Last weekend my generator was running but no power was getting to the coach. I took my 06 40 ft Alpine to the Cummins dealer and they say the generator is working fine but the transfer switch is bad. The inverter is working and the switch goes to shore power when plugged in. One year ago I had this switch replaced. Seems odd it would fail so quickly. Any ideas? Thanks, Doug

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-26-2011, 09:13 AM   #2
Monacoach is offline
Senior Member
Monacoach's Avatar
Join Date: Oct 2010
Posts: 628
We lost power from genny and it turned out to be the circuit board for the time delay. If this is the case with yours, you can by pass the circuit board by flicking a tiny dip switch located inside your transfer box.

__________________
2008 Holiday Rambler Vacationer 340 Cummins
  Reply With Quote
   
Old 07-26-2011, 09:28 AM   #3
njs42 is online now
Senior Member
njs42's Avatar


National RV Owners Club
Workhorse Chassis Owner
Join Date: Apr 2011
Location: Federal Way, Wa.
Posts: 1,235
Quote:
Originally Posted by nssracer View Post
Last weekend my generator was running but no power was getting to the coach. I took my 06 40 ft Alpine to the Cummins dealer and they say the generator is working fine but the transfer switch is bad. The inverter is working and the switch goes to shore power when plugged in. One year ago I had this switch replaced. Seems odd it would fail so quickly. Any ideas? Thanks, Doug
You ask for an opinion so here is mine.


The year of your Alpine is not listed but your join date is 2009. If that is the year of your rig then your old switch lasted as long as the new one-----I can't imagine these going out so often--mine is nine years old and I would be weepy if it quit tomorrow. Sounds to me like something else is going on in there----or just bad switches. Maybe try a different manufacturer of switches this time.

Or some Alpine type will be along and have something definate.

Good luck to you.
__________________
I do all my own stunts
03 Dolphin LX 6355, Workhorse W22, 8.1 vortec, 04 CR-V, Blue Ox, Brake Pro----Norm, Barb and
Doc(He's a PhD)
  Reply With Quote
   
Old 07-26-2011, 07:46 PM   #4
EngineerMike is offline
Senior Member


Join Date: May 2004
Location: Auburn, CA, Havasu, AZ & Mulege, BCS
Posts: 3,683
When the xfer switch goes bad it goes bad, whether a month or ten years. I've been on sales lots w/the xfer switch in a brand just-delivered new coach was bumping on/off/on/off...

Just make sure they checked that proper gen power (120V) was coming into the xfer switch and not switching (not just that the gen was "working" according to somebody's definition) before they replace xfer. Sometimes they have a dumb test that doesn't really test the component properly.
__________________
Baja-tested '08 2-slide 36'
Alpine: The Ultimate DIY'er Project
  Reply With Quote
   
Old 07-26-2011, 07:59 PM   #5
RJay is offline
Community Administrator
RJay's Avatar


Newmar Owners Club
Join Date: Jan 2010
Posts: 4,593
The contacts on the switch are not made for switching high current. If switching between shore power and the generator or vice versa don't switch more than 5 to 6 amps.
__________________
2007 Newmar DSDP 4023
Discovery is seeing what everyone else has seen and thinking what no one else has thought.
If you want to see what man made go East; if you want to see what God made go West.
  Reply With Quote
   
Old 07-26-2011, 08:20 PM   #6
bluefox is offline
Junior Member
Join Date: May 2011
Location: Deerfield, Ohio
Posts: 29
I just order a new power relay for my transfer switch it's rated at 30 amps.The coil was bad in the old one. replace it myself. cost for new relay 37.00 got it online
www.onlinecomponent.com Oh yea mine a 1991 MH
__________________
  Reply With Quote
   
Old 07-26-2011, 08:40 PM   #7
Tom and Patty is online now
Senior Member
Tom and Patty's Avatar


Alpine Owners Club
Join Date: Jun 2004
Location: Indy Lakes, Indianapolis, IN.
Posts: 1,365
Quote:
Originally Posted by EngineerMike
Sometimes they have a dumb test that doesn't really test the component properly.
Would that be the part where I hold onto the output genset cable ends to tell you it's working?:-)
__________________
Tom, Patty and Abby Kat, Greenwood, Indiana
2000 36' FDS 72232, Towing '05 PT GT Conv
Our Photos
  Reply With Quote
   
Old 07-26-2011, 08:58 PM   #8
Dale777 is offline
Senior Member
Dale777's Avatar
Join Date: Apr 2004
Location: TX
Posts: 495
nssracer,

If you are comfortable using a Multimeter around alternating current, you can test the GenSet input to the transfer switch yourself. The transfer switch is in the basement, located on most model years attached to the ceiling area of a basement cross member.

Do NOT do this if you don't feel skilled at this task. If you DO feel skilled at this type of electrical measurement work, simply take the cover off the transfer switch and measure the voltage on the input to the transfer switch when the GenSet is running, then measure the voltage on the output of the transfer switch. Do the same type measurements when connected to shore power, then make comparisons. You should be able to diagnose whether proper voltage is getting to the transfer switch from the GenSet.

