I have a surge guard Model 34750 and it suggests I have power from the pole but I have no power in the motorhome, a tiffin allegro bay fred 37qdb - I reset the breakers I know about
is there a master breaker for the motorhome beacause all I can find is a panel in the bedroom but no breaker appears to be a master
Help as we are powerless in NH in Irene...
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
08-28-2011, 04:05 PM
|
#2
|
|
Senior Member
Freightliner Owners Club
Join Date: Aug 2008
Location: New Jersey
Posts: 1,216
|
Here are just some obvious things to check as I wasted about 30 minutes this morning during Irene in NJ when I didnt' check that the GFI button was reset.
1. Do you have any lights? If not, there should be a coach disconnect button near the front entrance door or steps.
2. Reset every GFI in the coach.
3. Does your inverter have a display and control panel. Make sure the inverter is on. (mine sometimes turns off and says 'bad AC').
4. Your genset should have a circuit breaker switch right by the on/off switch ON the genset (not by the on/off switch in the coach).
5. The inverter has a push button circuit breaker right on the chassis. Check that.
Good luck!
__________________
Tom and Katharine
'07 Winnebago Tour 40TD, 400hp Cummins
RVing for 14 years with three boys
|
|
|
|
| |
|
08-28-2011, 04:10 PM
|
#3
|
|
Senior Member
Tiffin Owners Club Workhorse Chassis Owner
Join Date: May 2005
Location: Full-timers - Home is where we park it.
Posts: 2,477
|
I'm not aware of Tiffin having a master breaker other than the ones in the main box, but then again, our coach is several years old so yours may be different.
The surge guard will shut down power if there is a fault condition such as reversed polarity, missing ground, high or low voltage. There should be a readout or indicator lights on the surge guard that indicates if fault has occurred. If there are no warnings, try plugging in without the surge guard to see if you have power.
The other possibility is the transfer switch is faulty. You should hear a soft thump coming from the electrical bay a few seconds after you plug in. That would be the sound of the transfer switch kicking on. If you don't hear a thump, try running the genset to see if you have power.
__________________
05 Allegro Bay 37DB W24//06 Saturn Vue V6 AWD
Full-timers...Home is where we park it. 
Check out our blog: Living Our Dream
|
|
|
|
| |
|
08-28-2011, 04:18 PM
|
#4
|
|
Member
Join Date: Nov 2009
Posts: 70
|
Quote:
Originally Posted by RVThere
Here are just some obvious things to check as I wasted about 30 minutes this morning during Irene in NJ when I didnt' check that the GFI button was reset.
1. Do you have any lights? If not, there should be a coach disconnect button near the front entrance door or steps. DONE
2. Reset every GFI in the coach. DONE
3. Does your inverter have a display and control panel. Make sure the inverter is on. (mine sometimes turns off and says 'bad AC'). DONE lights all fine
4. Your genset should have a circuit breaker switch right by the on/off switch ON the genset (not by the on/off switch in the coach).DONE
5. The inverter has a push button circuit breaker right on the chassis. Check that. ----------------Where is this located????
Good luck!
|
Surge protected flashes for 10 seconds and then goes out
|
|
|
|
| |
|
08-28-2011, 04:24 PM
|
#5
|
|
Member
Join Date: Nov 2009
Posts: 70
|
Quote:
Originally Posted by paz
I'm not aware of Tiffin having a master breaker other than the ones in the main box, but then again, our coach is several years old so yours may be different.
The surge guard will shut down power if there is a fault condition such as reversed polarity, missing ground, high or low voltage. There should be a readout or indicator lights on the surge guard that indicates if fault has occurred. If there are no warnings, try plugging in without the surge guard to see if you have power.
The other possibility is the transfer switch is faulty. You should hear a soft thump coming from the electrical bay a few seconds after you plug in. That would be the sound of the transfer switch kicking on. If you don't hear a thump, try running the genset to see if you have power.
|
Generator works fine...Surge protected flashes for 10 seconds and then goes out I am beginning to think the power out of the pole is faulty
|
|
|
|
| |
|
08-29-2011, 05:19 AM
|
#6
|
|
Junior Member
Tiffin Owners Club
Join Date: Aug 2011
Location: Helendale California
Posts: 19
|
if your generator is working and supplying power to the rv than its either shore power or the relay i would be suspicious of the shore power, we had a similar problem in Chicago power appeared OK but would only run one ac and couldn't run the washer or 2nd ac Generator ran every thing fine next stop everything worked fine and ever since'
I figured bad ground and was glad the rv didn't burn to the ground
__________________
Chuck 2004 Allegro bus
 If its worth doing, it is worth doing wrong till you get it right!
|
|
|
|
| |
|
08-29-2011, 08:41 AM
|
#7
|
|
Member
Join Date: Nov 2009
Posts: 70
|
As it turns out it was the shore power... as Irene blew through the voltage in the shore line exceeded 132 volts and our surge protector is designed to shut down when it hits this threshold... it would blink 8-10 seconds and thenshow we had shore power but would stop it before it got to the coach... looks like we jsut paid for that investment!
|
|
|
|
| |
|
08-30-2011, 12:03 PM
|
#8
|
|
Senior Member
Nor'easters Club Tiffin Owners Club
Join Date: Jan 2009
Location: ma
Posts: 274
|
Sounds like that small investment paid off for you.  Glad to hear no lasting issues! My surgeguard has bailed me out twice in the 3 years I've had it!
Dan
__________________
Dan 2008 Allegro 32 BA FRED, Honda Fit
There are 10 types of people in this world. Those who know binary, and those who don't.
|
|
|
|
| |
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|