Join CruisersForum Today
Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
Old 01-09-2008, 07:43 AM   #1
Ronnie Bledsoe 2006 Dutchstar 43' is offline
Senior Member
Ronnie Bledsoe 2006 Dutchstar 43''s Avatar


Join Date: Oct 2006
Location: Manteca, Ca
Posts: 1,121
Attempted to equalize baqtteries yesterday...only two of the four batteries equalized. Checked the schematic on the pullout tray and all was correct. The two batteries that equlized were the ones with the + and - cables on the terminals those with the jumpers did not boil.
Anyone have an idea of what is wrong?
Also noticed that there are + and - cables cables attached to the jumpered batteries that are not referenced on the schematic.
Anyone know what they are?
I have the 2000 watt RV2012 xantrex inverter, 8KVW gen tec generator, Hydro hot, etc.
Appreciate your help and information

__________________
"Piddln"
2008 Jeep Sahara '4Dr"
Ronnie Bledsoe
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-09-2008, 07:43 AM   #2
Ronnie Bledsoe 2006 Dutchstar 43' is offline
Senior Member
Ronnie Bledsoe 2006 Dutchstar 43''s Avatar


Join Date: Oct 2006
Location: Manteca, Ca
Posts: 1,121
Attempted to equalize baqtteries yesterday...only two of the four batteries equalized. Checked the schematic on the pullout tray and all was correct. The two batteries that equlized were the ones with the + and - cables on the terminals those with the jumpers did not boil.
Anyone have an idea of what is wrong?
Also noticed that there are + and - cables cables attached to the jumpered batteries that are not referenced on the schematic.
Anyone know what they are?
I have the 2000 watt RV2012 xantrex inverter, 8KVW gen tec generator, Hydro hot, etc.
Appreciate your help and information

__________________
"Piddln"
2008 Jeep Sahara '4Dr"
Ronnie Bledsoe
  Reply With Quote
   
Old 01-09-2008, 10:09 AM   #3
Spikester is offline
Senior Member
Spikester's Avatar


Newmar Owners Club
Join Date: Aug 2007
Location: Belfair WA.
Posts: 612
Ronnie, are all your batteries the same age?

If batteries are not the same age they can have extremely different charging characteristics. Generally speaking older batteries will take a higher voltage to equalize than newer batteries, also will take higher voltages to gas. Therefore it will be hard to equalize them all, or even obtain the same capacity on all cells when normal charging.

Best way to tell if they equalized is by using a hydrometer, (if you have one) to check the specific gravity of the electrolyte. Specific gravities should be relative the same on all cells of your batteries. Check the specs on your particular batteries for the 100% charge specific gravity.

Spike
__________________
2008 Newmar VTDP - 3330 - ISBXT 350 Spartan NVS
Toad - 2003 Mini Cooper
FMCA F113720, NKK 18573
  Reply With Quote
   
Old 01-09-2008, 10:17 AM   #4
Ronnie Bledsoe 2006 Dutchstar 43' is offline
Senior Member
Ronnie Bledsoe 2006 Dutchstar 43''s Avatar


Join Date: Oct 2006
Location: Manteca, Ca
Posts: 1,121
Battery age is the same...specific gravity is the same...in the white about 11.75. I will go back and check again
__________________
"Piddln"
2008 Jeep Sahara '4Dr"
Ronnie Bledsoe
  Reply With Quote
   
Old 01-09-2008, 10:36 AM   #5
Spikester is offline
Senior Member
Spikester's Avatar


Newmar Owners Club
Join Date: Aug 2007
Location: Belfair WA.
Posts: 612
If all of your gravities are relatively the same on all your cells, then I would say you have equalized your batteries. Generally the purpose of an equalizer charge is to correct low cell/cells voltages/gravities/performance. Hence the term equalizer. With the l.175 gravities I would say that you have been discharging your batteries since you completed your charge, 1.175 indicates that your batteries are at about 25 percent capacity. Normally would expect gravities to be up in the 1.270 range at the completion of an equalizer charge depending on the type and manufacture of your batteries. Once your batteries have set the gravity will drop a little due to electrolyte cooling but if setting without load should remain really high until discharged.

