What to expect with 30 amp
Old 06-20-2010, 11:05 PM   #1
OldHiker is offline
Senior Member
OldHiker's Avatar
Join Date: Aug 2007
Location: Chester, NY
Posts: 222
I am on my way to Alaska and many of the campgrounds only have 30 amp power available. I have changed the setting in the Energy Management panel to 30 amp for shore power. What can I expect to be able to use? It seems that I can only get one a/c to operate as long as I turn off the electric to the water heater. How do I turn off the block heater, as it is not needed. Is it really affecting anything?

What is the proper setup? Do I have to set the gen-set to 30 amp or can that be left at 50 amp? What other advice can you offer? Of course I can always run the gen-set but not sure how my neighbors would like it?

__________________
2007 Newmar Essex 4508 All Electric
H2 toad
Lil Thor, my wingman
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-21-2010, 07:09 AM   #2
69RoadRunner is offline
Senior Member
69RoadRunner's Avatar
Join Date: Jun 2007
Location: Northern Virginny
Posts: 694
Well, your Newmar is a different animal from mine, but my block heater is a wall plug in the storage bay with the electric hookup. I just plug it in when needed, which isn't often.

I can run 2 a/c units, but mine are 13.5k units. I run the water heater on propane, but that's because the electric isn't working right not. I would not run 2 a/c units and heat with electric.

Really, I just use 1 a/c unit at a time when I'm on 30 amps even though I have EMS. I run the front unit during the day and the back unit at night.

I also shut off the a/c when I run the microwave. I guess I could let the EMS handle it, but I end up doing it myself anyway.

I would avoid using the generator unless absolutely necessary out of courtesy. People don't expect neighbors to be running generators when there are electric hookups.

There's also a device that people have mentioned that allows you to combine the 30 amp and 20 amp connections that campsites have available. I wish I could remember what it's called.

The threads I've seen on it bring up some controversial issues. People claiming to be electricians point out that the 30 amp and 20 amp circuits must be independent, so there isn't a problem combining them.

Campgrounds, however, might frown on the extra useage. I would look into it, though.

__________________
09 Newmar Ventana 3942 (bunkbeds for the munchkins)
08 Ford Taurus X AWD Toad
69 Road Runner Convertible 528 Hemi 4 Speed
  Reply With Quote
   
Old 06-21-2010, 08:33 AM   #3
JC2 is offline
JC2
Senior Member
JC2's Avatar


Newmar Owners Club
Texas Boomers Club
Join Date: Dec 2003
Location: Mo
Posts: 1,828
I believe the previous poster was referring to one of these at Camping World. 50-Amp RV Box Adapter - Item - Camping World or here from PPL RV parts, RV Cheater Box - 50 amps from 30 & 20 or here from Tweetys RV parts, Tweetys.com - RV Parts & Accessories - RV Hitches - Warn Products - Search
__________________
2004 Newmar DSDP 4015-370hp Cummins-Spartan Chassis-2008 Saturn Vue-Texas Boomers Member-FMCA #402879
  Reply With Quote
   
Old 06-21-2010, 01:31 PM   #4
OldHiker is offline
Senior Member
OldHiker's Avatar
Join Date: Aug 2007
Location: Chester, NY
Posts: 222
I could use the device if other outlets were available, but the current campground, Ground Zero in Dawson Creek, only has 30 amp. So that option isn't even available. I just think they have poor power here.
__________________
2007 Newmar Essex 4508 All Electric
H2 toad
Lil Thor, my wingman
  Reply With Quote
   
Old 06-21-2010, 01:47 PM   #5
Iron Man is offline
Senior Member
Iron Man's Avatar


Join Date: Jul 2006
Posts: 693
I addition enable the energy management. This for the most part will keep the coach from using no more amperage that what you have set. It will shunt off electrial devices it has control over. You will not be able to turn on the energey management unless the shore power is set on something less than 50 amps. We have used it on several occasions and it has worked well. Have fun.
__________________
John, Pam, Nicholas, Little Man and Aria
NKK 16073L
2007 Essex 4502 2004 Avalanche
  Reply With Quote
   
Old 06-21-2010, 08:57 PM   #6
clubmed98 is offline
Senior Member
clubmed98's Avatar
Newmar Owners Club
Join Date: Mar 2006
Location: Anywhere
Posts: 315
i had a different rig then i do now when i went up, 98 DS, but having seen many an RV er pop a 30 amp breaker you are correct on not running air and electric hot water heater at same time...never needed the air in 2008 once got north of fort nelson...on my dutch air the oasis control panel has a block heater on off switch for heating with hot water/coach heating boiler, even though not hooked up on the DA..on my 98 DS there was a plug in electric compartment and switch and can not remember where it on my DA..will look for it... with electric stove on you will draw large number of amps so may not be able to perk coffee, run stove, and fridge at same time..each appliance should list its watts and they can be converted to amps..google for formula, can't remember my basic electric class..and remember that you probably have close to an amp of parasitic load and most electric motors and compressors draw more amps at start up, peak amps, then they do when running..hope this helps..
__________________
I didn't survive cancer to die of stress
2009 DADP "4331" Alaska trip site and more
http://mytripjournal.com/Peddy-DickMar2-29667
  Reply With Quote
   
