Hi All,
Our air conditioning is working sporadically when running the generator. Both air conditioners are fine with shore power. Symptoms - both will run on generator, sometimes neither will, sometimes 1 or the other. The thermostat will not show any display for 1 or both. When there isn't any display, there isn't any air conditioning. I have electrical schematics and am trying to trace the 5amp 12v control power for the thermostats. The 2004 39S has the Intellitec system and I think the problem lies within that control system when running on the generator. Bumps will cause the air conditioners to start and or stop. I think I may have a grounding problem. I'm in the process of joining the DOAI site but that takes up to 4 days to get forum credentials, so I decided to see if someone on IRV2 had any thoughts.
__________________
Ray & Paula
'99 Newmar Mountain Aire 3758, Ford V10, 3 Pugs, the toad is RTOAD - 06 CRV
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
07-05-2008, 05:47 PM
|
#2
|
|
Member
Join Date: Jan 2004
Location: Woodbury, MN, USA
Posts: 44
|
Hi All,
Our air conditioning is working sporadically when running the generator. Both air conditioners are fine with shore power. Symptoms - both will run on generator, sometimes neither will, sometimes 1 or the other. The thermostat will not show any display for 1 or both. When there isn't any display, there isn't any air conditioning. I have electrical schematics and am trying to trace the 5amp 12v control power for the thermostats. The 2004 39S has the Intellitec system and I think the problem lies within that control system when running on the generator. Bumps will cause the air conditioners to start and or stop. I think I may have a grounding problem. I'm in the process of joining the DOAI site but that takes up to 4 days to get forum credentials, so I decided to see if someone on IRV2 had any thoughts.
__________________
Ray & Paula
'99 Newmar Mountain Aire 3758, Ford V10, 3 Pugs, the toad is RTOAD - 06 CRV
|
|
|
|
| |
|
07-05-2008, 05:49 PM
|
#3
|
|
Member
Join Date: Jan 2004
Location: Woodbury, MN, USA
Posts: 44
|
Hi All,
One other question. I would think there is a way to jumper each air conditioner. I don't believe I'm having a problem with the AC power to each conditioner, the problem seems to be on the control side.
Ray
__________________
Ray & Paula
'99 Newmar Mountain Aire 3758, Ford V10, 3 Pugs, the toad is RTOAD - 06 CRV
|
|
|
|
| |
|
07-06-2008, 04:34 AM
|
#4
|
|
Community Moderator
Fleetwood Owners Club Freightliner Owners Club Florida Cooters Club
Join Date: Jan 2000
Location: Silver Springs, FL. USA
Posts: 9,581
|
The lack of a t-stat display is your clue - you seem to have a 12v problem in generator mode only, which seems strange. Maybe a coincidence and you use the genset only in some circumstance that is also related to the problem?
As you know, the t-stat circuits go through the Intellitec EMS. Two of the relays in the EMS are for 12v circuits and normally the a/c t-stats are wired through them to give the EMS control over them. May have a loose wire or bad relay there.
Also make sure your EMS display shows that the generator is running when it is in fact running. There is a special bypass in the EMS to turn off energy management when the genset runs and the "generator" light on the display should be lit to indicate that mode. If it isn't lit, then the EMS will try to limit you to 30A max and may be intentionally shutting off the a/cs. There is a terminal on the EMS board that must receive +12v when the genset is on to force it into generator mode.
__________________
Gary Brinck
2004 American Tradition; 2007 GMC Acadia
Homebase in the Ocala Nat'l Forest near Ocala, FL
|
|
|
|
| |
|
07-18-2008, 08:45 AM
|
#5
|
|
Senior Member
Fleetwood Owners Club Solo Rvers Club
Join Date: Dec 2007
Location: Las Vegas NV
Posts: 1,055
|
This is going to sound strange but TRY it... Turn on some OTHER 120V item at the same time... anything will do. Several Bounders have a similar problem and it's a ground feed back.. turning on another item usual cures it while your driving with Generator on or parked with it on.
__________________
1999 Fleetwood Bounder 32H Las Vegas Nevada No Dog * No Cat * No Co-Pilot
|
|
|
|
| |
|
07-18-2008, 11:50 AM
|
#6
|
|
Senior Member
Join Date: Dec 2007
Location: Wellington, FL
Posts: 148
|
I had a problem with the RJ11/phone line type jack having a poor connection inside one of my AC units which would cause my AC's to not work. Cleaned all of them, both AC connections and also inside on the control panel and all was well.
__________________
2002 Newmar Dutchstar 3852
Ted, Nancy & Our Westie's Nikki & Willie
|
|
|
|
| |
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|