We have a Surge Guard Plus 50 Amp Hard-Wired Power Monitor and it has prevented the AC connection to come into the coach on 5 occasions in the past 7 years of travel. It properly diagnosed "open ground", "Low voltage", and identified "defective circuit breakers". It has worked each time every time we have hooked up.
One comment to all is you should check the incoming electrical connections annually to ensure they have not loosened over time while traveling. DO NOT CHECK CONNECTIONS WHILE PLUGGED INTO A 120V OUTLET OR WHILE YOUR GENERATOR IS RUNNING.
Safe Travels and THE JOY IS IN THE RIDE
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
02-09-2017, 10:21 AM
|
#16
|
Senior Member
Join Date: Oct 2014
Posts: 1,121
|
New Hughes Autoformer with surge protector built in.
__________________
Phil and Laura (and Sam too!)
2024 Coachmen Beyond 22RB (on order)
|
|
|
02-09-2017, 10:40 AM
|
#17
|
Senior Member
Join Date: Oct 2012
Posts: 1,111
|
Quote:
Originally Posted by RV735
We have a Surge Guard Plus 50 Amp Hard-Wired Power Monitor and it has prevented the AC connection to come into the coach on 5 occasions in the past 7 years of travel. It properly diagnosed "open ground", "Low voltage", and identified "defective circuit breakers". It has worked each time every time we have hooked up.
One comment to all is you should check the incoming electrical connections annually to ensure they have not loosened over time while traveling. DO NOT CHECK CONNECTIONS WHILE PLUGGED INTO A 120V OUTLET OR WHILE YOUR GENERATOR IS RUNNING.
Safe Travels and THE JOY IS IN THE RIDE
|
Do you have the remote monitor on your Surge Guard? How did you know these specific problems? Or was it further checking after receiving a fault? I only have lights and none tell me specifically those issues.
__________________
2021 Newmar Ventana 3717 with 2019 Ford Ranger toad
Full timing since 2016
My life goal is to be as smart as the others on this forum.
|
|
|
02-09-2017, 11:03 AM
|
#18
|
Senior Member
Join Date: Aug 2011
Posts: 709
|
Quote:
Originally Posted by TechWriter
I'm using the new Hughes 50A autoformer (on our park model) and a 50A TRC Voltage Regulator (on our RV).
The voltage regulator and the autoformer do the same thing -- boost low voltage.
I've used the TRC unit for a couple of years but the Hughes unit for only a couple of months.
At this point, if I had to choose, I'd go with the TRC voltage regulator. On the same power, my Hughes unit seems to stay in boost mode far more than my TRC.
|
I was all set to buy the Hughes unit until I read your post. What are the differences between the two - price, advantages, etc..?
Thanks!
|
|
|
02-09-2017, 11:09 AM
|
#19
|
Senior Member
Join Date: Aug 2011
Posts: 709
|
Quote:
Originally Posted by TechWriter
|
Why are you switching to the Power Pal? Thanks!
|
|
|
02-09-2017, 11:18 AM
|
#20
|
Senior Member
Newmar Owners Club Tiffin Owners Club Workhorse Chassis Owner
Join Date: Jan 2015
Location: Byhalia, MS
Posts: 3,368
|
Quote:
Originally Posted by ghaynes754
Progressive Industries external EMS-50PTX. Their service rocks. Had the previous model for 3 years and ended up with some melting of the 50a socket. For $89.95 they sent a 'refurbished' unit, in fact it was the latest 50PTX model. Lifetime warranty and lifetime replacement for a reasonable fee for user error make them the only choice in my book.
|
I don't understand. They have a lifetime warranty. Why were you charged for a refurbished unit? Were they claiming abuse? I have one of their surge protectors and am seriously considering upgrading to one of their EMS units. But maybe I need to reconsider.
jt
__________________
2019 Tiffin Phaeton 40IH
2005 Newmar Kountry Star Gas (Sold)
2022 JL Wrangler 4xe or 2017 Harley Ultra in tow
JT, Em & the boys, Kong & Baxter (rescued grey tabbies)
|
|
|
02-09-2017, 11:25 AM
|
#21
|
Senior Member
Join Date: Nov 2011
Location: Full time RV'er
Posts: 5,146
|
Like others, I wanted a Progressive because of their liberal return and repair policy, which I took advantage of when my remote display went south on the 30A protector. Now have a newer RV and soon after purchase installed the 50 amp. Found it on Craigs List for $150.
Progressive EMS-LCHW50 50 Amp EMS Surge & Electrical Protection
Power bay before ATS
Self Installed
Note, in many RVs, the water hose snakes through the electrical bay for some reason. This can spell disaster in numerous scenarios so I'd recommend the EMS be mounted up off the floor a couple inches. Although the cover is fairly watertight, the cable clamp entrances into the EMS are not.
Down here in Mexico, we had an overvoltage situation and my Progressive shut down at least 25 times over the 3 weeks before the electrical tap on the transformer was lowered. Than a week after that, a late arriving RV'er caused a crazy short of some kind, knocking out the entire RV park for 2 days. The Progressive protected me mostly, I just lost a SWiM power supply for my DirecTv but one camper lost nearly all their equipment, TV, DVR, chargers. The RV park replaced her stuff.
Here's my blog post about installing the Progressive, with pictures: Progressive EMS Installation
|
|
|
02-09-2017, 11:44 AM
|
#22
|
Registered User
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
|
My Electrical Management System of choice is the Progressive Industries 50 amp model EMS-HW50C.