If you don't want to do this measurement yourself, then ask the Cummins technician what his test results were in doing what I described.
__________________
Dale & Karin
2006 Alpine Coach Limited 36FDTS
Watercolor Artist: http://www.cindydaunis.com/
  Reply With Quote
   
Old 07-27-2011, 12:37 AM   #9
takepride is offline
Senior Member
takepride's Avatar


Alpine Owners Club
Join Date: Aug 2007
Location: Long Beach, CA
Posts: 1,505
If the tech's idea of the generator working, includes only that it is running, it could just be the breaker on the generator is tripped and not sending power. Mine does that occasionally, especially when I abuse it by overloading it.

As mentioned, if your are okay using a multimeter, just follow the flow.
__________________
2003 Alpine 40FDTS (400HP)
Long Beach, CA
  Reply With Quote
   
Old 07-27-2011, 07:01 PM   #10
Jim A is offline
Senior Member
Jim A's Avatar
Join Date: Jun 2005
Posts: 691
Takepride,

I had the same thing happen with the circuit breaker on the generator. But only once so far. Not sure what made me look at it. I was ready to get the multimeter out.
__________________
Jim A
'04 Alpine Coach 36' MDDS
  Reply With Quote
   
Old 07-27-2011, 07:08 PM   #11
Dr4Film is offline
Senior Member
Dr4Film's Avatar


Monaco Owners Club
Join Date: Oct 2009
Location: Anchorage, AK
Posts: 1,194
Send a message via Skype™ to Dr4Film
If your Transfer Switch is an IOTA, Get rid of it and never buy another one. It's a POS.

Replace it with an ESCO Transfer Switch and you won't be sorry.

Only My Opinion.

Dr4Film ----- Richard.
__________________
2002 Monaco Windsor PBT 40Ft. (R HOME) - 26Ft. 2006 Pace Trailer (R JUNK).
Trailer Has 06 VUE (R TOWD) 04 Victory Alen Ness Edition (R RYDE) & Junk.
Full-Timer 9 Yr's & Still Lov'n It. Now in Anchorage Alaska for Two Months.
  Reply With Quote
   
Old 07-27-2011, 07:09 PM   #12
EngineerMike is offline
Senior Member


Join Date: May 2004
Location: Auburn, CA, Havasu, AZ & Mulege, BCS
Posts: 3,683
Tom- Wish I could be there for the test, but I can't. Have Patty video the process and post the link here so we can all have the benefit of the outcome
__________________
Baja-tested '08 2-slide 36'
Alpine: The Ultimate DIY'er Project
  Reply With Quote
   
Old 07-27-2011, 11:30 PM   #13
takepride is offline
Senior Member
takepride's Avatar


Alpine Owners Club
Join Date: Aug 2007
Location: Long Beach, CA
Posts: 1,505
Quote:
Originally Posted by EngineerMike View Post
Tom- Wish I could be there for the test, but I can't. Have Patty video the process and post the link here so we can all have the benefit of the outcome
Especially if you're not good with a multi-meter!
__________________
2003 Alpine 40FDTS (400HP)
Long Beach, CA
  Reply With Quote
   
Old 08-01-2011, 01:27 AM   #14
Rick J Fisher is offline
Senior Member
Rick J Fisher's Avatar
Alpine Owners Club
Join Date: May 2008
Posts: 108
My 2007 has the Surgeguard transfer switch. The little Surgeguard panel shows the voltage on each leg of the "50" amp system. Inside the box are three relays (called contactors by some) that switch the two legs and the neutral from shore to generator power. One of the contactors failed so it wasn't switching. I was able to push a button on the contactor to complete the circuit but it would not hold. Surgeguard repaired it under warranty but the box is a bear to remove. It is hard wired so all the heavy wires have to be removed to get the box out. When I re-installed it I used three sets of "50" amp connectors which i wired on short lengths of cable to the box. After installation, I just plugged it in. If it fails again, I can replug the coach feed directly in to the shore line. The problem with this solution is the connectors are expensive and there is not much room for all the cables around the box.

__________________
Rick J Fisher
2007 Alpine 34FDDS Limited SE
Main Passenger, Judy Fisher
  Reply With Quote
   
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Automatic Transfer Switch (Power Switch) Ragman National RV Owner's Forum 2 07-18-2011 09:51 AM
Transfer Switch Dilemma migrantdawgs RV Systems & Appliances 2 06-21-2011 06:51 PM
LPT50CA Transfer Switch RedHotSoup Alpine Coach Forum 7 04-29-2011 09:24 AM
Transfer switch hums djhinds Class A Motorhome Discussions 1 12-04-2010 07:54 AM
Transfer Switch SC RV'er Alpine Coach Forum 12 03-24-2010 10:58 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 06:59 PM.