Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
 


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 03-22-2017, 01:30 PM   #1
Winnie-Wise
 
Join Date: Jul 2010
Posts: 343
What I thought was a Onan Generator problem...

What I thought was a Onan Generator problem has now led to something else...

Recap: My generator would not start and threw a Fault Code 27; I discovered that if I turned off the 30 amp breaker at the generator, the generator would start and run, but didn't supply 110v power since the generator breaker was turned off. Would instantly shut-down once the 30 amp breaker was turned back on.) The local repair shop discovered that there is a breaker panel (total of six breakers) under the refrigerator and that when one was turned off, the generator would start, run and produce power properly. They mistakenly told me it was the refrigerator circuit and that I needed a repair shop that could work on coach wiring and appliances. Their thought was that something with the refrigerator was putting too big a load on the circuit. (But the breaker has NEVER tripped.)

Looking through Winnebago wiring diagrams that I can't follow, I discovered that the 'bad' breaker is actually labeled as 'Recps 2' and seems to only power four 110v receptacles, one at the dinette and three in the bedroom. Just by chance, when I took the motorhome back to storage last night and before I discovered that it wasn't the 'refrigerator' circuit, I had checked around to see what was dead in the coach and came up with the exact same receptacles. None have anything plugged into them and only the one at the dinette do we ever even use, for charging iPads and using MacBook Pro's. While I had the generator running, I tried the microwave and turned on the A/C; both worked as they should and amperage-used showed up on the electrical monitor panel. Turned off the microwave and A/C and when I flipped the problem-breaker to 'on', the generator immediately shut-down.

Since Workhorse won't work on coach wiring or appliances, they gave me a couple of referrals, one of which I called. I did mistakenly tell him the problem seemed to be the refrigerator circuit, which I now know not to be correct. He insisted that it couldn't be the refrigerator as it only draws 300 watts, but I pointed out that whatever it was, it wasn't tripping a breaker. He then told me that it had to be the generator but I told him that I had already verified that the generator would start, run and supply power as long as I had the refrigerator breaker turned off. (Of course, it's actually the Recps 2 breaker.) He then stated it had to be a battery issue, but I told him I replaced all the batteries just a few months ago and both the engine and generator would turn over instantly. He then said it must be some sort of problem with the 12v wiring going to the generator but I pointed out again that it will start and run if the problem-breaker is turned off. He then told me I needed to plug into shore power and when I asked for an explanation of what that would tell me, he got pretty upset with me and essentially ended the conversation. I don't understand what the shore-power connection would tell me, since the generator wouldn't be running and couldn't shut down.

My father-in-law said I should start by disconnecting one wire on the Recps 2 breaker and then see if the generator will start and power the coach, but from there, I'm not sure what else I could check. Any ideas on what else I could check out?

Thank-you. -RT
Attached Thumbnails
Click image for larger version

Name:	MH Breaker Panel.jpg
Views:	314
Size:	319.3 KB
ID:	155692  
__________________
Ricardo Tegarini
2005 Itasca Sunova
Workhorse Chassis W20
RTegarini is offline   Reply With Quote
Old 03-22-2017, 01:36 PM   #2
Winnebago Camper
 
Join Date: Sep 2014
Posts: 37
Shorepower and genset both supply your AC power.

If everything works perfectly on shorepower with all the breakers on then it would point to genset or the wiring from genset, etc.
__________________
1998 Tioga Class C
400 amp/hrs solar, Trimetric
Retire 2020 GLW
okcnewbie is offline   Reply With Quote
Old 03-22-2017, 02:02 PM   #3
Winnebago Watcher
 
Join Date: Feb 2014
Posts: 1
Nice write up on your problem. I think you have it narrowed down to the 4 outlets on the recep2 breaker. Since the outlets are accessible, I would shut off all power, remove the face plates from each of the receptacles and look inside with a flashlight. If you see anything "burned", then just replace the offending outlet. If you have a multi-meter, check between the hot/black wire on the outlet and the ground/green wire to look for a short circuit. Do the same between the black and neutral/white wire. You should see infinite resistance, these wires should not be connected to each other in the wall. If you see any continuity between the black and white, or the black and green that means you have a short circuit. The only problem then is to find the short. The only way to do that is by inspecting the outlets one by one. Hope this helps.

Mike
7riders is offline   Reply With Quote
Old 03-22-2017, 02:08 PM   #4
Winnebago Owner
 
Podivin's Avatar
 
Join Date: Dec 2015
Location: Jacksonville, Fl
Posts: 225
Quote:
Originally Posted by okcnewbie View Post
Shorepower and genset both supply your AC power.