Reasons are: excellent customer service, lifetime warranty on the unit including future owners, field replaceable control modules, super fast relay reaction time, user choice of two different power-up delay times, etc.
It is hardwired into the shore power supply cord directly after the Power-Master Voltage Booster and prior to the automatic transfer switch.
I installed it along with two displays, one outside in my Service Bay to view immediately after hooking up shore power and the second one is inside an overhead cabinet in the bedroom.
I believe it is the industries gold standard for excellence and performance. It has never let me down and has severed really bad power situations many times over preventing thousands of dollars worth of damage.
Photos below.
Dr4Film ----- Richard
|
|
|
02-09-2017, 02:48 PM
|
#23
|
Senior Member
Join Date: Oct 2014
Posts: 1,121
|
Quote:
Originally Posted by specmga1
I was all set to buy the Hughes unit until I read your post. What are the differences between the two - price, advantages, etc..?
Thanks!
|
The Hughes has a surge protector built in and the TRC does not. Also the Hughes is available direct from the manufacturer and the TRC must be purchased from a dealer (like the dreaded CW). Those are the reasons why I went with Hughes.
__________________
Phil and Laura (and Sam too!)
2024 Coachmen Beyond 22RB (on order)
|
|
|
02-09-2017, 02:58 PM
|
#24
|
Senior Member
Join Date: Dec 2004
Location: Edmond, Oklahoma
Posts: 414
|
Quote:
Originally Posted by Dr4Film
My Electrical Management System of choice is the Progressive Industries 50 amp model EMS-HW50C.
Reasons are: excellent customer service, lifetime warranty on the unit including future owners, field replaceable control modules, super fast relay reaction time, user choice of two different power-up delay times, etc.
It is hardwired into the shore power supply cord directly after the Power-Master Voltage Booster and prior to the automatic transfer switch.
I installed it along with two displays, one outside in my Service Bay to view immediately after hooking up shore power and the second one is inside an overhead cabinet in the bedroom.
I believe it is the industries gold standard for excellence and performance. It has never let me down and has severed really bad power situations many times over preventing thousands of dollars worth of damage.
Photos below.
Dr4Film ----- Richard
|
Did you use a splitter to allow for two displays? When I asked Derral about a second display, he said you could only use 1. I like the idea of seeing the power condition when I plug in, but also being able to see a display in the middle of the night without having to go outside!
__________________
2017 DSDP 4054 Spartan Chassis
|
|
|
02-09-2017, 03:03 PM
|
#25
|
Senior Member
Newmar Owners Club Freightliner Owners Club Spartan Chassis
Join Date: Apr 2012
Location: ON THE ROAD...SOMEWHERE
Posts: 6,973
|
Quote:
Originally Posted by BattChief
Did you use a splitter to allow for two displays? When I asked Derral about a second display, he said you could only use 1. I like the idea of seeing the power condition when I plug in, but also being able to see a display in the middle of the night without having to go outside!
|
The PI system requires a switch. My switch is in the power bay near one display. I select the power bay display when connecting and when done back to the one in the coach.
__________________
Don, Sandee & GSD Zeus. Guardian GSDs Gunny (7/11/15) & Thor (5/5/15)
2006 2015 DSDP 4320 4369, FL Chassis, 2013 CR-V 2020 Jeep Overland, Blue Ox Avail, SMI AF1.
[SIGPIC][/SIGPIC]
|
|
|
02-09-2017, 03:55 PM
|
#26
|
Senior Member
Winnebago Owners Club
Join Date: Nov 2010
Location: New York
Posts: 473
|
RMD3819, I have a remote monitor. The low voltage and open ground were identified by the surge protector with a written message on the viewing screen. The bad circuit breaker was identified and replaced by the park because the surge protector would not allow the connection to the power source.
Safe Travels and THE JOY IS IN THE RIDE
|
|
|
02-09-2017, 04:59 PM
|
#27
|
Registered User
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
|
Quote:
Originally Posted by BattChief
Did you use a splitter to allow for two displays? When I asked Derral about a second display, he said you could only use 1. I like the idea of seeing the power condition when I plug in, but also being able to see a display in the middle of the night without having to go outside!
|
The additional display comes with an A/B Switch to choose which display you want active. Because of the data cable you can only have one display active at one time, not both.
Look at the third photo of my previous post and you will see the A/B Switch on the right and the display is on the left.
Basically the single data cable coming out of the EMS-HW50C goes to the center of the A/B Switch. Then two data cables come out of the switch, one going to each display.
Dr4Film ----- Richard
|
|
|
02-10-2017, 01:18 AM
|
#28
|
Senior Member
Ford Super Duty Owner
Join Date: Oct 2011
Location: Diamond Bar, CA
Posts: 757
|
I am using the Progressive HC50 installed after the transfer switch so can monitor both shore and generator power. Would not allow 135 volt PM power in Cody, WY. I can avoid the generator breakers opening due to high a load and monitor volts, amps, and frequency for each leg of generator power to manage summer AC, appliances use, and charger. I normally boondock and have used shore power only a few times each year. The monitor is above the door with all 12 &120 electric controls.
__________________
2012 Bay Star 2901, 2 ACs, 5.5KW Onan, 765W solar & Outback FM-60, 800 AH Lifeline AGMs & Magnum MS2812 + AGS + BMK, Koni FSDs, Safe-T-Plus, Super Steer Rear Track Bar, MCD Duo shades w/powered cockpit, remodeled galley, Sumo springs and 2008 Tacoma 4x4 toad.
|
|
|
|
|