Electrical Conundrum

On a 3 week road trip and I have an electrical issue and would appreciate some help/advice.

1)Currently shore power is not working.
2)For a short time only a few outlets and the refrigerator worked on shore power but now nothing works.
3)The generator is working properly and the alternator is also recharging the batteries while we are driving down the road.
4)I had a RV service tech in Utah try to diagnose and fix this problem but he was only able to get my inverter working by replacing a bad fuse (Freedom 458 inverter).
5)With the inverter now working and after a bit of research I’m wondering if I have a transfer switch problem. If so, how do I confirm this is the root cause and next — what is the fix?

We are currently in Fort Collins, CO for a few days so if anyone knows of a crack RV tech in the area please let me know so I can get this problem resolved. Thanks!
-Max
__________________
Max Wasinger
2004 Alpine 36’ MDDS
Mjw2347 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-30-2019, 11:16 PM   #2
Senior Member
 
Dave Fernandez's Avatar
 
Alpine Owners Club
Join Date: Jun 2003
Location: Ontario, CA USA
Posts: 1,403
I think you diagnosed the problem being the transfer switch. The fix is replacement. It is located in the bays forward of the holding tanks on the ceiling. It is a fairly easy task just about RV store should have them in stock.
__________________
Dave Fernandez
2001, 38ft FDDS, 350 ISC, Tow 2018 RAM 1500
https://www.alpinesocal.com
Dave Fernandez is offline   Reply With Quote
Old 05-31-2019, 03:32 AM   #3
YC1
Senior Member
 
YC1's Avatar


 
Join Date: Jun 2011
Location: FL
Posts: 11,452
To be clear. The generator does make the inverter/charger work? And some of the outlets did work on shoreline.

Easy enough to check the transfer panel as mentioned. There may be a schematic on the inside of the cover to help or find one online.

IF you have an electric reel that could be causing the problem but more likely it is the transfer panel.

In a pinch you could bypass it or maybe swap the generator input with the shoreline input. A new one is not that difficult to change but one needs to take pictures first.
__________________
Certified Senior Electronic Technician, Telecommunications Engineer, Telecommunications repair Service Center Owner, Original owner HR 2008

.
YC1 is offline   Reply With Quote
Old 05-31-2019, 04:43 AM   #4
Senior Member
 
Jeep401's Avatar
 
Join Date: Nov 2017
Location: Marysville, WA
Posts: 556
We're you plugged in directly to a 50amp plug or were you by chance using an adapter? If a adapter is being used, it is mostly where the problem is.
__________________
Angelo & Leslie
2005 Alpine 36FDDS #75268
MARYSVILLE, WA.
Jeep401 is offline   Reply With Quote
Old 05-31-2019, 05:14 AM   #5
Senior Member
 
oscarvan's Avatar
 
Join Date: Feb 2017
Posts: 1,037
Yes, sounds like the transfer switch could be the problem. The tech should have looked in to that.

Follow the shore power cord in, it will lead to a box. When switching between sources you should hear pretty audible "CLICK" coming out of this box. (It's the relay driven contacts flopping back and forth)

It's job is to allow EITHER the generator OR the shore power in, as both at the same time is not good.

There are a few different designs out there, but most likely with the generator OFF and plugging in the shore power you should hear it. MOST transfer switches will favor the generator. SOME are at rest in that position. MANY are dual relay and EITHER will close when power is applied, with the generator having priority, and never both at the same time.

If you don't hear any clicking it's time to go in there with a volt meter and see what the transfer switch is doing.

(Some people have had results "whacking" the box to shake the relays loose, but that's not really a fix)
__________________
'20 RAM 3500, '20 Heartland Road Warrior 430 https://thecastle.blog/ Also: Eagle Cap 950 Before:'17 Berkshire 38A class A https://dragonship.blog/ '11 Heartland Cyclone TH, '11 Lance TC, '05 Keystone TT, '76 Coachmen class A and a '16 DIY Transit conversion........
oscarvan is offline   Reply With Quote
Old 05-31-2019, 06:24 AM   #6
Senior Member
 
Alpine Owners Club
Join Date: Sep 2017
Posts: 114
Electrical issue

Thanks for the immediate responses... 1) Yes, the generator makes the inverter work. 2) I have been using an adapter because 50 amp is not available. Off to Walmart to pick up a new adapter. 3) I will also try to replace the transfer switch if I can find one in FC...
__________________
Max Wasinger
2004 Alpine 36’ MDDS
Mjw2347 is offline   Reply With Quote
Old 05-31-2019, 06:32 AM   #7
Senior Member
 
Jeep401's Avatar
 
Join Date: Nov 2017
Location: Marysville, WA
Posts: 556
Quote:
Originally Posted by Mjw2347 View Post
Thanks for the immediate responses... 1) Yes, the generator makes the inverter work. 2) I have been using an adapter because 50 amp is not available. Off to Walmart to pick up a new adapter. 3) I will also try to replace the transfer switch if I can find one in FC...
I suspected, not uncommon to cause problems. I don't know for sure, but I don't think the transfer switch would only cut out one leg of your 110v, which sounds like what was going on, but it could be, I'm just not sure on that part. New adapter is cheap and easy to try first.
__________________
Angelo & Leslie
2005 Alpine 36FDDS #75268
MARYSVILLE, WA.
Jeep401 is offline   Reply With Quote
Old 05-31-2019, 07:09 AM   #8
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
This could all be an adapter or cord problem. Since the generator works that means that half of the transfer switch is working correctly. You could have a bad contact or coil in the transfer switch relay.

