Old 03-30-2008, 11:54 AM   #1
JerryKelly is offline
Senior Member
Join Date: Nov 2006
Location: Cleveland, OH
Posts: 391
My 5 year old portable Surge Guard just stopped working. Afer it checks for low/ high voltage, it does not allow power to the MH. Niether the red fault light nor the green ok light comes on. I checked each power leg and each has around 125 volts. Combined I am getting around 250, which is well within the SurgeGuard tolerances for over/under.

I need to decide if I should go with a new portable unit or one that is installed between the transfer switch and fuse panel. With the recent failure of the portable unit, I am inclinded to replace it with another portable. However, what protects my electronics and appliances when using the generator? I am considering the Progressive Industries 50 amp unit that provides surge protection, checks polarity, LOW/High voltage, AC delay, and other features.

In over 5 years, I have never experienced a power problem where my SurgeGuard blocked power.

__________________
Jerry

2006 Newmar Mountain Aire 4304
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-30-2008, 11:54 AM   #2
JerryKelly is offline
Senior Member
Join Date: Nov 2006
Location: Cleveland, OH
Posts: 391
My 5 year old portable Surge Guard just stopped working. Afer it checks for low/ high voltage, it does not allow power to the MH. Niether the red fault light nor the green ok light comes on. I checked each power leg and each has around 125 volts. Combined I am getting around 250, which is well within the SurgeGuard tolerances for over/under.

I need to decide if I should go with a new portable unit or one that is installed between the transfer switch and fuse panel. With the recent failure of the portable unit, I am inclinded to replace it with another portable. However, what protects my electronics and appliances when using the generator? I am considering the Progressive Industries 50 amp unit that provides surge protection, checks polarity, LOW/High voltage, AC delay, and other features.

In over 5 years, I have never experienced a power problem where my SurgeGuard blocked power.

__________________
Jerry

2006 Newmar Mountain Aire 4304
  Reply With Quote
   
Old 03-30-2008, 01:02 PM   #3
oemtech is offline
Senior Member
oemtech's Avatar


Commercial Member
Newmar Owners Club
Texas Boomers Club
Join Date: Feb 2003
Location: Jarrell, TX 76537
Posts: 3,792
Send a message via AIM to oemtech
I install an in line. It protects both inputs (gen/shore) if wired correctly. You also don't have to lock it up all the time.

I did a writeup on my install. Link Here
__________________
Dale/aka-Oemy Oemy's UltraPower Performance
Ultra Power'd/Ultra Trac'd/Magnum Plug Wires/AC 41-101's/DIY CAI/Koni's
2004 Mountain Aire MACA 3651-1997 Honda CRV - Toad
  Reply With Quote
   
Old 03-30-2008, 01:12 PM   #4
Route 66 is offline
Community Administrator
Route 66's Avatar


Newmar Owners Club
Join Date: May 2000
Location: Newark, DE
Posts: 13,893
One of the big advantages of the hardwired unit is the indoor display.

You can tell what's going on without going outside.

The indoor display is also handy for watching your loads when on 30 amp service.
__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, '07 DSDP, '11 Virtual RV


  Reply With Quote
   
Old 03-30-2008, 01:46 PM   #5
Dav5942 is offline
Senior Member
Dav5942's Avatar


Join Date: Feb 2005
Location: Lake Oklawaha RV Resort(\
Posts: 1,185
Best of both worlds Progressive Ind. 50amp inline/"hardwired" that can be removed with plugs(can be wired with or without Genny), with two displays-one indoors and one in the power compartment! Easy installation plugs and cable are available at local hardware. Great for easy removal upon failure(have seen two fail). Have also seen Genny put out between 50 and 270 volts-luckily did not destroy anything.

ATME-mods


__________________
High Line Toyhauler '07 Mid Engine 42' ATME 4153 w/ '96 Fatboy,Rubicon(w/4" Lift,Moto Metal whs,33X13.5" Mickey Thomps Baja Claw) in tow, 2-Grizzlys in garage
http://picasaweb.google.com/dav5942/...T2AlaskaBeyond
  Reply With Quote
   
Old 03-30-2008, 01:51 PM   #6
NLOVNIT is offline
Community Administrator
NLOVNIT's Avatar


Ford Super Duty Owner
Fleetwood Owners Club
Pond Piggies Club
Join Date: Mar 2002
Location: Central OH, USA
Posts: 8,835
Blog Entries: 1
DH hardwired the Progressive surge guards on our last 2 rv's. Wouldn't have it any other way. Like Dirk states, the inside display panel is great for monitoring without having to traipse outside.

As for protecting appliances/electronics while on generator, from what my dealer techs have told me & from what I've read on this forum, generator power is so reliable it's not necessary to protect for surges/low power from that. I think what's important is to protect the transfer switch (as well as your appliances/electronics on shore power). That's one expensive switch to have to replace if it gets zapped.

L-
__________________
Lori & Dave - Central OH / FMCA #419886
2006 Fleetwood Bounder 36Z & Jeep Liberty Limited, My iRV2 Photo Albums
  Reply With Quote
   
Old 03-31-2008, 03:53 AM   #7
Bill Barclay is offline
Member
Join Date: May 2007
Location: Texas
Posts: 49
Was in shop last week having HW50A installed. Guy in next bay was having MH repaired from accidently plugging into 220/240a service without HW50A or equivalent. He estimated $2-3,000 damage. Makes my $5-600 installed price look small. By the way, where does the second remote plug into the unit? I only see 1-telephone wire connection for 1-remote that I used for the inside remote. Thanks.
__________________
'06 W Journey,36G,'07 Yukon,Rdmstr, M & G Brake,Alpine Nav, KVH R6, Direct TV, PortaBote Under,
  Reply With Quote
   
Old 03-31-2008, 03:59 AM   #8
JerryKelly is offline
Senior Member
Join Date: Nov 2006
Location: Cleveland, OH
Posts: 391
Updte:

I found out that my Surge Guard is working as designed. I rechecked my pedestal and found out that I have 122V on one leg and 127-128V on the second leg. The Surge Guard will shut down power at 128V. Now I need to figure out why I am getting 128V on the second leg. My home power pedestal has been working fine for 5 years with the same Surge Guard. Could it be the breaker to the pedastal? My electricial initially wired it with a GFCI breaker. Not sure what has changed to cause this.

