your coach is wired for 30A. When your generator is supplying power into the coach, your Powerline info center should switch automatically from the 30A LED to the 50A LED. (-Assuming your generator breakers are "on" and the transfer switch kicked over).
__________________
Last Brave 2004 34D
  Reply With Quote
   
Old 04-04-2006, 10:38 AM   #8
MrTransistor is offline
Senior Member
MrTransistor's Avatar
Join Date: Jan 2004
Location: Albuquerque, NM
Posts: 600
Hi Matt1616,
Transfer switch! If whacking it doesn't free a stuck contactor, take it apart and look for a loose or disconnected ˜fast-on' connector. See photo in my photo section. Normally, the two contactors are de-energized and allow either single phase 120VAC 30 Amp. (20 Amp.) or two phase 240VAC 50 Amp. power through to the PowerLine control unit. It's the PowerLine that detects 30 or 50 Amp. service.

The transfer switch energizes it's contactors when the generator is supplying power. A problem in the transfer switch which prevents the contactors from energizing prevents AC form reaching the PowerLine from the generator even though the light is lit on the PowerLine indicating generator is supplying power. Because the contactors are de-energized, shore power continues to pass to the PowerLine.

Been there, done that, on two coaches and decided to replace the transfer switch with a microprocessor controlled ESP intelligent transfer switch (also pictured) which has surge protection and also pre-qualifies the power connection before connecting the coach. I left the old switch in place, disconnected, as a fall back.

__________________
Have Fun!! Mark & Donalda 04 Horizon 40WD no TOW 90,900+ miles and counting
Triumph Bonneville & Susuki S40 on the back
  Reply With Quote
   
Old 04-12-2006, 04:35 PM   #9
Matt1616 is offline
Junior Member
Join Date: Mar 2005
Location: Mars, PA
Posts: 26
Finally got around to troubleshooting last weekend and Cruzer was spot on with his troubleshooting advice. It was the breaker on the Onan generator itself. I flipped the switch and everything was working just fine.

Thanks for all of the help. This community of Winnebago owners is just great!

__________________
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Powerline Mngt System will not read 50 Amp T Busch Winnebago Industries Owner's Forum 17 11-27-2009 12:01 PM
Energy Management System Bob O Winnebago Industries Owner's Forum 12 07-14-2008 02:55 PM
Need Urgent Help With Powerline System AdrianLee Winnebago Industries Owner's Forum 24 05-29-2006 10:05 AM
Energy Management System DancinCampers Winnebago Industries Owner's Forum 4 03-07-2006 09:17 AM
powerline system on 98 Chieftain head_west Winnebago Industries Owner's Forum 6 08-26-2005 05:34 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 07:34 PM.