However, the first thing that I would verify is that you have both legs energized AT THE TRANSFER SWITCH from the shore power cord. If you are not comfortable with measuring voltages...do not do this. If you are, remove the cover and verify that you have 120 volts between the black and white and the red and white coming from the shore power cord. You should also hear a "clunk" when you plug in the shore power cable, which would be the shore relay pulling in. If it doesn't clunk, you either have no power to the switch or a bad relay coil or control board.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 05-31-2019, 08:16 AM   #9
Senior Member
 
Jim28730's Avatar
 
Newmar Owners Club
Join Date: Dec 2008
Location: Maggie Valley, NC
Posts: 903
X2 on the transfer switch.....
Jim28730 is offline   Reply With Quote
Old 05-31-2019, 01:01 PM   #10
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,840
Either the transfer switch (as discussed) OR the shore power cord

First symptom was the 'partial; working issue (fridge/some outlets---probably all fed from same bus bar)
Then nothing worked on shore power


Need to open transfer box and check/tighten ALL wire connections...shore in/gen in and main out---ALL AC Power OFF!!!!


Then plug in shore power cord and test that both legs are HOT (L1/L2)
Both hot...then test Main out. No main out---bad relays/connects in transfer switch


Both NOT hot..bad power cord
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 05-31-2019, 03:54 PM   #11
Senior Member
 
paul65k's Avatar


 
Alpine Owners Club
Join Date: Nov 2015
Location: Lake Havasu City, AZ
Posts: 3,014
My first thought was the transfer switch......if that's not the issue it ce the inverter not passing power through....something worth checking
__________________
Paul & Jean
2001 Alpine 36FDDS (74291)-3900W Solar, 13,440Wh (525Ah @24V) LiFePO4
2019 Jeep Grand Cherokee Trailhawk (Hemi)
2006 Alpenlite 32RL - Sold
paul65k is online now   Reply With Quote
Old 05-31-2019, 09:06 PM   #12
Senior Member
 
Alpine Owners Club
Join Date: May 2008
Location: Ocala, FL
Posts: 260
There is a Camping World about 25 miles south of Fort Collins on I 25. Also Trans West in Frederick Co works on Motorhomes. They are 35 miles south of Fort Collins on I 25.
Trans West does good work. I don’t know about Camping World but they may have parts.
__________________
Jim & Sandy
2008 34' FDDS Alpine
Limited SE
JLMunsil is offline   Reply With Quote
Old 06-01-2019, 12:13 AM   #13
Senior Member
 
Alpine Owners Club
Join Date: Sep 2017
Posts: 114
Electrical problem update

Update — Found a local RV service center (Nathan’s RV Service) in Fort Collins that carved out some time for us today. He determined my Inverter is defective and quickly designed a viable work around the Inverter so we now have shore power to get us through the balance of our trip. Will need to get the Inverter fixed or replaced when I get back to Southern California. Thanks for all of the comments, support and help...
__________________
Max Wasinger
2004 Alpine 36’ MDDS
Mjw2347 is offline   Reply With Quote
Old 06-01-2019, 06:01 AM   #14
Senior Member
 
veraken's Avatar


 
Monaco Owners Club
Vintage RV Owners Club
Holiday Rambler Owners Club
Join Date: Jul 2012
Location: Lexington, SC
Posts: 2,820
Here's a short video on how to test your transfer switch

__________________
Vera & Ken
1998 Holiday Rambler Imperial, RR8S Chassis
Cummins 6C8.3 mechanical engine, 325HP, 3060 Allison
Towing 2014 Ford Explorer
veraken is offline   Reply With Quote
Reply

Tags
electric, electrical, problem



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
tire conundrum litespeed Newmar Owner's Forum 15 07-25-2012 12:25 PM
Refrigerator conundrum Victoriaten Full-Timers 7 02-02-2012 06:43 AM
The Phoenix Conundrum Jack1234 Camping Locations, Plans & Trip Reports 8 11-26-2011 06:43 PM
Motorhome choice conundrum Jsoguinn Class A Motorhome Discussions 17 01-07-2011 09:45 AM
“Caliper Conundrum" letter in MH Magazine Richard 34A Workhorse and Chevrolet Chassis Motorhome Forum 11 02-01-2009 07:23 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:30 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.