By the way, I spoke with Newmar customer service this morning and was advised that the transfer box should be surge protected and power from the generator is generally reliable. I have a call into my tech at Bridgeway Cummins-Onan to discuss this issue. Perhaps we need two devices?

Update: According to Prgressive Industries, the surge protector should be installed before the transfer box. No need to protect power from the generator.
__________________
Jerry

2006 Newmar Mountain Aire 4304
  Reply With Quote
   
Old 03-31-2008, 08:50 AM   #9
RVDude is offline
Senior Member
RVDude's Avatar
Join Date: Sep 2006
Posts: 1,341
jerry: Under load your 128v will certainly drop... The Surge Guard will not trip instantly on detecting a nominal over/under-voltage, there is a time delay.
Given that these devices are typically hard wired between the 50amp cord and the transfer switch your switch is protected. The genset typically goes directly into the transfer switch.
__________________
2007 and 7/8ths Newmar Essex 4502
  Reply With Quote
   
Old 03-31-2008, 08:58 AM   #10
RVDude is offline
Senior Member
RVDude's Avatar
Join Date: Sep 2006
Posts: 1,341
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Bill Barclay:
having MH repaired from accidentally plugging into 220/240a service </div></BLOCKQUOTE>

Huh? 50amp service by code is typically 220/240vAC, it can also be only 120vAC but that is more the exception. Either way is no problem. Hence, I don't understand what happened to to the guy next to you by plugging into a standard 50amp 220v pedestal? (Of course, a 220v 30amp RV plug would be a bit of a problem and clearly wired off code - meaning liability on the plug owner's part.)
__________________
2007 and 7/8ths Newmar Essex 4502
  Reply With Quote
   
Old 03-31-2008, 09:07 AM   #11
RVDude is offline
Senior Member
RVDude's Avatar
Join Date: Sep 2006
Posts: 1,341
dav
I am guessing the foreground plug in your most excellent solution is the hot directly from the power cord? Do I notice that it is also a male plug - meaning hot spades if cord is plugged in?
__________________
2007 and 7/8ths Newmar Essex 4502
  Reply With Quote
   
Old 03-31-2008, 09:12 AM   #12
"007" is offline
Community Moderator
"007"'s Avatar


Nor'easters Club
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,612
If you can reach another 50 amp pedestal plug your 50 amp cord in to check your own setup. I had a problem with CG pedestal with two 50 amp plugs and the other plugin was ok just the one assigned to my lot was defective. I wired my Gen and shore line thru SP but just the shore line will be just fine for most of your use.
__________________
98KS,99MA,03-KS-3740 W-22 & 6 Ford's 3 V-10's
VISIT the NEWMAR QUICK TIPS & EASYMODS1&2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS
  Reply With Quote
   
Old 03-31-2008, 11:59 AM   #13
K-Star is offline
Moderator Emeritus
K-Star's Avatar


Newmar Owners Club
Mid Atlantic Campers
Ford Super Duty Owner
Texas Boomers Club
Join Date: Jan 2000
Location: Fulltime - Currently somewhere in the lower 48
Posts: 1,724
Yes, 50A is 220/240 (110/120 on each of the 2 legs).

I have the portable and now wish I had purchased the hardwired. Like said earlier it will protect both power an generator power and is more secure.
__________________
John, Joyce & Libby the Yellow Lab. - Fulltime since May 2008
2005 Kountry Star FW-35LKSA
by Newmar pulled by 2008 Ford F-450 King Ranch, PSD, Automatic, 4:88's
  Reply With Quote
   
Old 03-31-2008, 12:12 PM   #14
Spikester is offline
Senior Member
Spikester's Avatar


Newmar Owners Club
Join Date: Aug 2007
Location: Belfair WA.
Posts: 612
To me its a simple matter of logistics. If you have enough room in your electrical power compartment to install the surge protector on the discharge of your transfer switch so you get protection on the shore power and generator side, then I would suggest that is the preferred type and method of installation. If you do not have the room to accomplish that type of permanent installation then the portable protector is your answer. Look at this way also, if you purchase one that give the most protection you have $400 invested, with a portable at least you can take it with you when you decide to trade MH's. Also with a permanently wired/installed surge protector if the protector goes bad you have a considerable amount of wiring to undo just to get power to your coach until you can replace the existing surge protector.

Spike

__________________
2008 Newmar VTDP - 3330 - ISBXT 350 Spartan NVS
Toad - 2003 Mini Cooper
FMCA F113720, NKK 18573
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
surge protector moldmkr Winnebago Industries Owner's Forum 14 08-26-2008 05:22 PM
surge protector bench Monaco Owner's Forum 13 06-16-2008 07:49 AM
Portable Surge Protector - Theft Protection Eusefull Alpine Coach Forum 10 11-14-2007 04:17 PM
How Many Use an RV Surge Protector? bbarry MH-General Discussions & Problems 32 02-20-2005 10:59 AM
Surge Protector - Portable or inline? RV Systems & Appliances 16 12-31-1969 06:00 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 02:22 PM.