Spike
__________________
2008 Newmar VTDP - 3330 - ISBXT 350 Spartan NVS
Toad - 2003 Mini Cooper
FMCA F113720, NKK 18573
  Reply With Quote
   
Old 01-09-2008, 11:48 AM   #6
Spikester is offline
Senior Member
Spikester's Avatar


Newmar Owners Club
Join Date: Aug 2007
Location: Belfair WA.
Posts: 612
Heres some info I put together about equalize charging of your batteries. Compiled from Trojan and Interstate Web sites. Table is relative to Trojan batteries, but is good reference/relative for most lead-acid deep cycle RV batteries.

Equalizing is an overcharge performed on flooded lead-acid batteries after they have been <span class="ev_code_BLUE">fully charged</span>. It helps eliminate stratification and sulfation, two conditions that can reduce the overall performance of a battery.

Recommend equalizing only when low or wide ranging cell specific gravity (+/- .015) is detected after <span class="ev_code_BLUE">fully charging a battery</span>.

Procedure
1. Remove all loads from batteries.
2. Start equalizing mode with battery charger.
3. Batteries should begin gassing and bubbling vigorously.
4. Take Specific gravities every hour.
5. Equalization is complete when specific gravity values no longer rise during the gassing state.


% State
of Charge
Specific Gravity
Corrected to
80 Deg F* Open Circuit Voltage
6 Volt 12 Volt
100 1.277 6.37 12.73
90 1.258 6.31 12.62
80 1.238 6.25 12.50
70 1.217 6.19 12.37
60 1.195 6.12 12.24
50 1.172 6.05 12.10
40 1.148 5.98 11.96
30 1.124 5.91 11.81
20 1.098 5.83 11.66
10 1.073 5.75 11.51
State of charge as related to specific gravity and <span class="ev_code_BLUE">open-circuit voltage</span> open-circuit voltage.
*Correct the readings to 80?F:
"¢ Add .004 to readings for every 10? above
80?F.
"¢ Subtract .004 for every 10? below 80?F.

Hope this is some help to all.

Spike
__________________
2008 Newmar VTDP - 3330 - ISBXT 350 Spartan NVS
Toad - 2003 Mini Cooper
FMCA F113720, NKK 18573
  Reply With Quote
   
Old 01-10-2008, 04:01 PM   #7
Bikeboy57 is offline
Senior Member
Bikeboy57's Avatar
Join Date: Feb 2007
Location: Fort Worth
Posts: 156
Uh Ronnie,

Not trying to be a wise guy, but you said the wiring agrees with the schematic, and then you said there are two wires connected that are not on the schematic. Both of those statements can't be exactly true.

Here's the point, I don't know what those connections go to either, you didn't say if they were heavy guage or lightweight so I won't even take a guess.

Here is what I would do. Move those two unknown wires to the same terminals where all the other stuff is attached. Then equalize again and see what happens.

Or just turn on the equalize function again and measure the voltage across all the batteries one at a time. If those unidentified connections are robbing same voltage, you should be able to pick that up.

__________________
Richard, Rhonda, Ty, and Alex

1995 Newell, 470HP Detroit Diesel Series 60
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
New batteries trapshooter MH-General Discussions & Problems 3 09-27-2007 05:56 PM
Equalizing Batteries falcon88 Boondocking 9 08-01-2007 04:56 AM
Equalizing batteries vacation on wheels Class A Motorhome Discussions 6 01-06-2007 02:52 PM
Equalizing Charge htg3 Alpine Coach Forum 7 02-02-2006 11:17 AM
equalizing hitch and coleman pop-up skeetshooter Pop Up Discussion 3 06-29-2005 05:47 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 05:54 AM.