If everything works perfectly on shorepower with all the breakers on then it would point to genset or the wiring from genset, etc.
Agreed, plug in shore power to see if the problem persists.
If yes then the problem is either the Recps2 breaker itself or something downstream of it.

I'd say to plug in the shore power the Recps2 OFF, check some things to see if they work and THEN turn Recps2 on. If the breaker trips don't fight it or try to turn it back on, just start looking for loose wires. Pull each outlet and check for loose connections. If one of the four outlets is GFCI then start with that one.
__________________
2013 Winnebago Sightseer 36V
Podivin is offline   Reply With Quote
Old 03-22-2017, 02:16 PM   #5
Winnie-Wise
 
Join Date: Jul 2010
Posts: 343
Wow! Thank-you everyone for your replies. RV storage is closed today but hopefully can try some of the suggestions posted. I'm anxious to see if I can figure this out... -RT
__________________
Ricardo Tegarini
2005 Itasca Sunova
Workhorse Chassis W20
RTegarini is offline   Reply With Quote
Old 03-22-2017, 05:43 PM   #6
Winnebago Owner
 
Join Date: Jul 2005
Location: Carmel, Indiana
Posts: 135
I would take the breaker panel cover off and see if a wire is somehow shorting out to one side of the Recp2 breaker or that the wires on the breaker itself are loose? I would also think about replacing that breaker itself as well. It sounds from your write up that everything really works, but something is causing a dead short in that circuit which the generator somehow senses and shuts itself off. You may also want to check the wire connections for each of the four outlets on that circuit as well.
__________________
Clayton
2006 Winnebago Journey 36G
Cat 350
CWHTRAINS is offline   Reply With Quote
Old 03-22-2017, 08:30 PM   #7
Winnie-Wise
 
Join Date: Jul 2010
Posts: 343
Quote:
Originally Posted by CWHTRAINS View Post
I would take the breaker panel cover off and see if a wire is somehow shorting out to one side of the Recp2 breaker or that the wires on the breaker itself are loose? I would also think about replacing that breaker itself as well. It sounds from your write up that everything really works, but something is causing a dead short in that circuit which the generator somehow senses and shuts itself off. You may also want to check the wire connections for each of the four outlets on that circuit as well.
All great suggestions that I will do. I already ordered a OEM breaker which I may not need, but they aren't expensive, so why not replace it and cross that off the list. Since there are only four receptacles on that circuit with easy access, I can check the wiring there too. Next will require further testing down-line from the breaker and will require me to figure out where those breaker wires go to at the other end, along with the ground.

I again thank all those that have posted suggestions! -RT
__________________
Ricardo Tegarini
2005 Itasca Sunova
Workhorse Chassis W20
RTegarini is offline   Reply With Quote
Old 03-23-2017, 09:37 AM   #8
Winnebago Owner
 
Join Date: Jun 2007
Posts: 109
Quote:
Originally Posted by RTegarini View Post
...I already ordered a OEM breaker which I may not need, but they aren't expensive, so why not replace it and cross that off the list...
Because then you are just throwing parts at the problem without actually determining what the cause is.

Check the wiring, as suggested, and the surrounding area before changing parts.
__________________
NoMoreAZ

2006 Itasca Horizon 40KD, 2004 Honda CR-V
NoMoreAZ is offline   Reply With Quote
Old 03-23-2017, 09:53 AM   #9
Winnebago Owner
 
Join Date: Jun 2005
Location: behind the steering wheel
Posts: 95
nomoreaz is correct. take the 4 outlets out and disconnect the black wires., check each wire for a short to ground. did you just fasten something to the walls, or outside using a screw? any repairs done near the area of the wires?
ive found that to be a common problem. anyway, you will find the offending wire.
repair it from there, dont just throw parts at it.
azpete is offline   Reply With Quote
Old 03-23-2017, 12:21 PM   #10
Winnebago Owner
 
