Furnace in a 2903 Bay Star Sport

So I was using my rig this weekend and noticed when using the furnace for heat I get hot air blowing out under the sink near the door, and then under the refrigerator, and that's kind of it. Nothing from the floor vents (well low wall vents) in the bed pedestal in back, nothing from under the shower. I opened up the grill to the furnace as others have inidicated that sometimes the furnace has non-plugged openings, it does not, there are only two hoses coming off the furnace one going forward one to the back.

Anyone have this experience and figure out what to do?

thank you.
__________________
2015 Newmar BayStar Sport 2903 (The downsized)
gremlin is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-14-2016, 01:17 PM   #2
Registered User
 
mel s's Avatar
 
Join Date: Mar 2010
Posts: 8,777
Quote:
Originally Posted by gremlin View Post
So I was using my rig this weekend and noticed when using the furnace for heat I get hot air blowing out under the sink near the door, and then under the refrigerator, and that's kind of it. Nothing from the floor vents (well low wall vents) in the bed pedestal in back, nothing from under the shower. I opened up the grill to the furnace as others have inidicated that sometimes the furnace has non-plugged openings, it does not, there are only two hoses coming off the furnace one going forward one to the back.
Anyone have this experience and figure out what to do?
thank you.
gremlin
In my coach, (not a Bay Star) two duct hoses supply hot air to only 2 registers.
All of the other heat registers in my coach are supplied by duct work , (and/or insulated hoses), under the floor... via the plenum under my Suberban propane furnace.
(Similar to the way the "downflow furnaces" in mobile homes are ducted):

DOWNFLOW FURNACE DUCTWORK

Methinks you may gave a blockage in the plenum under your furnace... or in the ductwork under the floor.... or disconnected ductwork.

Mel
'96 Safari
mel s is offline   Reply With Quote
Old 05-02-2016, 03:45 PM   #3
Senior Member
 
Join Date: Mar 2013
Location: Washington
Posts: 332
Well indeed, the furnace has a plenum exactly like your diagram. Unfortunately it's routed in a manner which is a tad confusing, despite all the vents from the furnace being on the passenger side it runs down the drivers side of the coach. So from the furnace it goes 4 feet across the coach and then down the drivers side branching back to the passengers side for the bathroom and bedroom ducts.


So Anyone else with a BayStar Sport 2903 can you tell me do you get decent air out of the furnace duct below your bed in the back?
__________________
2015 Newmar BayStar Sport 2903 (The downsized)
gremlin is offline   Reply With Quote
Old 05-02-2016, 05:02 PM   #4
Senior Member
 
Petersr58's Avatar
 
Join Date: Mar 2014
Location: Hyannis, MA
Posts: 120
If your Bay Star is like my Canyon Star 3610 a good portion of the furnace heat goes to the lower bays to heat the tanks. I have a four inch vent right over my fresh water tank. The next time you use the furnace check and see if the lower bays are warm. Mine are toasty.
Petersr58 is offline   Reply With Quote
Old 06-02-2016, 01:56 PM   #5
Senior Member
 
Join Date: Mar 2013
Location: Washington
Posts: 332
I did find a vent above my tanks, so I taped it up to see if that would help, no appreciable difference, I really feel like there's a probability someone stepped on the plenum while it was being built, but absent like a 20 foot controllable camera snake I don't know how to see for sure.
__________________
2015 Newmar BayStar Sport 2903 (The downsized)
gremlin is offline   Reply With Quote
Old 06-02-2016, 02:07 PM   #6
Senior Member
 
ga80486's Avatar
 
Newmar Owners Club
Ford Super Duty Owner
Join Date: Jun 2015
Location: Ada, MI
Posts: 156
Is there a second furnace in the bedroom?
__________________
2015 Newmar Bay Star 3308
2015 Jeep Grand Cherokee 4X4 Limited
[SIGPIC][/SIGPIC]
ga80486 is offline   Reply With Quote
Old 06-03-2016, 12:26 PM   #7
Senior Member
 
Join Date: Mar 2013
Location: Washington
Posts: 332
Quote:
Originally Posted by ga80486 View Post
Is there a second furnace in the bedroom?
Nope only one furnace in this unit.
__________________
2015 Newmar BayStar Sport 2903 (The downsized)
gremlin is offline   Reply With Quote
Old 11-06-2016, 11:19 PM   #8
Junior Member
 
Join Date: Oct 2016
Posts: 20
Quote:
Originally Posted by gremlin View Post
So I was using my rig this weekend and noticed when using the furnace for heat I get hot air blowing out under the sink near the door, and then under the refrigerator, and that's kind of it. Nothing from the floor vents (well low wall vents) in the bed pedestal in back, nothing from under the shower. I opened up the grill to the furnace as others have inidicated that sometimes the furnace has non-plugged openings, it does not, there are only two hoses coming off the furnace one going forward one to the back.

