Quote:
Originally Posted by CalPauly
I have a 1998 Sea Veiw 8330 with a Intellitec EMS panel that flashed a E1 error code. everyrthing seemed to work fine, I reset the shore power to clear and all was well. Does anyone know what may have caused this code and what I can do to avoid a repeat? It was my first time hooking up to shore power with this MH. Im new to the MH world and is my first MH.
Thank you and happy holidays!
CalPauly 
|
Hi... got his from another Forum... Strictly FYI...
First step.. UNPLUG from shore power... You can also call them, they are awesome techs to work with.. Good Luck... I'm sure this forum will give you plenty of help..
From the manual:
AC Overload
(the status indicator
blinks on 4 times every
4 secs)
The inverter has turned off because the
connected loads are larger than the
inverters output capacity or the output
wires are shorted.
Reduce the AC loads connected to the
inverter or remove all AC output wiring and
restart the inverter.
More from the manual:
Protection Mode
There are five fault conditions that will cause the inverter to
shutdown; Low Battery, High Battery, Over-temperature, AC
Overload, and Internal faults. If your inverter has shutdown,
monitor the status indicator and count the number of blinks that
occur every four seconds to determine the particular reason for
the shutdown. Once you have determined the reason for the
shutdown, refer to the Troubleshooting section to help diagnose/
clear the fault condition.
• Blinks on 1 time every four seconds - Low Battery fault.
• Blinks on 2 times every four seconds - High Battery fault.
• Blinks on 3 times every four seconds - Over-temperature fault.
• Blinks on 4 times every four seconds - AC Overload fault.
• Blinks on 5 times every four seconds - Internal fault.
Over-temperature condition
(the status indicator blinks on 3 times every 4 secs)
The internal temperature of the inverter has risen above acceptable
limits; caused by loads too great for the inverter to operate continuously, or by lack of ventilation to the inverter.
When the unit has cooled, it will automatically reset and resume operation.
Reduce the number of electrical loads that you are operating, this will avoid a repeat Overtemp shutdown if the cause was too many loads for the ambient conditions.
Check ventilation around the inverter, ensure cool air is available to pass-through the inverter.
More info....