Quote:
Originally Posted by Bobmn
Hello to all; 2001 Discovery, 7500 Onan diesel Genset, 458 Freedom charger/inverter (2000w) If I run the genset, no charge...if I plug into 110...no charge! The only way the house batteries will charge is when you run the engine.
I have ck'd the fuses under the fridge, and all the breakers there. I installed 4 new 6v golf cart batteries last week. nope! Still the same. Is there some thing in the inverter that could have gone bad? The breaker on the inverter is not out, and the other 2 breakers are good, that are on the front. Maybe a "spike" at a campground? Has anyone had this happen to them? Thanks BobMn
|
When you are un-plugged from shore power, does the inverter work? (e.g. provide 120vac to the designated circuits) It would be very unusual for the inverter to operate, but for the charger portion to NOT work, since most of the internal circuitry is used for both functions. Also the external path from the 458 to/from the batteries is common (and required) for both functions.
If neither the charge or invert functions work, then I suspect there is a blown Class-T (DC) fuse between the batteries and the input to your inverter/charger.
Shore power and the generator use the 458 to charge the batteries while the engine charges them from the alternator through a separate path.
PS - troubleshooting can also be complicated by the fact that on most Heart Interface and Xantrex inverter chargers, the ac passthru function of the internal transfer switch will not function without 12vdc on the DC side. This would be indicated by the circuits normally fed by the inverter NOT working even when plugged into shore/gen power.