09-07-2008, 07:54 PM
|
#1
|
|
Senior Member
Join Date: Aug 2006
Posts: 254
|
When I run the front air conditioner along with either the electric water heater or the refrigerator on electricity, one of the two coupled 50Amp main breakers pops. I am wondering if this is a common problem with the 2000 Alpines or if I just have a breaker that needs replacing.
This occurs if I am plugged into shore power or running off the generator. When it is hot I must switch the water heater and refrigerator to operate off gas to keep the air running in the front.
__________________
Tom & Laurel
2000 Alpine Coach Limited 36FDS
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
09-07-2008, 07:54 PM
|
#2
|
|
Senior Member
Join Date: Aug 2006
Posts: 254
|
When I run the front air conditioner along with either the electric water heater or the refrigerator on electricity, one of the two coupled 50Amp main breakers pops. I am wondering if this is a common problem with the 2000 Alpines or if I just have a breaker that needs replacing.
This occurs if I am plugged into shore power or running off the generator. When it is hot I must switch the water heater and refrigerator to operate off gas to keep the air running in the front.
__________________
Tom & Laurel
2000 Alpine Coach Limited 36FDS
|
|
|
|
| |
|
09-08-2008, 06:34 AM
|
#3
|
|
Junior Member
Join Date: Jul 2008
Location: Dayton-Florida
Posts: 15
|
I had a 2000 40Ft same color as yours, wish I had kept it. I would get a amp probe and see at what amps breaker is tripping. The breaker is most likley weak and needs changing. I could run all and never tripped. Also check to see if all wiring is tight, from power cord and generator.
2005 40Ft FDQS
__________________
|
|
|
|
| |
|
09-09-2008, 06:45 AM
|
#4
|
|
Member
Join Date: Jul 2006
Posts: 35
|
We bought our 2000 new & have never had that problem.
(70,000 miles)
__________________
MAC & ANNE
36' 2000 MDS
Acura Toad
|
|
|
|
| |
|
09-09-2008, 07:30 AM
|
#5
|
|
Community Administrator
Newmar Owners Club
Join Date: May 2000
Location: Newark, DE
Posts: 13,893
|
With 50 amp service, which is really 100 amp service, you should be able to run just about everything at once.
At noted above, an amp probe will determine the actual amperage draw of each item.
The coach could also be miswired so that the loads are not balanced between the two legs and one leg is drawing more than 50 amps.
If the amp probe shows correct amperage, then the breaker would be suspect.
__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, '07 DSDP, '11 Virtual RV

|
|
|
|
| |
|
09-09-2008, 08:27 AM
|
#6
|
|
Senior Member
Alpine Owners Club
Join Date: May 2008
Location: Vancouver, WA
Posts: 1,719
|
Please do a search on generator wiring and also electrical issues. My guess, is the incoming service has loose connections, and the generator wiring has worked loose. You might not have had problems before, but things get loose on the coaches.
__________________
Monty & Janet - 2007 Alpine APEX 40 MDTS
S/N - 75715 - Enterprise ONE-RV Solutions
Master Certified RV Tech
|
|
|
|
| |
|
09-11-2008, 07:17 AM
|
#7
|
|
Senior Member
Join Date: Aug 2006
Posts: 254
|
This morning I took the breaker panel cover off to check the 50a main breaker connection and guess what I found? The red cable coming from the transfer switch to the main breaker wasn't tight. Without much force I was able to pull the cable out of the breaker connection. Tonight I'll fire up the generator and test the breaker using an amp probe.
__________________
Tom & Laurel
2000 Alpine Coach Limited 36FDS
|
|
|
|
| |
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|
Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 03:06 PM.