Old 06-21-2010, 10:26 PM   #7
"007" is offline
Community Moderator
"007"'s Avatar


Nor'easters Club
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Oct 2004
Location: Salisbury,Ma. 01952
Posts: 13,612
Your ESSEX should have all the power you need with 30 amps.
Most days temps will be in 80's and maybe 100 in flatlands of Big Delta.
You will not have any humidity its just a dry heat as in the winter its so dry your ear's would fall off if frozen.
People that have been to Alaska in recent years have found even cooler weather in summer months.
Its great country enjoy your stay and take lots of pictures. ENJOY
__________________
98KS,99MA,03-KS-3740 W-22 & 6 Ford's 3 V-10's
VISIT the NEWMAR QUICK TIPS & EASYMODS1&2
QUICK TIPS # 3
RV SYSTEMS & APPLIANCES & RECALLS
  Reply With Quote
   
Old 06-22-2010, 12:09 AM   #8
saydiver is offline
Senior Member
saydiver's Avatar
Join Date: Oct 2006
Location: on the road fulltiming
Posts: 242
No AC has been needed on our trip north to Alaska until yesterday afternoon when we stopped at Liard Hot Springs. Both the prov. park and the overflow lot were full, so we pulled into the Lodge campground, which was powered by a very loud generator. By late afternoon the campground was full.

We chose the end spot on the 30 amp row so our satellite dish would see the satellite over the top of the trees. The end spot worked well for our satellite dish, but bad for power and water pressure.

Our microwave/convection oven drew enough current to cause the pedestal voltage to drop under 105, which caused the Progressive EMS to disconnect from shore power forcing us to run the generator until our baking was completed. At the 30 amp setting the EMS keep disconnecting. At the 20 amp setting, along with shutting most systems down, we were able to run one ac.

Sue
__________________
2008 King Aire 4562 - custom
2012 Jeep Liberty Limited Jet
Our blog
  Reply With Quote
   
Old 06-22-2010, 07:03 AM   #9
clubmed98 is offline
Senior Member
clubmed98's Avatar
Newmar Owners Club
Join Date: Mar 2006
Location: Anywhere
Posts: 315
found my block heater switch..it in top right front area with ems and such next to tv...if you have to you will have to run gen or you may have to change your life style a little to accommodate the trip...a small price to pay for the greatness of the trip..
__________________
I didn't survive cancer to die of stress
2009 DADP "4331" Alaska trip site and more
http://mytripjournal.com/Peddy-DickMar2-29667
  Reply With Quote
   
Old 06-22-2010, 07:17 AM   #10
wa8yxm is offline
Senior Member


Workhorse Chassis Owner
Damon Owners Club
Join Date: Mar 2009
Posts: 8,070
With 30 amps you can generally run TWO big ticket items, plus television

Big ticket: A/C (note just one less you clean them) however in Alaska this should not be a problem even in August. Microwave, Converter if batteries are dead/very low (If bateries full the converter is a minor issue) Block heater, Water heater.

I routinely run 1 A/C and water heater Since I cleaned them last week I can actually run both A/C's but... Nothing else.
__________________
Home is where I park it!
  Reply With Quote
   
Old 06-22-2010, 07:49 AM   #11
Dav5942 is offline
Senior Member
Dav5942's Avatar


Join Date: Feb 2005
Location: Lake Oklawaha RV Resort(\
Posts: 1,185
We lived on a 2000 watt inverter for most of our trips to Alaska, sometimes up to 15 days at a time. No need for AC, etc.

__________________
High Line Toyhauler '07 Mid Engine 42' ATME 4153 w/ '96 Fatboy,Rubicon(w/4" Lift,Moto Metal whs,33X13.5" Mickey Thomps Baja Claw) in tow, 2-Grizzlys in garage
http://picasaweb.google.com/dav5942/...T2AlaskaBeyond
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric system monitor panel shows 30 amp when hooked up to 50 amp Magumba Winnebago Industries Owner's Forum 13 03-05-2010 08:09 PM
30 amp to 50 amp Electrical Upgrade mikwallace Winnebago Industries Owner's Forum 17 11-30-2009 10:17 AM
30/20 amp to 50 amp adapter soonerdave RV Systems & Appliances 21 04-02-2009 01:23 PM
Frank's Super Automatic 50 amp Voltage Booster and Surge Guard. Logthumper RV Systems & Appliances 2 08-29-2006 07:23 AM
Hughes Autoformer, 30 or 50 Amp??? Logthumper RV Systems & Appliances 5 08-06-2006 11:27 PM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 12:42 PM.