That kind of sounds like duct blockage may be your problem. Note it is just a guess but low air flow kind of points to that.
Tom
|
Duct blockage is a possibility, but more likely excessive friction from too small duct work cross section.
Typical air temperature drop from air input thru output coils is 18 to 20 degrees...max. Common to see 3 to 5 degrees temperature increase per 10 feet of duct length.
Temperature drop is not determined by number of Btu's. The volume of cooled air increases with Btu rating. The volume of cooled air, if it is high enough, can overcome the air leakage, and insulation heat leakage, and reduce the interior temperature.
The higher the losses, the higher the room temperature at max cool. Recirculating the air thru the coils can bring the room temperature down to any reasonable level and will be limited only by air and insulation leakage.
Time to make some temperature delta measurements. If the temp drop across the coils is 18 to 20 degrees, the air conditioner is working properly.
The numbers you give us indicates the system is working at the limit and you have too heavy a heat load.