Turning off House Batteries kills 50amp!?!
Old 06-23-2010, 08:16 PM   #1
RickO is offline
Community Moderator
RickO's Avatar


Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 5,151
I was doing my battery maintenance today and decided to remove and clean all of the cables from the battery terminals. I disconnected the house batteries first via the "Aux Battery Disconnect" switch but as soon as I threw the switch, it killed the 50amp service to the coach. I expected the inverter to keep even the 12v running but no dice. It went dead along with the 50amp.

My Powerline EMS has been acting funny the past few months... it doesn't protect 20/30 amp circuits by properly sheding loads, the load lights don't even light...and I'm going to be visiting Forrest City after the GNR to have it looked at with a few other things, but this surprised me.

Anybody have any ideas? Am I missing something silly? I also tried to leave the Aux Bat Switch in the on position but when I disconnected the cable everything went dead again.

__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-23-2010, 11:21 PM   #2
makemecrazy is offline
Junior Member
Join Date: Jun 2010
Posts: 7
Mine does the same thing. Surprised me at first too. It's sort of like pulling the main breaker in your home.

__________________
  Reply With Quote
   
Old 06-24-2010, 08:32 AM   #3
AFChap is offline
Senior Member
AFChap's Avatar


Winnebago Owners Club
Join Date: Aug 2002
Location: ...hopefully on the road!
Posts: 3,176
Mine certainly doesn't work that way. I use the battery disconnect switch to disconnect 12v item every time I run the equalization cycle on the house batteries. But perhaps something is different about newer models... I would check it with Winnie Owner Relations to make sure that is right.
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
'03 Winnebago UA 40e / '00 Honda Odyssey toad
  Reply With Quote
   
Old 08-10-2010, 07:58 AM   #4
pameridan04 is offline
Senior Member
pameridan04's Avatar
Mid Atlantic Campers
Join Date: Oct 2007
Location: Allentown, PA
Posts: 367
Ricko:

Mine does the same thing. I was camping a few weeks ago. I hooked up to 50 amp service, Aux switch was on.

I said I don't need this now that I am hooked up, turned off the Aux Battery switch and lost all power.

It seems if you want power to the coach, the Aux Power Switch has to be on.

I also find that I don't see any amp read outs in 50 amp mode on pannel. Just says 50 amp.??

Regards Jim P.
__________________
Meridian 2004 36G DP
2010 Jeep Sahara Unlimited
Two HD's for company
  Reply With Quote
   
Old 08-10-2010, 08:30 AM   #5
RickO is offline
Community Moderator
RickO's Avatar


Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 5,151
Hi Jim P... I still haven't gotten around to calling Winnie to check on the proper operation of the chassis battery switch but I'm pretty sure it is normal not to see any amp use on your panel when hooked up to 50 amp. I never really understood why but that's the way it is for most of us I believe. If you want to know how much current you're drawing you can switch to generator temporarily.
__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
  Reply With Quote
   
Old 08-10-2010, 10:02 AM   #6
AFChap is offline
Senior Member
AFChap's Avatar


Winnebago Owners Club
Join Date: Aug 2002
Location: ...hopefully on the road!
Posts: 3,176
It is called "Aux Battery DISCONNECT Switch" because it disconnects the house battery bank from all 12v loads...lights, radios, thermostats, refer control board, etc. It normally will NOT disconnect loads from the chassis battery bank. And it does not disconnect shore power from the coach. There is still power coming in.

The load center will not show amps used when on 50a shore power. I guess that is because they figure there is no way you are going to use more than the 100a you have available on the two power legs. You only see amps used when using 20a, 30a, or generator. ...and do you know how many amps your generator could potentially put out so you know you are pushing the limit? You have to do some math ... i.e. my Onan 7500 has a potential of apx 62.5a ...watts / voltage = amps.
__________________
Paul (KE5LXU) ...was fulltimin', now parttimin'
'03 Winnebago UA 40e / '00 Honda Odyssey toad
  Reply With Quote
   
Old 08-10-2010, 10:59 AM   #7
RickO is offline
Community Moderator
RickO's Avatar


Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 5,151
Right you are Paul but their choice of wording has always made me smile because it starts to feel like a "who's on first" skit. Both my Aux Battery Disconnect switch and Chassis Battery Disconnect switch have to be "on" in order to NOT disconnect the batteries.

Maybe it's twisted reasoning but it just seems to me if a switch is labeled "disconnect"... when one turns it "on"... something should get disconnected. Instead we turn "off" the disconnect switch to disconnect the batteries.

Now, was I don't know on second?
__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
  Reply With Quote
   
Old 08-10-2010, 11:01 AM   #8
RJay is offline
Community Administrator
RJay's Avatar


Newmar Owners Club
Join Date: Jan 2010
Posts: 4,593
Rick,
I think what going on has to do with the EMS. The EMS has normally open relays that control the circuits connected to it. When connected to a 50 amp service all the relays are closed allowing the circuits to be fed from the 50 amp service. But there are a couple of 12VDC relays that control low voltage applications such as thermostats and when battery voltage is lost these relays will open. Did you have to reset the the main breakers at the AC panel?
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
  Reply With Quote
   
Old 08-10-2010, 11:37 AM   #9
cyko is offline
Senior Member
Join Date: Feb 2002
Location: Ames, IA, USA
Posts: 126
I've never heard it explained this way, but I think the reason that there is no current display when hooked to 50 amps is that the current used is divided between two different 120-volt lines, and it would require more instrumentation to "add up" the total. The situation is complicated by the fact that the two currents are out-of-phase, so they don't add up in a simple manner. When hooked to 30 amps, the two lines are driven in parallel, and the total current can be measured at the source.
__________________
What do you do when you just can't do what you do when you do what you do?