PJStough's Avatar
 
Join Date: Oct 2015
Posts: 61
If there was a short to ground somewhere on the offending circuit, shouldnt the breaker for that circuit kick out, or if it fails, shouldnt the breaker on the generator kick out? Seems to me there is another issue at play here. Do you have an inverter that is powering that circuit, and the inverter is on?
__________________
Paul & Ann Iowa
2005 Winnebago Voyage 38J
https://stoughrvadventure.blogspot.com/
PJStough is offline   Reply With Quote
Old 03-23-2017, 02:23 PM   #11
Winnebago Master
 
bobmac's Avatar
 
Join Date: Mar 2008
Location: Southern Ontario
Posts: 562
If one of the outlets is a gfci on the circuit that is in question, I would replace it before the panel breaker. GFCIs in RVs seem to be prone to failure so that might very well be the cause of the problem in the circuit. Good luck and insure the power and inverter are off before you tackle any wiring in the coach.
__________________
Bob
09 Journey 39Z
Southern Ontario
bobmac is offline   Reply With Quote
Old 03-23-2017, 07:10 PM   #12
Winnie-Wise
 
Join Date: Jul 2010
Posts: 343
So to cover a few of the above questions, there is no GFCI and there is no inverter on this particular circuit. The circuit consists of four receptacles, with three of them in the bedroom and I'm pretty sure we have never used any of them. The fourth one though is at the dinette and definitely used a lot when traveling and camping to charge iPhones, iPads and use MacBooks, so I'm going to start the inspection process there.

I did have a few minutes to run over to the RV storage today to look things over a bit more; the breaker physically looks good, no burnt wires or arc marks in the panel and all the wires were tight. The generator will run and produce power by turning off the Recps 2 breaker and it will also continue to run if I disconnect the wire from the breaker. That should mean the the breaker likely isn't 'bad' but I'm going to change it out anyway. It was noted that just changing parts may not really solve the issue but for $12, the cost seems insignificant and I can keep the old one (or the new one) as a spare. Had the breaker been available locally, I actually would have checked things out further and only ordered if needed. But since I have a weekend away scheduled at the end of the month and need the motorhome, I figured it was worth the gamble.

NoMoreAZ and azpete, my next step is to check all the receptacles for a short. Also, about a year ago I had the awning replaced and the new awning had shorter arms, so in essence they were pop-riveted into the sidewall in a slightly different location, or at least the pop-rivets probably were. While the bedroom receptacles are within the overall width of the bedroom side and the awning arms are more forward of the slide, I guess conceivably the installers could have hit the circuit wire if the wiring runs horizontally in that area. If that's the case, not sure how the heck I could repair the wire. Could a pop-rivet through the gelcoat sidewall, if it hits a wire, short it out? I'm assuming that the pop-rivet would be only touching gelcoat, maybe some thin wood and some styrofoam. Anyway, I'll start with the dinette receptacle and move on from there.

Thanks again for all the suggestions!! -RT
Attached Thumbnails
Click image for larger version

Name:	MH Breaker Panel.jpg
Views:	620
Size:	401.6 KB
ID:	155896  
__________________
Ricardo Tegarini
2005 Itasca Sunova
Workhorse Chassis W20
RTegarini is offline   Reply With Quote
Old 03-24-2017, 05:42 AM   #13
Winnebago Master
 
bobmac's Avatar
 
Join Date: Mar 2008
Location: Southern Ontario
Posts: 562
You might also want to trace the route of the conductor between outlets. Winnebago uses covered plastic outlet boxes in the circuit as wire junction connection points between outlets if necessary. These are usually located on the floor of the coach. You can usually access them by checking under furniture or by removing bottom drawers if there are cabinets on route. You should also look for signs of any damage that may have been caused by mice chewing. I would check for this after you have verified the frequently used outlet is good. Good luck,
__________________
Bob
09 Journey 39Z
Southern Ontario
bobmac is offline   Reply With Quote
Old 03-24-2017, 08:04 AM   #14
Winnebago Camper
 
Join Date: Sep 2015
Location: Bloomsburg, PA
Posts: 15
May not help but you can buy a very inexpensive tester that plugs into a receptacle that has 3 lights and indicates proper polarity and ground. May point you to a wiring problem.
RandyLee is offline   Reply With Quote
Old 03-24-2017, 11:21 AM   #15
Winnebago Owner
 
PJStough's Avatar
 
Join Date: Oct 2015
Posts: 61
Back to my question about the breaker in the panel for this circuit, and the breaker at the generator. Am I correct in assuming that if there was a short to ground in this circuit shouldnt the breaker in the panel for this circuit kick out, and if that circuit breaker were to fail shouldnt the circuit breaker at the generator then kick out?

If I am correct in this assumption, wouldnt that indicate that a short to ground is not the problem?

