03-05-2017, 10:41 PM
|
#1
|
Member
Tiffin Owners Club
Join Date: Nov 2016
Location: On the Move . . .
Posts: 57
|
2016 Phaeton - Magnum AGS Control
Enabled AGS to turn on generator when falls below 11.9V & set to run for 1 hr. Seems to work.
However, more than once, I've gone to check later in day (when generator is off ) "AGS Control" & it's been disabled.
I am very careful not to disable it while I'm checking, so need to know why / how it's disabling.
Sometimes, during the AGS initiated 1 hr generator run I will turn off generator using on / off switch on the dash. Could this throw AGS into disable?
Between automatic runs, sometimes I'll manually turn on the generator for 30 - 40 minutes, then turn it off. Could that disable the auto-start?
Any other ideas? Trying to figure out if user error or if I need it serviced?
Thx!
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
03-05-2017, 11:07 PM
|
#2
|
Senior Member
Tiffin Owners Club Appalachian Campers Mid Atlantic Campers Coastal Campers Freightliner Owners Club
Join Date: Jan 2015
Posts: 1,622
|
Yes, when you manually stop the generator, it turns off the autostart. See the ME-AGS-N manual, page 53
__________________
DaveB, Raleigh, NC
2015 Tiffin RED 33AA, w/Honda CRV
VMSpc, Magnum BMK/ARC50
|
|
|
03-05-2017, 11:54 PM
|
#3
|
Member
Tiffin Owners Club
Join Date: Nov 2016
Location: On the Move . . .
Posts: 57
|
Quote:
Originally Posted by Kiawah
Yes, when you manually stop the generator, it turns off the autostart. See the ME-AGS-N manual, page 53
|
Thx!
|
|
|
03-06-2017, 03:01 PM
|
#4
|
Registered User
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
|
"Sometimes, during the AGS initiated 1 hr generator run I will turn off generator using on / off switch on the dash. Could this throw AGS into disable?"
YES
to disable this 'feature' - go into your Magnum panel settings for AGS, under the 'TYPE' setting, change it from 'RV' to 'Other'.
This provides for the AGS to remain in Enable mode, even if you turn it off manually after the AGS has already started the generator. In essence, disabling the disabling!
most of us learn this by the same process you have - it is certainly NOT intuitive that the setting option of RV and OTHER would be this way, since you are, after all, in an RV!
|
|
|
03-23-2017, 08:18 PM
|
#5
|
Junior Member
Tiffin Owners Club
Join Date: Aug 2006
Location: Livingston, TX
Posts: 15
|
I'm concerned that you're setting the AGS to only run for an hour and keep the battery charge up. With over 3000 hrs on our Onan 10k generator, charging 3 8D AGS batteries, we sčem to need about 2 1/2 hrs daily when dry camping. Of course, if using more power, such as the ACs or microwave, we run the generator far more. As I said above, we have 3000 hrs on our generator since 2010.
__________________
Orv Hazelton
2010 Phaeton 2011 Honda CR-V Toad
Rock 'N' Rollin Allegros Club #210
|
|
|
03-24-2017, 11:17 AM
|
#6
|
Senior Member
Tiffin Owners Club Appalachian Campers Mid Atlantic Campers Coastal Campers Freightliner Owners Club
Join Date: Jan 2015
Posts: 1,622
|
Quote:
I'm concerned that you're setting the AGS to only run for an hour and keep the battery charge up. With over 3000 hrs on our Onan 10k generator, charging 3 8D AGS batteries, we sčem to need about 2 1/2 hrs daily when dry camping. Of course, if using more power, such as the ACs or microwave, we run the generator far more. As I said above, we have 3000 hrs on our generator since 2010.
|
What's nice about installing the Magnum BMK and ARC-50, is you can change the way the AGS works. For instance, you can have it trigger ON if the battery bank gets below 60% of capacity, and turn OFF when it achieves a state of charge of 85%. Values are all adjustable, and you know exactly how much capacity your batteries have.
__________________
DaveB, Raleigh, NC
2015 Tiffin RED 33AA, w/Honda CRV
VMSpc, Magnum BMK/ARC50
|
|
|
03-28-2017, 01:05 PM
|
#7
|
Senior Member
Join Date: Mar 2016
Location: South of Houston Tx.
Posts: 395
|
I thank you for this answer, I also set my AGS to " auto therm" and even though I do not use the dash button it still reverts back to the OFF position,,
maybe now I can get it to stay enabled....
thanks
__________________
2018 Entegra Anthem 44B Victory Blue..
2016 F150 4x4 Platinum and 2014 Jeep Rubicon X
M&G brake on both. Using hydralift for 2014 HD CVO Limited
|
|
|
04-04-2017, 09:53 AM
|
#8
|
Member
Tiffin Owners Club
Join Date: Dec 2016
Location: Usa
Posts: 56
|
newbie question
Hi all,
I have a question. We are new to all this so excuse me if this is stupid but, in the manual it says to turn off all items that will draw power from the generator before turning the generator on and then again before turning it off. If you set up the AGS to turn the generator on and off automatically how do you insure nothing is on when it starts and stops? Thanks!
|
|
|
04-04-2017, 01:43 PM
|
#9
|
Senior Member
Join Date: Mar 2016
Location: South of Houston Tx.
Posts: 395
|
time delay, A/c units will not start until Gen is running, and a/c units shut down and off. then Gen will idle down and shut off long as there is no demand for any power anything again,
__________________
2018 Entegra Anthem 44B Victory Blue..
2016 F150 4x4 Platinum and 2014 Jeep Rubicon X
M&G brake on both. Using hydralift for 2014 HD CVO Limited
|
|
|
04-05-2017, 02:21 PM
|
#10
|
Member
Tiffin Owners Club
Join Date: Dec 2016
Location: Usa
Posts: 56
|
Thanks Slice!
So let me get this straight, the ACs simply won't start unless the generator is already on (or hooked up to electric)? And the ACs will turn off automatically before the generator is scheduled to shut down (I'm working under the assumption that I program the generator to run automatically through the AGS)? I guess if you are hooked up to electric there would never be a reason to run the generator so a scenario like that isn't worth worrying about.
What about the fridge? Is the draw too low to worry about turning it off and on with generator use or does it also turn off and on when using the AGS to run the generator? I think I read that some people don't worry about the fridge being on or off when they start and stop their generators.
As you can see, I'm worried about messing up my transfer switch or whatever it is in the generator that gets screwed up when you start and stop it while running things that put a load on it.
Thanks
|
|
|
|