50 amp Y adapter

This might be a good question for Twinboat or anyone with electrical ability,

i have a 31 foot national seaview with original 30 amp service.

i have 2 roof air conditioners. one roof ac is a dometic 13500 btu unit.
the other ac is a 15000 btu dometic unit.

i cannot run both air condtioners at the same time unless i use my generator.

i really dont like to use my generator as it is noisy and i dont want to disturb
my campground neighbors with my loud generator running all night.

however, i on occasions i would like to run both air units at the same time.

i was wondering if i bought one of those 50 amp to 30 amp y adapter
splitters if i could run both air conditioners safely at the same time??

if this will work for me it will be a lot cheaper than converting my coach
over to 50 amp service. thanks for any help or suggestions.

that 50 amp y adapter is only $33 on amazon with free shipping, sounds
like a good deal to me. even if i cant run both airconditioners at the same
time it probably is a good idea to carry one of these in the coach??

thanks for any help or insight.
mr. seaview is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-16-2019, 11:37 PM   #2
Senior Member
 
chboone's Avatar


 
National RV Owners Club
Ford Super Duty Owner
Join Date: Sep 2010
Location: Horse Town USA, CA.
Posts: 3,781
The Y adapter won't help you still only have 30 amp shore cord and breaker panel. The issue is the compressor starting amps (in rush). What you need is a soft start for the air conditioners.
https://www.microair.net/collections...nt=30176048267
__________________
1999 35 ft. Dolphin 5350, F53, Banks System, 5 Stars Tune, Air Lift Air Bags, Koni Shocks, Blue OX TruCenter, TigerTrak track bars F&R, Roadmaster 1-3/4" rear auxiliary sway bar, 2004 F450 Lariat Pickup 6.0 Diesel Crew Cab DRW, 4X4, GVWR 15,000, Front GAWR 6,000, Rear GAWR 11,000, GCWR 26,000,1994 36ft Avion 5er, GVWR 13,700, 2,740 Pin Weight.
chboone is online now   Reply With Quote
Old 09-17-2019, 12:32 AM   #3
Junior Member
 
damcrv's Avatar
 
Join Date: Aug 2019
Posts: 28
Hey Seaview, I know a bit about this power stuff. The way some Motorhomes are wired is still a little vague. To answer the question no. You have a 30A 120V shore power connection that limits your shore power to 3600W. Those A/C units are too much for that circuit. Same thing happens o the 50A when adapted to the 30A outlets. Can’t run them both.
damcrv is offline   Reply With Quote
Old 09-17-2019, 01:52 AM   #4
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 3,165
some say they can run 2 A/C's on 30 amps. If they can then that's all they can run.

30 amp service is 120 volts. 50 amp service is 240 volts. The adpt will not provide this. You only get 30 amps to your rig. You would need to replace your shore power cord and your Main Breaker box. $$$$$

The 50/30 adpt allows you to plug into 50 shore power if you have a bad 30 amp outlet. It will only give you 50 amps at 120 volts BUT your main breaker limits you to 30 amps.
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is offline   Reply With Quote
Old 09-17-2019, 03:07 AM   #5
Senior Member
 
Join Date: Jul 2014
Posts: 35,402
You will need a second power cord coming from the RV second air conditioner to one of the Y adaptor connectors.

Your generator has 2 power feeds, ( a 30 and a 15/20 amp ) coming from it, that's why it can run 2 air conditioners.

An electrician can find and figure it out but its not that simple if you still want to run the second air off the generator.
twinboat is offline   Reply With Quote
Old 09-17-2019, 05:54 AM   #6
Senior Member
 
Join Date: Aug 2017
Posts: 2,101
What happens when you try to run both A/C units at the same time on shore power ? Does the main breaker or pedestal breaker trip ? If you are tripping the pedestal breaker , the adapter might work , but then your main breaker might trip . If your main is tripping, it won't help. Installing a soft start on one unit will work, but running the 2 units will max out the 30a main.
__________________
1993 Tiffin Allegro Bay 32'
Soppy is offline   Reply With Quote
Old 09-17-2019, 08:12 AM   #7
Senior Member
 
winniman's Avatar
 
Join Date: Jan 2013
Location: Muskoka Ontario Canada
Posts: 3,142
The adapter could possibly feed 240 volts into the camper, which is designed for only 120 volts. Lots of info on what happens to your camper if you feed the higher voltage in. Don't do it.
__________________
2000 coachmen santara 370 5.9 cummins isb
winniman is offline   Reply With Quote
Old 09-17-2019, 09:36 AM   #8
Senior Member
 
Join Date: Jul 2014
Posts: 35,402
Quote:
Originally Posted by Soppy View Post
What happens when you try to run both A/C units at the same time on shore power ? Does the main breaker or pedestal breaker trip ? If you are tripping the pedestal breaker , the adapter might work , but then your main breaker might trip . If your main is tripping, it won't help. Installing a soft start on one unit will work, but running the 2 units will max out the 30a main.
It won't do it. There is a panel to select which A/C you want to run while on 30 amp power. Both isn't an option.