*****************************
  Reply With Quote
   
Old 08-10-2010, 11:41 AM   #10
RickO is offline
Community Moderator
RickO's Avatar


Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 5,151
Quote:
Originally Posted by RJay View Post
Rick,
I think what going on has to do with the EMS. The EMS has normally open relays that control the circuits connected to it. When connected to a 50 amp service all the relays are closed allowing the circuits to be fed from the 50 amp service. But there are a couple of 12VDC relays that control low voltage applications such as thermostats and when battery voltage is lost these relays will open. Did you have to reset the the main breakers at the AC panel?
Thanks RJay, this makes sense. I don't think I had to reset the breakers but this happened six weeks ago and digging deeper hasn't made it's way up my priority list yet.
__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
  Reply With Quote
   
Old 08-10-2010, 11:55 AM   #11
RJay is offline
Community Administrator
RJay's Avatar


Newmar Owners Club
Join Date: Jan 2010
Posts: 4,593
Quote:
Originally Posted by cyko View Post
I've never heard it explained this way, but I think the reason that there is no current display when hooked to 50 amps is that the current used is divided between two different 120-volt lines, and it would require more instrumentation to "add up" the total. The situation is complicated by the fact that the two currents are out-of-phase, so they don't add up in a simple manner. When hooked to 30 amps, the two lines are driven in parallel, and the total current can be measured at the source.
cyko,
When connected to 50 amp service the EMS goes to sleep, it doesn't measure anything so there is no current reading and all and all the circuits in the service panel are energized. For a 30 amp service, since the EMS current transformer is connect to the neutral, the load current of each connected load is “learned” as it is energized by the EMS and the EMS will connect the appropriate load based on how much current is available from the total load seen by the neutral.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
  Reply With Quote
   
Old 08-10-2010, 12:17 PM   #12
azloafer is offline
Senior Member
azloafer's Avatar
Winnebago Owners Club
Join Date: Oct 2009
Posts: 1,169
Quote:
Originally Posted by pameridan04 View Post
Ricko:

Mine does the same thing. I was camping a few weeks ago. I hooked up to 50 amp service, Aux switch was on.

I said I don't need this now that I am hooked up, turned off the Aux Battery switch and lost all power.

It seems if you want power to the coach, the Aux Power Switch has to be on.

I also find that I don't see any amp read outs in 50 amp mode on panel. Just says 50 amp.??

Regards Jim P.
I only get an amp readout when my generator is on. Shore power just lights up the 50 amp light. I wish it did show the amps when on shore power, but I am told that this is normal. Joe
__________________
2008 Itasca Latitude 39W. Cummins ISB 6.7 Turbo 340HP. Allison 6 Speed. Freightliner XCS. Michelin XRV 255/80R 22.5 LRG. SuperSteer MCU. Safe-T-Plus.
  Reply With Quote
   
Old 08-10-2010, 05:59 PM   #13
pdq_bc is offline
Senior Member
pdq_bc's Avatar
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Aug 2009
Location: where ever we're parked
Posts: 341
Quote:
Originally Posted by pameridan04 View Post
...I also find that I don't see any amp read outs in 50 amp mode on pannel. Just says 50 amp.??.....

Hi Jim:

i have had direct communication with the manufacturer on this - for i wanted to know too!
below is a cut & paste of the reply.

regards, pdq
(peter)


If your Powerline unit is p/n 00-00740-xxx then we connected to 50 Amp
service the remote current display area is disabled.
If your part number is 00-00911-xxx and you are connected to 50 Amp service, the remote current display area is disabled as well.
Prior version of the EMS would behave the same, meaning the remote display would be disabled.
__________________
peter & larry
itasca 2009 suncruiser 35P ~ pontiac 2009 G5
we're here... http://map.datastormusers.com/user1.cfm?user=12260
  Reply With Quote
   
Old 08-10-2010, 08:13 PM   #14
RickO is offline
Community Moderator
RickO's Avatar


Join Date: Jan 2007
Location: Litchfield Park, Arizona
Posts: 5,151
Doesn't seem to be much question that the EMS is working as designed when not showing current draw when hooked to 50 amp shore power. I think RJay's speculation was "why" it can't show the draw.

__________________
Rick, Nancy, Peanut & Lola our Westie Dogs & Bailey the Sheltie.

2007 Itasca Ellipse 40FD
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How many House Batteries in '05 Kountry Star Rmellen Newmar Owner's Forum 8 11-30-2009 06:57 AM
2002 Allegro Bus--I need some help with house batteries! mrsbongo1 Tiffin Motorhomes Owners Forum 1 11-07-2009 02:14 PM
House batteries not charging while driving bobpie Winnebago Industries Owner's Forum 14 11-01-2009 06:12 PM
house batteries?? txbeachfolks Winnebago Industries Owner's Forum 3 06-12-2008 01:02 PM
House Batteries RayT MH-General Discussions & Problems 5 09-12-2007 08:08 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 02:08 AM.