11-21-2016, 11:04 AM
|
#1
|
Senior Member
Newmar Owners Club Freightliner Owners Club iRV2 No Limits Club
Join Date: Nov 2016
Location: Tucson, Arizona
Posts: 1,580
|
Question regarding my TRC SurgeGuard Model 34560 problems
I have a problem/issue that I haven't resolved conclusively (my wife says I have a lot of those).
Yesterday we arrived in Fredricksburg, Texas. I plugged the coach into a 50 amp service. The surge protector went through it's 2:16 second time delay and then went into a rather violent sounding buzzing and became very hot in just a few minutes.
Both "lines in" had indicator LED's lit, the time delay LED was flashing as it should. Then the violent buzzing occurred.
In order to get power I ended up wiring around it use an 8 ganged buss block temporarily as the "bypass switch" did nothing. Any thoughts? Internal relay is likely shot is what I am thinking
What say the collective?
__________________
Our Blog - Wandering Toes
Our Coach - 2005 Newmar Northern Star | 350 Cat C7 3126 | Freightliner XC Chassis
2018 Jeep Renegade Trailhawk
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
11-21-2016, 12:32 PM
|
#2
|
Senior Member
Newmar Owners Club Nor'easters Club Appalachian Campers Ford Super Duty Owner Coastal Campers
Join Date: Dec 2007
Posts: 2,463
|
Sounds like the big relay is buzzing. Does this happen to be mounted flat on the floor? That's the only position TRC does not recommend, it's possible the relay won't work reliably for a long period of time in this position. Otherwise it just failed, which happens. TRC has a one year warranty IIRC, so if it is new contact them and they'll tell you what to do.
__________________
Stewart, Brenda and kids
2008 Newmar Canyon Star 3410, now at a new home
2006 Roadtrek Versatile 210
|
|
|
11-21-2016, 12:46 PM
|
#3
|
Senior Member
Newmar Owners Club Freightliner Owners Club iRV2 No Limits Club
Join Date: Nov 2016
Location: Tucson, Arizona
Posts: 1,580
|
Quote:
Originally Posted by Luv2go
Sounds like the big relay is buzzing. Does this happen to be mounted flat on the floor? That's the only position TRC does not recommend, it's possible the relay won't work reliably for a long period of time in this position. Otherwise it just failed, which happens. TRC has a one year warranty IIRC, so if it is new contact them and they'll tell you what to do.
|
It happened while mounted on a side wall. I called TRC and they said it sounded like the circuit board bit the dust. About my luck.
__________________
Our Blog - Wandering Toes
Our Coach - 2005 Newmar Northern Star | 350 Cat C7 3126 | Freightliner XC Chassis
2018 Jeep Renegade Trailhawk
|
|
|
01-21-2017, 01:38 PM
|
#4
|
Senior Member
Newmar Owners Club Freightliner Owners Club iRV2 No Limits Club
Join Date: Nov 2016
Location: Tucson, Arizona
Posts: 1,580
|
I would like to revisit this subject. Can these surge protectors be rebuilt? Does anyone know of any place that does it? TRS said they will only warrant new units and they no longer service faulty units out of warranty. Seems a waste to just trash it if repairs can be made. Call me cheap.
__________________
Our Blog - Wandering Toes
Our Coach - 2005 Newmar Northern Star | 350 Cat C7 3126 | Freightliner XC Chassis
2018 Jeep Renegade Trailhawk
|
|
|
01-21-2017, 04:01 PM
|
#5
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
|
I do not know about his model but the older one I have can indeed be rebuilt,, however the rebuild falls into one of 3 or 4 categories.
I got a "Deal" on mine cause the outlet was history (melted) First time I've ever seen a 50 amp outlet melt down. had to put a new outlet on it.
You (or rather TRC) can replace the control board/read out assembly
Or the Contactors
or the MOVs (Spike Supressors) in fact I can do the MOV's.
__________________
Home is where I park it!
|
|
|
01-21-2017, 05:36 PM
|
#6
|
Senior Member
Official iRV2 Sponsor
Join Date: May 2011
Posts: 8,305
|
Quote:
Originally Posted by Charlie72704
I would like to revisit this subject. Can these surge protectors be rebuilt?
|
I just replaced a Surgeguard that had gone bad with a Progressive. The Surgeguard had performed well (for 6 years) but Progressive makes a big deal about the fact that they can and will provide parts for rebuilding failed units.
__________________
Joel (AKA docj)--
RV Technology Specialist
|
|
|
01-21-2017, 08:42 PM
|
#7
|
Senior Member
Join Date: Mar 2014
Posts: 1,459
|
Progressive simply rocks. I had some arcing at some point between the PT-50c and connecting cable. Progressive will do a refurbished exchange for $89.95. They don't appear to supply parts for repair. Simply replace or refurbish.
So after three years I have a new update PT-50C. Doesn't get any better than that. This was a user error/ordinary wear situation, well documented on their website. If the unit failed internally they would simply replace.
__________________
Gary 2021 NH Majestic
Ram 5500 with Bodywerks bed
Box Elder, SD and the road
|
|
|
|