Several items to consider:
The t-stat has a one minute delay built in when second stage cooling is called for.
The PC board momentarily turns off the outdoor blower motor when second compressor is started.
I would think that tieing together the first & second compressor, y1 & Y2, should work on 50A, but would cause problems on 30A.
My choice would be to disable the reversing valves with a double pole single throw switch (115vac), then switch the y1 to w, with a single pole double throw switch (12v). This would force the PC board to thinking it was in heat pump mode, but without the reversing valves operating.
In heat pump mode, all actions are accomplished by the pc board, and both compressors always operate.
Also, you would need to reverse the indoor and outdoor coil thermisters.
I am not sure if you could add the switch to the reversing valves without opening up the unit.