On generator, you can run both because its a 5500 watt or more generator with 2, 120 volt outputs.
twinboat is offline   Reply With Quote
Old 09-17-2019, 09:42 AM   #9
Senior Member
 
powercat_ras's Avatar
 
Winnebago Owners Club
Solo Rvers Club
Join Date: May 2015
Posts: 1,834
Something like this might work for you...

30 to 50 modification
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2020 Ford Escape Hybrid
[SIGPIC][/SIGPIC]
powercat_ras is offline   Reply With Quote
Old 09-17-2019, 10:05 AM   #10
Senior Member
 
xrated's Avatar
 
Join Date: Jan 2017
Location: "Murvul", TN
Posts: 1,665
Quote:
Originally Posted by winniman View Post
The adapter could possibly feed 240 volts into the camper, which is designed for only 120 volts. Lots of info on what happens to your camper if you feed the higher voltage in. Don't do it.
Uh, no! The 50 to 30A adapter only picks up one of the hot legs from the 50A receptacle. If you look, there are only three female connection points on the 30A end of the adapter....a hot, a neutral, and the ground.
__________________
2016 F350 Crew Cab Dually Diesel King Ranch 4x4
2018 Grand Design Momentum 394M Toy Hauler
Excessive Payload Capacity is a Wonderful Thing!
xrated is offline   Reply With Quote
Old 09-17-2019, 10:11 AM   #11
Senior Member
 
Join Date: Jul 2014
Posts: 35,402
Quote:
Originally Posted by xrated View Post
Uh, no! The 50 to 30A adapter only picks up one of the hot legs from the 50A receptacle. If you look, there are only three female connection points on the 30A end of the adapter....a hot, a neutral, and the ground.
But there are 2, 30 amp outlets on the Y. Each will be using a different leg of the 240 volts plug.
twinboat is offline   Reply With Quote
Old 09-17-2019, 07:25 PM   #12
Senior Member
 
Join Date: Aug 2017
Posts: 2,101
Quote:
Originally Posted by twinboat View Post
It won't do it. There is a panel to select which A/C you want to run while on 30 amp power. Both isn't an option.

On generator, you can run both because its a 5500 watt or more generator with 2, 120 volt outputs.

That makes sense to me. If both cannot be selected , there is no no way an adapter will allow operation of both units !
__________________
1993 Tiffin Allegro Bay 32'
Soppy is offline   Reply With Quote
Old 09-17-2019, 07:39 PM   #13
Senior Member
 
Join Date: Jul 2014
Posts: 35,402
Quote:
Originally Posted by Soppy View Post
That makes sense to me. If both cannot be selected , there is no no way an adapter will allow operation of both units !
That's what I said in post #5.
twinboat is offline   Reply With Quote
Old 09-17-2019, 08:35 PM   #14
Senior Member
 
Join Date: Aug 2010
Posts: 2,772
50 amp Y adapter

Quote:
Originally Posted by twinboat View Post
But there are 2, 30 amp outlets on the Y. Each will be using a different leg of the 240 volts plug.


It’s a 50 amp plug not a 240 volt plug. The 2 30 amp outlets on the Y will both be carrying the current (30 amps) as they are sharing ONE leg of the 50a!
__________________
Terry & Alice
2006 Bounder 38L DP
2012 GMC Terrain
firedoc is offline   Reply With Quote
Reply

Tags
ada



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using an adapter to plug 30 amp RV to 50 amp service Dmiles MH-General Discussions & Problems 45 05-16-2018 06:56 PM
30 amp plus 20 amp to make 50 amp Adapter? okmunky RV Systems & Appliances 14 05-15-2016 06:58 PM
30 amp v/s 50 amp adapter cord ?? tbbronson RV Systems & Appliances 9 05-05-2014 09:00 AM
30 amp male to 50 amp female adapter arnoldjf9191 Class A Motorhome Discussions 33 10-13-2011 05:07 PM
30/20 amp to 50 amp adapter soonerdave RV Systems & Appliances 21 04-02-2009 01:23 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:20 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.