Old 07-18-2018, 07:41 AM   #1
HRF
Member
 
Winnebago Owners Club
Join Date: Aug 2016
Location: Smyrna, DE
Posts: 96
Onan 7500 Quiet Diesel Generator no start

The generator in my 2007 Fleetwood would not start after the MH was sitting in storage for 5 days with the battery disconnect switches off. The generator set a fault code 32 and said low battery and slow crank speed. The batteries were almost fully charged and when I tried to start the unit again 3 days later, it started okay. Then 2 days later it would not start and set code 32 again. Coach is not plugged in and the batteries check okay. Any ideas as to what would cause it to not start one day and start okay 3 days later, only to fail again 2 days after that?
HRF is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-18-2018, 09:08 AM   #2
Senior Member
 
Jake21's Avatar
 
Join Date: May 2012
Posts: 3,296
Have you tried cleaning all the battery cable connections? I would start there.
Jake21 is offline   Reply With Quote
Old 07-19-2018, 07:51 AM   #3
HRF
Member
 
Winnebago Owners Club
Join Date: Aug 2016
Location: Smyrna, DE
Posts: 96
Battery cables were cleaned this spring and appear to be okay but I will check.
HRF is offline   Reply With Quote
Old 07-21-2018, 06:37 AM   #4
Junior Member
 
Join Date: Jul 2018
Posts: 1
onan 7500 quiet start

I too am having troubles getting my BRAND new onan to start it has 78 hours on it. For the first 70 hours, no problems. Replace oil and filter at 37hrs.
This is on a food truck .

The truck batteries have a kill switch on them to prevent draining.

The last 3 times I have tried to use generator, I get one crank then Nothing....

the first two times, I put jumper cables to the generator and was able to start right up. this last time, it did not do the trick.


Still not starting. Any advice? Anyone have a problem like this? Of course its a weekend and there isn't a shop open until Monday.

Any experience with this or advice would be appreciated....
blendabowl is offline   Reply With Quote
Old 07-22-2018, 06:39 AM   #5
HRF
Member
 
Winnebago Owners Club
Join Date: Aug 2016
Location: Smyrna, DE
Posts: 96
Don't know if new generators set codes like my 2007 does but on mine the light in the start/stop switch will flash a code. Count the flashes. Mine flashed 3 times paused and flashed 2 times for a code 32. Your owners manual should tell you about codes.
HRF is offline   Reply With Quote
Old 07-22-2018, 07:21 AM   #6
Senior Member
 
TwelveVolt's Avatar
 
Join Date: Oct 2012
Posts: 1,115
Onan 7500 Quiet Diesel Generator no start

The first questions in electronics troubleshooting are “Is it plugged in.” and “Is it turned on?”. For generators it is “Does the tank have enough fuel?”. The generator usually requires more than 1/4 tank, but possibly more if parked on an incline. If it was low at any time, even though it is full now, fuel may have dropped out of the tube to be replaced with air. If you hold the switch in the off position for 60 seconds, the pump will run to push air through and replace it with fuel.

I know the problem here seems to be the battery, but you did not say how long you were cranking before getting the battery low condition.
TwelveVolt is offline   Reply With Quote
Old 07-22-2018, 08:57 AM   #7
Member
 
Truckerdave's Avatar
 
Join Date: Apr 2018
Location: Flushing, Michigan
Posts: 88
Mine is an older model. 1993. Generator starts hard after sitting a few months. Cranks but does not start. When it does start it runs ruff for about 30 seconds then smooths out. Half a tank of diesel fuel. I am guessing mine is losing its prime.
Truckerdave is offline   Reply With Quote
Old 07-22-2018, 09:17 AM   #8
Senior Member
 
Join Date: Feb 2013
Posts: 212
Quote:
Originally Posted by Truckerdave View Post
Mine is an older model. 1993. Generator starts hard after sitting a few months. Cranks but does not start. When it does start it runs ruff for about 30 seconds then smooths out. Half a tank of diesel fuel. I am guessing mine is losing its prime.



If your 7.5 qd is like my 1997, if you push the bottom side of the start switch it operates the electric lift pump and should prime the generator.
aboatguy is offline   Reply With Quote
Old 07-22-2018, 09:20 AM   #9
Senior Member
 
Join Date: Feb 2013
Posts: 212
Quote:
Originally Posted by HRF View Post
The generator in my 2007 Fleetwood would not start after the MH was sitting in storage for 5 days with the battery disconnect switches off. The generator set a fault code 32 and said low battery and slow crank speed. The batteries were almost fully charged and when I tried to start the unit again 3 days later, it started okay. Then 2 days later it would not start and set code 32 again. Coach is not plugged in and the batteries check okay. Any ideas as to what would cause it to not start one day and start okay 3 days later, only to fail again 2 days after that?
Are you checking the voltage after the disconnect switch (maybe the switch is causing a voltage drop) ?



