The propane furnace in our 2006 KSDP will work perfectly for 24 hours or so and then all of a sudden it will not cut off, and the coach keeps getting hotter and hotter inside until I turn the gas off and pull the 20 amp DC fuse. Turning the thermostat off does no good.

After the unit cools down a bit, I can turn the gas back on, reinstall the fuse, and the unit works perfectly for an undetermined amount of time.

What could be causing the furnace to run out of control periodically? I could take the coach to a service center, but if the problem is not occurring, a technician cannot fix it.

Any advice will be appreciated.

__________________
2006 KSDP 3909

Cummins ISL 350HP
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-02-2010, 07:08 PM   #2
palehorse89 is offline
Senior Member
palehorse89's Avatar
Newmar Owners Club
Join Date: Oct 2009
Posts: 237
Somewhere your thermostat wire is shorted together or make contact with the two wires going to the controller. If the wires are able to make contact it is like the thermostat calling for heat and will not shut down till the wires are seperated. Just a thought. I had it happen to me in my garage heater wire, a staple shorted the two wires together and it would not shut down.

__________________
2000 MADP 4060 MOUNTAIN AIRE
350 HP ISC, 2011 WRANGLER SAHARA ,2006 ULTRA CLASSIC
  Reply With Quote
   
Old 12-02-2010, 07:19 PM   #3
RVhauler is offline
Senior Member
Join Date: Apr 2010
Posts: 678
agree with palehorse89. Would run a temporary line from furnace to stat or use another stat for shorter wire run and check operation. If your furnace has a electronic board then could also be problem. Can check furnace operations by disconnecting stat wires and replacing with jumper wire on furnace
__________________
  Reply With Quote
   
Old 12-02-2010, 07:34 PM   #4
Luv2go is offline
Senior Member
Luv2go's Avatar
Appalachian Campers
Newmar Owners Club
Ford Super Duty Owner
Coastal Campers
Nor'easters Club
Join Date: Mar 2009
Posts: 703
What kind of thermostat do you have, the Comfort Control (most Newmar's have them) or something else? According to the furnace schematic in this manual the only thing that can keep the power going to the gas valve is if the thermostat (which in a Comfort Control is really a relay in the control board in one of your A/C units) stays closed. There also could be an intermittent short in the wiring as has been previously suggested.

Note the Comfort Control does not directly control the furnace, you will only find a phone cord coming out of it and it goes to the A/C unit's control board. The Comfort Control has a micro-controller in it that talks to the control board in the A/C which turns on the relay when the furnace is needed.

To troubleshoot this you can find the blue wires coming out of your furnace (there should be at least one) and unhook it when the problem occurs. If the furnace turns off after a few minutes your problem is in the control board of your A/C unit or wiring, if it does not the problem is in your furnace. This knowledge will help the tech pinpoint the problem even if he can't replicate it.
__________________
Stewart, Brenda and kids
2008 Newmar Canyon Star 3410
  Reply With Quote
   
Old 12-02-2010, 08:08 PM   #5
"007" is offline
Community Moderator
"007"'s Avatar


Nor'easters Club
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,607
This PDF will show how control is wired to AC's & furnace.
__________________
98KS,99MA,03-KS-3740 W-22 & 6 Ford's 3 V-10's
VISIT the NEWMAR QUICK TIPS & EASYMODS1&2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS
  Reply With Quote
   
Old 12-03-2010, 06:34 PM   #6
ricere is offline
Senior Member
ricere's Avatar
Newmar Owners Club
Join Date: Mar 2007
Location: Crewe, Virginia
Posts: 167
I appreciate you guys taking time to answer my post. Don't think the problem is with wiring because it does not happen consistently. The thermostat works fine with the heat pumps, so I don't believe there is a problem there. The furnace has been working perfectly for the past 36 hours. That makes me believe it is a circuit board problem at the heat pump. That could be an expensive fix.