For the OP, do you have an inverter in your RV, and if so, is it on when you try and start the generator?
__________________
Paul & Ann Iowa
2005 Winnebago Voyage 38J
https://stoughrvadventure.blogspot.com/
PJStough is offline   Reply With Quote
Old 03-24-2017, 11:46 AM   #16
Winnebago Camper
 
Join Date: Mar 2012
Posts: 8
In the motor home I just traded, (Itasca Sunstar 30T) the bedroom and dinette receptacles were energized by the inverter. When the generator was on, or we were plugged in, the inverter allowed the power to 'pass through' whether it was turned on or off.
Given the symptoms, I'd take a good hard look at the inverter. Perhaps the 'pass through' function isn't working right, thus killing the generator somehow.
One easy check would be remove the AC wiring from the inverter and wire nut the like colors together, effectively taking the inverter out of the AC circuit, and see if that cures the problem.
__________________
2017 Airstream 27FB
2015 Silverado CC 1500
JMynes is offline   Reply With Quote
Old 03-24-2017, 11:48 AM   #17
Winnebago Owner
 
Join Date: Jul 2005
Location: Carmel, Indiana
Posts: 135
Which model of 2005 Sunova do you have?

IPD 27C
IFD 29R
IFD 30B
IFD 33L
IFD 34A
IFD 35N
__________________
Clayton
2006 Winnebago Journey 36G
Cat 350
CWHTRAINS is offline   Reply With Quote
Old 03-24-2017, 12:13 PM   #18
Winnie-Wise
 
Join Date: Jul 2010
Posts: 343
Quote:
Originally Posted by CWHTRAINS View Post
Which model of 2005 Sunova do you have?
I have the 34A. -RT
__________________
Ricardo Tegarini
2005 Itasca Sunova
Workhorse Chassis W20
RTegarini is offline   Reply With Quote
Old 03-24-2017, 12:20 PM   #19
Winnie-Wise
 
Join Date: Jul 2010
Posts: 343
Quote:
Originally Posted by JMynes View Post
In the motor home I just traded, (Itasca Sunstar 30T) the bedroom and dinette receptacles were energized by the inverter. When the generator was on, or we were plugged in, the inverter allowed the power to 'pass through' whether it was turned on or off.
Given the symptoms, I'd take a good hard look at the inverter. Perhaps the 'pass through' function isn't working right, thus killing the generator somehow.
One easy check would be remove the AC wiring from the inverter and wire nut the like colors together, effectively taking the inverter out of the AC circuit, and see if that cures the problem.
While it's hard for me to follow wiring diagrams, I have looked at them for my model. The Recps 2 breaker only serves four receptacles, three of which are in the bedroom. But there is actually another receptacle in the bedroom that ties into the inverter circuit and serves in part the bedroom T.V., which I have verified has 110v power with the generator running. The only breaker that the generator is having issues with is the Receps 2 breaker, also referred to as 'brown', but neither the breaker or wire color is actually brown in color. I assume that the 'brown' means that's how the wire is labeled from Winnebago for that particular circuit.

Thank-you. -RT
__________________
Ricardo Tegarini
2005 Itasca Sunova
Workhorse Chassis W20
RTegarini is offline   Reply With Quote
Old 03-24-2017, 12:26 PM   #20
Winnie-Wise
 
Join Date: Jul 2010
Posts: 343
Quote:
Originally Posted by PJStough View Post
Back to my question about the breaker in the panel for this circuit, and the breaker at the generator. Am I correct in assuming that if there was a short to ground in this circuit shouldnt the breaker in the panel for this circuit kick out, and if that circuit breaker were to fail shouldnt the circuit breaker at the generator then kick out?

If I am correct in this assumption, wouldnt that indicate that a short to ground is not the problem?

For the OP, do you have an inverter in your RV, and if so, is it on when you try and start the generator?
I'm not expert at all on electrical issues, which you can tell with all my questions, but I've read that the Onan generator, at start-up, in milliseconds takes a voltage reading in millivolts and if the number doesn't match up to the required specifications, it shuts down the generator to protect it. Because of this, I could have some sort of short but maybe not a dead short that would trip the breaker. I'm told it's a lesser type of short but can't really explain it properly.

I do have the OEM 300 watt inverter, but it's on a different wiring circuit. It is 'on' and doesn't trip a breaker or effect the generators' ability to run properly if I turn off the Recps 2 breaker, which is a different circuit.

Thank-you. -RT
__________________
Ricardo Tegarini
2005 Itasca Sunova
Workhorse Chassis W20
RTegarini is offline   Reply With Quote
Reply

Tags
generator, onan


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Winnebago Industries or any of its affiliates. This is an independent, unofficial site.


All times are GMT -6. The time now is 12:07 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.