ACs and 30 amp Hook up only?
08-23-2011, 12:13 PM
|
#1
|
|
Senior Member
Join Date: Oct 2010
Posts: 178
|
All:
My Newmar 3352DP has a 50 AMP system with two ACs. My question is, when stopping at a CG with only 30 AMP service, can I still turn on one of the ACs ? It is my understanding that 30 AMPs would not support two ACs.
If I can run one AC on 30 AMPs would I do this by turning one of my zones off at the thermastat, perhaps the bedroom AC?
Thanks in advance for your advise.
Dave
__________________
Dave and Anita
Two empty-nesters
2003 Newmar KS3352DP
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
08-23-2011, 12:20 PM
|
#2
|
|
Senior Member
Join Date: May 2011
Location: Vancouver, WA
Posts: 4,278
|
We have 2 13.5 heat pumps in our DSDP, I can run both of them on 30 amps but not much else. I turn the water heater to gas, the refer doesn't make much difference although I do change it over too.
__________________
2002 Newmar Dutch Star 4090 ISC 350/1050 with Banks Kit, now 435/1200
Charter Good Sam Lifetime Member, FMCA f47302s
RV'ing since 1957, NRA Benefactor Life Member
|
|
|
|
| |
|
08-23-2011, 12:25 PM
|
#3
|
|
Community Moderator
Nor'easters Club Newmar Owners Club Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,606
|
You control your zones with your thermostat settings.
30amps will run your 1 AC may even run both if fridge, hot water heater are placed on LP gas.
If you had a digital meter plugged in outlet you would see your voltage drop as appliances are used.
To much of a voltage drop will harm your AC operation.
|
|
|
|
| |
|
08-23-2011, 01:23 PM
|
#4
|
|
Senior Member
Newmar Owners Club
Join Date: Feb 2011
Posts: 204
|
Our previous coach had an EMS panel with a digital readout of our amp usage. Loved it and miss it in this new coach. What can we get to take its place? We're in a campground with 30 amp service now; running one A/C and the fridge on electricity. Turn off the A/C to use the microwave.
BTW, the coach was shaking with that earthquake even though we're in mid-NY.
__________________
2011 Ventana 3434
|
|
|
|
| |
|
08-23-2011, 01:41 PM
|
#5
|
|
Senior Member
Join Date: Oct 2010
Posts: 178
|
OK, thanks! I feel better knowing that if I only have 30 amps I can still use the ACs with some degree of caution.
__________________
Dave and Anita
Two empty-nesters
2003 Newmar KS3352DP
|
|
|
|
| |
|
08-23-2011, 01:54 PM
|
#6
|
|
Senior Member
Join Date: Mar 2010
Location: Sarasota,FL
Posts: 296
|
You might get away with running both AC's on 30 amps but chances are you are close to tripping the source breaker. I tried it with a short 50 to 30 adapter and after 1 hour that short adapter was hot and limp. If the source pole also has a standard recepticle then this usually supplies 15 amps. I went to Camping World and got the box adapter that has 2 30 amp plugs but it also contains an adapter to run one of the plugs to a standard 15 amp plug. Together this gave me approx 45 amps which was plenty to run both AC's and fridge but not the water heater. The microwave was used sparingly. But having both AC's in this summers extreme heat was well worth it. During the day they ran non-stop until dusk.
__________________
Lynda & Ronny OSC, USN RET
Sarasota, Florida
2005 DutchStar 3809 DP
|
|
|
|
| |
|
08-23-2011, 02:01 PM
|
#7
|
|
Senior Member
Join Date: Oct 2010
Posts: 178
|
Sounds like something I need to add! We try to avoid, extreme heat camping, but coming and going from Texas it is a fact. We will be heading south from the Smokie Mountain NP in late September and a few of the Georgia SPs that I have considered all have 30 AMP hook-ups. Weather temps might still be warm enough to require AC but not too much.
When I get back into the real heat I will look for 50 AMPS if needed.
Thanks,
Dave
__________________
Dave and Anita
Two empty-nesters
2003 Newmar KS3352DP
|
|
|
|
| |
|
08-23-2011, 02:17 PM
|
#8
|
|
Community Moderator
Nor'easters Club Newmar Owners Club Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,606
|
You may find that 15 or 20 amp outlet off the 30 or 50 amp service in some camp grounds, just saying.
|
|
|
|
| |
|
08-23-2011, 02:28 PM
|
#9
|
|
Senior Member
Join Date: Jan 2011
Location: NY & FL
Posts: 833
|
I have run both my 13.5 BTU AC units with NOTHING ELSE on (even the battery charger), and my EMS ammeter showed 24-25 amps. This agrees with the Mfr. Specs for the AC's.