I have a Comfort Control unit, and thank you all. Luv2go and 007, your advice was very useful.
__________________
2006 KSDP 3909

Cummins ISL 350HP
  Reply With Quote
   
Old 12-04-2010, 04:57 AM   #7
"007" is offline
Community Moderator
"007"'s Avatar


Nor'easters Club
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,607
One thing you might want to do is check all the screw connections for your 12 volt wiring.
You will find screw connections in the 12v fuse panel near load center a block on refrigerator deck and even into the control board pins.
Vibration can cause many problems going down the road some of us have been through this.
When I say 12v's that means positive & negative connections you need both with tight connections.
While at control board check all connection pins any one could have a loose connection.
For warmer nights in your future.
__________________
98KS,99MA,03-KS-3740 W-22 & 6 Ford's 3 V-10's
VISIT the NEWMAR QUICK TIPS & EASYMODS1&2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS
  Reply With Quote
   
Old 12-09-2010, 06:34 PM   #8
ricere is offline
Senior Member
ricere's Avatar
Newmar Owners Club
Join Date: Mar 2007
Location: Crewe, Virginia
Posts: 167
Furnace problem fixed. Turned out to be the circuit board in the #1 heat pump (air conditioner). Took it to an RV repair shop, and after some troubleshooting, it was determined that the circuit board was the most logical explanation for the problem. They swapped the circuit board from #2 heat pump to #1 heat pump and the problem is gone.

The circuit boards are identical, but the furnace part on the #2 board is not needed unless there are 2 furnaces installed in the coach. I only have one and it is connected to the #1 heat pump.

Thanks for all the info.
__________________
2006 KSDP 3909

Cummins ISL 350HP
  Reply With Quote
   
Old 12-10-2010, 08:54 AM   #9
GaryKD is offline
Senior Member
GaryKD's Avatar


Newmar Owners Club
Join Date: Jul 2006
Location: Wellington, Florida
Posts: 6,933
Hi ricere,
Thanks for providing the solution. It helps all of us to know that was the final answer.
__________________
Gary
2005 Newmar KSDP 3910,
The Avatar Is Many Times Around The USA
Nobody Knows Your Coach Like Somebody Who Owns One Just Like Yours
  Reply With Quote
   
Old 12-10-2010, 09:17 AM   #10
Luv2go is offline
Senior Member
Luv2go's Avatar
Appalachian Campers
Newmar Owners Club
Ford Super Duty Owner
Coastal Campers
Nor'easters Club
Join Date: Mar 2009
Posts: 703
Glad you found the fix and you had a "spare"
__________________
Stewart, Brenda and kids
2008 Newmar Canyon Star 3410
  Reply With Quote
   
Old 12-10-2010, 02:37 PM   #11
"007" is offline
Community Moderator
"007"'s Avatar


Nor'easters Club
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,607
Thanks for the follow up ricere that information about changing the boards is most helpful if we can remember the next time this comes up.
__________________
98KS,99MA,03-KS-3740 W-22 & 6 Ford's 3 V-10's
VISIT the NEWMAR QUICK TIPS & EASYMODS1&2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS
  Reply With Quote
   
Old 12-12-2010, 08:19 PM   #12
ricere is offline
Senior Member
ricere's Avatar
Newmar Owners Club
Join Date: Mar 2007
Location: Crewe, Virginia
Posts: 167
Hopefully what happened to me will help someone else. That's what it's all about. I appreciate all your feedback.
__________________
2006 KSDP 3909

Cummins ISL 350HP
  Reply With Quote
   
Old 12-14-2010, 08:14 PM   #13
Wingman02 is offline
Member
Join Date: Oct 2008
Location: Harbinger
Posts: 85
I checked the website tonight to start my search for a furnace issue I am having. Didn't have to search long and got some good information to get me started. Glad yours worked out for you and thanks to those that helped answer ricere's questions!!

__________________
2006 Newmar Ventana 3613
2009 Ford Taurus Toad
2002 & 2004 GL1800's,
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Atwood furnace problem clintstimson RV Systems & Appliances 9 03-23-2010 03:14 AM
Dirty oil or problem with actuators? TEO Caterpillar Engine Forum 6 09-21-2009 12:44 PM
Hydro Flame furnace problem Jim.UT RV Systems & Appliances 1 08-01-2009 04:04 AM
Dometic Frig Problem dieselclacker RV Systems & Appliances 2 07-29-2009 03:12 AM
Suburban furnace won't light in cold weather BryannasTreasureBox MH-General Discussions & Problems 9 01-22-2005 07:12 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 10:00 AM.