Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > THE OWNER'S CORNER FORUMS > Alpine Coach Owner's Forum
Click Here to Login
Register FilesVendors Registry Blogs FAQ Community Calendar Today's Posts Search Log in
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 07-11-2018, 09:36 AM   #1
Senior Member
 
TheKassman's Avatar
 
Join Date: Mar 2016
Posts: 169
50 amp vs 220

Staying at my brother in law and he has a 220 plug with an adapter to fit my 50A cord. Can I do that? I know 50A is two 115 lines. So is that the same. Can I plug in??
TheKassman is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-11-2018, 09:43 AM   #2
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
What does the plug look like that you are adapting to?
3 prong 220, NO.
4 prong 220, maybe.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 07-11-2018, 09:45 AM   #3
Senior Member
 
Winepress's Avatar
 
Join Date: Jul 2012
Posts: 1,737
Quote:
Originally Posted by TheKassman View Post
Staying at my brother in law and he has a 220 plug with an adapter to fit my 50A cord. Can I do that? I know 50A is two 115 lines. So is that the same. Can I plug in??


Have qualified electrician verify that the outlet is wired for RV 50 amp. Not wired correctly and you will most likely fry everything electrical in the RV.
Someone will probably post the drawings of the proper configuration.
__________________
2018 Dutch Star 4369
Everything was working fine, until it wasn't.
Winepress is offline   Reply With Quote
Old 07-11-2018, 09:51 AM   #4
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,400
…."normally," a 50 amp double pole plug in a residential setting is designed for use with an electric kitchen range or similar appliance. This type of plug and your 50 amp RV plug are the same. Not sure what you mean by an "adaptor"--usually these plugs are compatible with no adaptor required [this could be a "red flag"][normal 4-prongs config--round grd on top, 120v on either side, and neutral on bottom]. Double-pole breaker is required to provide phased 120V legs so neutral is not overloaded. Think I would double-check the breaker box and confirm that circuit is powered by a 50 amp/double-pole breaker....
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is online now   Reply With Quote
Old 07-11-2018, 10:01 AM   #5
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,500
Have him plug in his RV first.

Mr_D , said it , if the wall plug is 3 prong 220volt/50amp, don't hook up to it.
Here's the test for an RV outlet.
Attached Images
 
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 07-11-2018, 10:12 AM   #6
Senior Member
 
Join Date: Jul 2014
Posts: 35,446
If its got 4 blades its good. 3 blades is missing the neutral.

Your RV needed the neutral to split the 240 volts to 120 at your RVs main breaker panel..

If its 30 amp 240 volt service, it still must be 4 blade. The old 3 blade 240 volt service, with No neutral, has been phased out but still around for dryers.

http://www.myrv.us/electric/Pg/50amp_Service.htm
twinboat is offline   Reply With Quote
Old 07-11-2018, 10:55 AM   #7
Community Moderator
 
TonyDi's Avatar


 
Newmar Owners Club
Join Date: Feb 2011
Location: Point Pleasant Beach, NJ
Posts: 31,559
[QUOTE=Skip426;4285702]Have him plug in his RV first.

Now that's funny.
__________________
Tony & Ruth........... FMCA#F416727
2016 London Aire 4519, Freightliner chassis, Cummins ISX, 2018 Jeep Wrangler Unlimited, Blue Ox Avail with AF1. TST 507 TPMS
No amount of money can buy you an extra second of time.
TonyDi is offline   Reply With Quote
Old 07-11-2018, 11:24 AM   #8
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,848
Well............did you plug in OR have you found that using an adapter is NOT needed if BIL outlet is correct???
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 07-11-2018, 01:01 PM   #9
Senior Member
 
AKOne's Avatar
 
Join Date: Jun 2015
Location: Alaska
Posts: 904
This is the cheat sheet I made for testing 50 amp shore power: 50 Amp Test.pdf
__________________
Tim & Ruth
Alpine Coach 1999 40FDS, Cummins ISC 350
Project Restoration
AKOne is offline   Reply With Quote
Old 07-11-2018, 01:06 PM   #10
Senior Member
 
Join Date: Oct 2014
Posts: 7,882
As already posted, his 220 amp COULD BE OK OR COULD DESTROY YOUR ELECTRICAL SYSTEM.


As suggested, verify with a voltmeter. The critical issues is that his 220 is not a three wire with no neutral. If no neutral, it can not be used on any RV.



Follow the diagrams above to test.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is online now   Reply With Quote
Old 07-11-2018, 01:07 PM   #11
Senior Member
 
Cooperhawk's Avatar
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: Jun 2013
Location: 5 miles south of Lakeville, Mn
Posts: 3,047
If he says it's a 220 volt receptacle then you CANNOT plug into it.

I have several for my welders and large air compressor that are definitely 220. 50 amp is NOT 220 volts. It's two 110 volt lines with a return and ground.

It is entirely possible that someone might have wired the wrong receptacle into his system and you could fry everything.

Be very sure what you're plugging into.
__________________
Jim and Carol Cooper with Oreo the Kitty
FAA ATC ret, VFW, AL, VVA, NRA
US Army Aviation, MACV Vietnam 65-66
2012 Journey 36M, Cummings 360hp
Cooperhawk is offline   Reply With Quote
Old 07-11-2018, 01:45 PM   #12
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,400
CooperHawk----so help me understand--tell me the difference between your 220 volt "welder plug" and 220volt with two 120v legs for a 50 amp RV?
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is online now   Reply With Quote
Old 07-11-2018, 02:21 PM   #13
Senior Member
 
Join Date: Oct 2014
Posts: 7,882
Some welders use two hots and a ground.


Modern house 50 amp (like for a range) are the same as RV: two hots, ONE NEUTRAL and a ground. That is exactly how our home stove-top is wired.



So the answer is MAYBE-- depends on how his 220 is wired.



Said another way both are 220 (i.e. two hots). But one does not have the REQUIRED NEUTRAL.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is online now   Reply With Quote
Old 07-11-2018, 02:49 PM   #14
Senior Member
 
Join Date: Oct 2014
Posts: 7,882
Old Scout-- yes frustrating.


The only thing the OP said (have not seen any more posts by them since the original) is:


" 220 plug with an adapter to fit my 50A cord"


The "adapter" part has many of us suspecting this is not a "with neutral" outlet.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is online now   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
50amp & 120 or 220 Jazzylady Newmar Owner's Forum 14 09-15-2017 06:34 AM
New 6 volt 220 amp bats what charger? edsperfect MH-General Discussions & Problems 8 03-15-2015 02:54 PM
Woops! I put 220 V thru the coach....ideas on locating the short? tnsharon07 Newmar Owner's Forum 17 12-30-2008 08:59 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.