A thirty amp circuit is rated at 24 amps continuous (80 % Rule), so it's right at the max. My 50 to 30 adaptor was quite hot to the touch after an hour of running.
At all but one CG the voltage stayed above 112, so I felt OK about it. One dropped to 107, so I switched off the circuit breaker for one unit, and it came up to 111.
__________________
2008 Itasca Meridian 37H
2011 & 2012 Len & Pat's "One lap of America"
14K miles so far - Woo Woo!
|
|
|
|
| |
|
08-23-2011, 04:46 PM
|
#10
|
|
Senior Member
Join Date: Mar 2010
Location: Sarasota,FL
Posts: 296
|
bluepill, my 50 to 30 adapter didn't bother me as much as the park wiring did. At least I knew my adapter was in good shape and was able to handle the load. The box from camping world really reduced the worry about turning something on without compensating somewhere else. I also carry 2 50ft 30 amp cords in case I need to hook up to another source farther away. For most of the days at a particular park I was able to use the souce from the space adjacent to mine because I knew when it would be occupied then I switched to one 30 amp plug and the 15 amp plug which worked just fine without heating any cords up. So now I think I have every adapter known to man stored below. I guess I need to get something to monitor line voltage next. Just never ends.
__________________
Lynda & Ronny OSC, USN RET
Sarasota, Florida
2005 DutchStar 3809 DP
|
|
|
|
| |
|
08-24-2011, 08:33 PM
|
#11
|
|
Senior Member
Join Date: May 2011
Location: Vancouver, WA
Posts: 4,278
|
Quote:
Originally Posted by bluepill
At all but one CG the voltage stayed above 112, so I felt OK about it. One dropped to 107, so I switched off the circuit breaker for one unit, and it came up to 111.
|
That's why I have an Autoformer!
__________________
2002 Newmar Dutch Star 4090 ISC 350/1050 with Banks Kit, now 435/1200
Charter Good Sam Lifetime Member, FMCA f47302s
RV'ing since 1957, NRA Benefactor Life Member
|
|
|
|
| |
|
08-26-2011, 01:47 PM
|
#12
|
|
Member
Join Date: Mar 2011
Posts: 48
|
A Progressive Industries E M S with remote display will give you volts - amps each side of your 50 amp line - or you have to manually add the amps both sides if you are using a 30 amp outlet with a 50 amp adapter.It will not manage the load by turning off appliances (you will have to do that manually)but acts as surge-over/under voltage protector
__________________
|
|
|
|
| |
|
08-26-2011, 05:37 PM
|
#13
|
|
Senior Member
Fleetwood Owners Club Workhorse Chassis Owner
Join Date: Apr 2002
Location: Beaverton, OR, USA
Posts: 584
|
Dave1956, you might want to read up on the EMS in your RV. An EMS is a Energy Management System that efficiently manages the power consumption of your RV. There are two EMS system capacities, one for 30 amps and one for 50 amps.
My RV has a 30 amp version and it manages the power consumption of the RV to keep it under 30 amps. For example if both air conditioners running and someone uses the Microwave, one of the AC units (the rear one) compressors will be turned off (fan will still run). When the microwave shuts off the AC compressor will be allowed to run again (assuming an interval of time has passed, to protect the compressor). This unit also does not allow both compressors to turn on at the same time in order to avoid the combined surge current. It can also detect that a large load has been applied to any of the 120VAC outlets and shut off a compressor.
The 50 amp version is also the same, but it actually detects that you are connected to only 30 amps and manages the load the same way as described above. This ability is dependent in some cases on how the 50 amp to 30 amp adapter is wired. Often the detection of 30 vs 50 amps is done by sensing current on one leg of the 50 amp 240 volt supply, but not both. If the adapter is wired to supply current to both legs of the 50 amp cord this circuitry will be fooled and not manage the load.
Check, and read up, on what EMS your RV contains.
__________________
Alvin/KB7VHI
2002 35R Southwind, W22 8.1L Vortec UltraPower, 19.5' wheels
Toad: Wrangler, lifted and on 35" tires
|
|
|
|
| |
|
08-26-2011, 05:53 PM
|
#14
|
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Jul 2010
Posts: 342
|
__________________
|
|
|
|
| |
|
 |
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|