Roof A/C Condensate Pumps

None of the 3 on my units are working since I have water pouring off my roof. I have visually inspected all 3 of them, and being in the commercial HVAC business for over 30 years I can tell you thats not much of a pump! LOL.

Anyway, I do not see any blockage up there so I wanted to check in with others and see where they have had trouble in the past on these?
__________________

__________________
Loyd
2014 Itasca Ellipse 42QD
loydt is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-20-2019, 10:50 AM   #2
Senior Member
 
Join Date: Jul 2018
Posts: 888
Quote:
Originally Posted by loydt View Post
None of the 3 on my units are working since I have water pouring off my roof. I have visually inspected all 3 of them, and being in the commercial HVAC business for over 30 years I can tell you thats not much of a pump! LOL.

Anyway, I do not see any blockage up there so I wanted to check in with others and see where they have had trouble in the past on these?
Never seen a condensate pump on a roof ac, mine just gravity drain through tubing to a point under the rear cap to the ground. If you do not have the tubing to the pan under the evaporator, it just goes out on the roof.
If your tubing is blocked, that could be the problem.
__________________

__________________
Foretravel tag axle 40 ft. 500 hp/1550 ft/lbs ism 1455 watts on the roof. 600 a/h's lithium down below.
jcussen is online now   Reply With Quote
Old 03-20-2019, 11:17 AM   #3
Senior Member
 
Mark D's Avatar
 
Join Date: Nov 2016
Posts: 638
Quote:
Originally Posted by jcussen View Post
Never seen a condensate pump on a roof ac, mine just gravity drain through tubing to a point under the rear cap to the ground. If you do not have the tubing to the pan under the evaporator, it just goes out on the roof.
If your tubing is blocked, that could be the problem.
We have three, they do go bad. Best thing to do is disconnect from the pump and blow into the line. If air passes it's not the line.

I had one checked by the AC guy and said it was locked up, not sure how they inspect.

They are also very easy to change. I have a spare.
__________________
2011 American Coach, American Eagle 45B with 650hp ISX on a Liberty (Mountain Master Chassis K3 Tag) with two Vizsla's and two cats.....
Mark D is offline   Reply With Quote
Old 03-20-2019, 11:47 AM   #4
Senior Member
 
Join Date: Jan 2009
Posts: 1,761
I too had never heard of an RV rooftop unit that utilized a condensate pump. Just looked and sure enough, at least one manufacturer does. I would be interested in knowing why a manufacturer would design a unit like this in the first place when gravity should work just fine.

On the OP's issue, it's hard to believe that all three units have a high condensate level/overflow problem at the same time. Or do all three units empty to a common pan housing the condensate pump? I wouldn't think that a single unit with the problem would cause all three units to stop working unless this was the case.

How bout this? Since water is shedding off the roof, the compressor must be running. I wonder if the something could be going on with the reversing valve(s). Again, not likely all three at the same time. There is more than one thermostat, right?

Sorry I can't help any. I am curious to see what you find though, as this is something I haven't run across with rooftop units..
__________________
03 Itasca Sunova, Workhorse P32 with the 8.1 and 4L85-E
Mudfrog is offline   Reply With Quote
Old 03-20-2019, 12:32 PM   #5
Senior Member
 
Join Date: Jul 2018
Posts: 888
Quote:
Originally Posted by Mark D View Post
We have three, they do go bad. Best thing to do is disconnect from the pump and blow into the line. If air passes it's not the line.

I had one checked by the AC guy and said it was locked up, not sure how they inspect.

They are also very easy to change. I have a spare.
Do your pumps have to move the condensate up to empty out the tray? Just trying to visualize it.
__________________
Foretravel tag axle 40 ft. 500 hp/1550 ft/lbs ism 1455 watts on the roof. 600 a/h's lithium down below.
jcussen is online now   Reply With Quote
Old 03-20-2019, 07:22 PM   #6
Junior Member
 
Join Date: Feb 2014
Posts: 26
Quote:
Originally Posted by loydt View Post
None of the 3 on my units are working since I have water pouring off my roof. I have visually inspected all 3 of them, and being in the commercial HVAC business for over 30 years I can tell you thats not much of a pump! LOL.

Anyway, I do not see any blockage up there so I wanted to check in with others and see where they have had trouble in the past on these?
Check the end covers (look like a perforated piece of tubing) on the condensate drain lines under the rear cap....they just pull off and can get clogged with crud over time but are needed to keep out the wasps and mud dauber when coach in storage. (The ones on my 14 Journey when new were full of styrofoam bits from roof insulation and one pickup line to the condensate pump was kinked due to poor ac install at the factory.). Have not had a problem with condensate pumps on mine since I corrected those issues.