Are all the connections clean and tight?


What's the battery voltage at the generator when it won't start?


Mike
aboatguy is offline   Reply With Quote
Old 07-22-2018, 06:34 PM   #10
HRF
Member
 
Winnebago Owners Club
Join Date: Aug 2016
Location: Smyrna, DE
Posts: 96
The generator is in the front of a Fleetwood motor home and not on a slide out tray. Where do I go to check voltage at the generator? Under the coach?
HRF is offline   Reply With Quote
Old 07-23-2018, 12:19 PM   #11
HRF
Member
 
Winnebago Owners Club
Join Date: Aug 2016
Location: Smyrna, DE
Posts: 96
Quote:
Originally Posted by TwelveVolt View Post
The first questions in electronics troubleshooting are “Is it plugged in.” and “Is it turned on?”. For generators it is “Does the tank have enough fuel?”. The generator usually requires more than 1/4 tank, but possibly more if parked on an incline. If it was low at any time, even though it is full now, fuel may have dropped out of the tube to be replaced with air. If you hold the switch in the off position for 60 seconds, the pump will run to push air through and replace it with fuel.

I know the problem here seems to be the battery, but you did not say how long you were cranking before getting the battery low condition.
Thanks. The bottom half of my start button will prime and my tank level was a little over 1/4 full so maybe you are on to something that I did not think of. I will try when I get to the coach in a couple of days. However the generator was running but 3 days later with no decrease in fuel tank level, it would not start. Also it does not crank, just clicks for preheat for 10 seconds or so then nothing. The light then flashes the code 32 so I don't think it is a fuel issue but you never know. Thanks for the suggestion.
HRF is offline   Reply With Quote
Old 07-23-2018, 12:29 PM   #12
Senior Member
 
Monaco Owners Club
Join Date: Sep 2014
Posts: 4,569
Quote:
Originally Posted by HRF View Post
The generator is in the front of a Fleetwood motor home and not on a slide out tray. Where do I go to check voltage at the generator? Under the coach?
If you have a panel that removes from your genset than just inside that you should be able to follow the red cable to the relay.

You should be able to find the owners and service manuals here.
Index of /~n0nas/manuals/onan
__________________
1996 Tioga Class C
2007 Monaco Diplomat 40 PDQ
TOAD 2012 Cadillac SRX 4
okcnewbie is offline   Reply With Quote
Old 07-23-2018, 03:29 PM   #13
Senior Member
 
Tha_Rooster's Avatar
 
Join Date: Aug 2008
Location: Georgia
Posts: 8,638
Quote:
Originally Posted by HRF View Post
The generator in my 2007 Fleetwood would not start after the MH was sitting in storage for 5 days with the battery disconnect switches off. The generator set a fault code 32 and said low battery and slow crank speed. The batteries were almost fully charged and when I tried to start the unit again 3 days later, it started okay. Then 2 days later it would not start and set code 32 again. Coach is not plugged in and the batteries check okay. Any ideas as to what would cause it to not start one day and start okay 3 days later, only to fail again 2 days after that?


When you say batteries are ok what is the house batteries voltage?
__________________
2007 Fleetwood Revolution LE 40V
Tha_Rooster is offline   Reply With Quote
Old 07-24-2018, 06:39 AM   #14
HRF
Member
 
Winnebago Owners Club
Join Date: Aug 2016
Location: Smyrna, DE
Posts: 96
Quote:
Originally Posted by okcnewbie View Post
If you have a panel that removes from your genset than just inside that you should be able to follow the red cable to the relay.

You should be able to find the owners and service manuals here.
Index of /~n0nas/manuals/onan
Thanks. I do have a panel and have never looked under it. I will check it out.
HRF is offline   Reply With Quote
Reply

Tags
diesel, generator, no start, onan, quiet



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cummins-Onan 7500 quiet diesel generator fault code 25 Bad Bolt Class A Motorhome Discussions 31 01-03-2019 06:05 PM
Onan quiet diesel 7500 generator Skyskier iRV2.com General Discussion 15 12-19-2017 10:39 PM
Onan quiet 7500 Diesel generator DrHexx Class A Motorhome Discussions 9 07-23-2017 04:38 PM
7500 onan quiet diesel wont start rdm Class A Motorhome Discussions 2 11-11-2012 08:47 AM