Anyone have this experience and figure out what to do?

thank you.
I have a 2903 2017 version, yes heat comes up by the foot of the bed, though the bedroom was not as warm as the rest of the coach.
__________________
2017 Newmar Bay Star Sport 2903
Old biker is offline   Reply With Quote
Old 11-06-2016, 11:50 PM   #9
Moderator Emeritus
 
"007"'s Avatar
 
Nor'easters Club
Workhorse Chassis Owner
iRV2 No Limits Club
Join Date: Oct 2004
Posts: 30,785
You need to open the grill under the fridge and gain access to furnace area and check the vent outlets of furnace metal housing and make sure none of the vent openings do not have a air hose that has fallen off vent ring and no hole is open with out a blocking ring for the ones not used.
You will have to take off the rear furnace panel facing you and look on floor for feed into the duct system in floor for no blockage.
All the tin foil ducts should be checked and make sure they are attached to finished vent, they can become loose and fall off vent if not taped.
__________________
98KSCA, 99MACA, 03 KSCA-3740- 8.1 Chev-- ALLISON Trans
VISIT the NEWMAR QUICK TIPS & EASYMODS 1 & 2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS --- TECH INFORMATION
"007" is offline   Reply With Quote
Old 11-07-2016, 07:11 AM   #10
Senior Member
 
Join Date: Sep 2014
Posts: 168
2903 Furnace

My 2903 had very little flow to the bedroom and the bathroom. There are two vents below the refrigerator. One is a return the other a outlet. I blocked the outlet, this enabled more flow to go back toward the bath and bedroom. Remove the cover in the bottom of the storage area under the bed. On the right side you will see the heater hose that moves with the bed. Check to see if it is still hooked up. The bath only has a 2" hose that feeds the outlet. This is hard to work on because it is under the shower pan and only workable thru the vent hole. The last thing you can do is silver tap the register box. Remove the return vent under the kitchen area. You will see the register with hole th
zrobotman is offline   Reply With Quote
Old 11-08-2016, 09:23 AM   #11
Senior Member
 
Join Date: Mar 2013
Location: Washington
Posts: 332
So I've done a fair amount of investigation including removing the furnace and taping up all the ducts on it except for the down draft vent and putting it back in, nothing increased the flow to the bedroom.

I then finally got it to a dealer (Guaranty) they found something that was "disconnected" but didn't specify what, in addition they installed a vent that I could close under the kitchen area (but weirdly not the one next to i under the refrigerator)

After that I could finally feel air moving out the bedroom vent, but not much at all, so I installed another block off under the kitchen, and I blocked off the vent in the storage compartments and that helped a bit more. It still blows to beat the band out the other ducts and not the bedroom, the only thing I can think of doing to fix it from here is to run a flexible duct off the furnace, under the fridge, under the shower and through the bottom of the cabinet into the bathroom and out the bedroom wall near the sliding door
__________________
2015 Newmar BayStar Sport 2903 (The downsized)
gremlin is offline   Reply With Quote
Old 02-02-2017, 06:09 AM   #12
Senior Member
 
aa9zz's Avatar
 
Tiffin Owners Club
Join Date: Aug 2012
Location: Vincennes, IN
Posts: 224
After warranty service, here is what I found out about the low air flow in the bedroom furnace vent.

The factory service people confirmed that I had slow or almost non existent air flow in the bedroom. They put a camera in the vent system and found the vent flowed from the font outlet all the way to the back of the coach, well beyond the last outlet. The air was by bypassing the bedroom vent; just going past it and to nowhere.

Just past the bedroom vent they installed a blocking device (a piece of plastic) so the air would not go past the outlet but instead be pushed up through that outlet.

This worked great. When I picked it up this week I started the furnace and it worked well.

I suggest you contact the folks at building 16 or go inside the vent and just block it with an angled piece that does not allow the air go beyond the vent and even pushes the air back and up the register.

You might also want to suppress or reduce the amount of air into the front, by the door, by using a piece of cardboard or plastic slightly covering some of the cent area in the front. They didn't suggest this but I thought it might help also.

I am now quite happy with my furnace air flow but I hope I never have to use it,

Phil
__________________
Phil and Linda Smith, Retired University Faculty
2017 Tiffin Allegro Red 33AA FMCA #F463160
2017 Jeep Cherokee Trailhawk
aa9zz is offline   Reply With Quote
Old 03-30-2017, 02:36 PM   #13
Senior Member
 
Join Date: Mar 2013
Location: Washington
Posts: 332
Follow up on my investigation, I opened up the area under the bed and found the 4" duct into the floor plenum for the heat. Removing that I found decent flow in that box, not at all what was coming up through the vent in the bed.

I tried just putting a deflector in there as the box actually extends past the 4" hole by at least a foot maybe two. This seemed to help but only a little. We stuck a camera in there and found no evidence that the vent wasn't closed off on the end, I still suspect somethings crushed somewhere in there, or it really just isn't designed well.

In the end we removed the 4" hole and then put in it's place a 6" flange we picked up at lowes. We used a rotozip to enlarge the hole into the floor plenum, and then changed the 4" flexible dryer hose that was used to connect to the vent at the foot of the bed with 6" hose and a step down to change the 6" to 4" at the vent. Screwed it all back together and the result was an increase in air flow probably double what we had, still not what I'd expect especially when you plug up the rest of the vents in the rig, but the 6" hose has much less pressure drop than the 4" so I believe this will help a lot.
__________________
2015 Newmar BayStar Sport 2903 (The downsized)
gremlin is offline   Reply With Quote
Reply

Tags
ace, furnace



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Almost there... 2016 Bay Star Sport 2903 WhatsHisName Newmar Owner's Forum 29 11-05-2016 08:48 AM
Fantastic fan in Bay Star Sport 2903 donnickerson Newmar Owner's Forum 1 03-04-2016 11:08 AM
Difference between the Bay Star and the Bay Star Sport Keithmq Newmar Owner's Forum 16 10-12-2014 08:36 PM
2014 Bay Star 2903 House hold Batteries roadtraveler Newmar Owner's Forum 19 04-07-2014 09:31 AM
Bay Star 2903 Leveling Jack Question roadtraveler Newmar Owner's Forum 1 03-27-2014 12:20 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:59 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.