Would seem very odd for all three to go bad at same time....just a thought - book does say water will run off on roof when using heat pumps vice AC....?
__________________
2014 Journey 36M/2014 Ford Edge
Demco Baseplate/Blue Ox Towbar
SMI Air Force One Toad braking
Rmedad is offline   Reply With Quote
Old 03-21-2019, 06:25 AM   #7
Senior Member
 
Mark D's Avatar
 
Join Date: Nov 2016
Posts: 638
Quote:
Originally Posted by jcussen View Post
Do your pumps have to move the condensate up to empty out the tray? Just trying to visualize it.
No more than a few inches. It's a small pump that sits in a tray under the coil. Not sure if it runs constantly or if there is a level switch. But it lifts the condensation a few inches up in a 3/8" tube and empties into a 3/4" line and it's all gravity from there. I have seen several that dump into the engine bay. All three of mine come out just under the wet bay.

It does make life easier, no water dripping off the coach and you can tell which one us running by looking at the tube.
__________________
2011 American Coach, American Eagle 45B with 650hp ISX on a Liberty (Mountain Master Chassis K3 Tag) with two Vizsla's and two cats.....
Mark D is offline   Reply With Quote
Old 03-21-2019, 07:00 AM   #8
Senior Member
 
grtharris's Avatar


 
Winnebago Owners Club
Join Date: Apr 2003
Location: Skiatook, OK
Posts: 2,392
Are you cooling or heating? The condensate pump only works in the cooling mode. You can get water on the roof when in the heating mode.
__________________
Grant & Pat
2014 Adventurer 35P
2012 Jeep Wrangler Rubicon
grtharris is offline   Reply With Quote
Old 03-21-2019, 07:08 AM   #9
Member
 
loydt's Avatar
 
Join Date: Nov 2010
Location: Cornelius, NC
Posts: 51
Cooling mode. I was down in the Florida Keys when I noticed it. I checked all the lines on the roof and I also cleaned out the screens on the bottom of the lines near rear engine bay. I am going to blow out the lines just to be safe for the areas I cannot see. But I suspect these little cheap pumps have failed.

My previous coach (Monaco) worked the same way, but they were able to gravity drain and pumps were not needed.
__________________
Loyd
2014 Itasca Ellipse 42QD
loydt is offline   Reply With Quote
Old 03-21-2019, 08:14 AM   #10
Senior Member
 
Join Date: Jul 2018
Posts: 888
Quote:
Originally Posted by Mark D View Post
No more than a few inches. It's a small pump that sits in a tray under the coil. Not sure if it runs constantly or if there is a level switch. But it lifts the condensation a few inches up in a 3/8" tube and empties into a 3/4" line and it's all gravity from there. I have seen several that dump into the engine bay. All three of mine come out just under the wet bay.

It does make life easier, no water dripping off the coach and you can tell which one us running by looking at the tube.
Thanks, guess my units are different. The pans are slightly above roof level, so drain tubing is on the roof, and joins the units, then drops down over the engine compartment and dumps under engine radiator. When camping, I put the dogs water dish under it, keeps it full of cool water.
__________________
Foretravel tag axle 40 ft. 500 hp/1550 ft/lbs ism 1455 watts on the roof. 600 a/h's lithium down below.
jcussen is online now   Reply With Quote
Old 03-21-2019, 10:17 AM   #11
Senior Member
 
DancinCampers's Avatar
 
Join Date: Nov 2004
Location: On the Road Westward
Posts: 1,316
I had to replace mine on the front unit several years ago. The motor bronze bearings froze up.



I clean out my lines by using a wet/dry vac on the tubes behind the cap, after removing the bug shield.


Due to a design flaw, IMHO, these pumps run whenever the compressor runs, cool and heat mode (at least on my units). Verified by emails to Winny and Airxcel.


These are small pancake motors and pump similar to ones used in evap coolers, just smaller. I think my replacement was about $60.
__________________

__________________
Dan & Sharon (Kasey-Our Yorkie Puppy RIP 9Jan05-26Jul17) On the Road (2012 Journey 36M, 2006 Jeep Liberty)
USN-Ret ('65-'93) Fulltimers, Class of 2012
DancinCampers is offline   Reply With Quote
Reply

Tags
roof



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
REMCO Pumps discontinuing Lube Pumps gregd Toads and Motorhome Related Towing 6 07-21-2015 07:28 PM
Roof Top AC with under Coach Condensate Drains Yoda2405 Winnebago Industries Owner's Forum 3 06-17-2014 04:05 PM
Roof Air Condensate Control ? Coconut iRV2.com General Discussion 3 02-24-2013 07:50 AM
AC Condensate Drain Dagwood National RV Owner's Forum 9 07-25-2010 09:09 PM
Roof Air Conditioner Condensate joelsr Monaco Owner's Forum 18 08-26-2008 03:55 PM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 08:22 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.