Onan generator turns but won't start
Old 01-23-2012, 11:01 AM   #1
baloo is offline
Junior Member
Join Date: Dec 2011
Posts: 28
I noticed a few postings about Onans turning over but not catching once the starter button is released.

I have an 03 Sun Voyager, and I have that problem. Is it possible that there is a starter switch inside the coach that must be turned on to start? We're new to the Sun Voy, and there are some switches up front that are puzzling. Also, I'm totally in the dark concerning the converter fuses/switches and other fuse locations.

I added 20gals of gas to the tank, thinking the generator pickup was not being fed, but that didn't help. The gas tank is 75gals, so I can't believe that it wouldn't start with 20gals.

I'm worried that it's in the oil pressure circuit.
Does anyone know how to bypass this oil-pressure shut-off circuit?

Any other ideas?
Thanks.

__________________
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-23-2012, 11:16 AM   #2
Stevegd007 is offline
Senior Member
Stevegd007's Avatar
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Mar 2005
Location: San Diego County, CA
Posts: 362
Most generators need a least 1/4 tank of fuel in the RV fuel tank to run. Even with your fuel gauge showing a tad over 1/4 sometimes the generator will not run. Adding 20 gals of fuel to an empty fuel tank may not be enough. Then you should not have 2nd button to push to run the generator. Just one. Onans will also have a starter switch "ON" the generator, behind the cover. Check to see all fuses are OK on the generator. Next if you have not changed out the fuel filter...an 03 RV...might have a look see at replacement of the fuel filter for the generator.
Best of Luck.

__________________
Steve & Leslie
Winnebago Adventurer 38T
Honda CR-V "Toad" w/Falcon 2 towbar
  Reply With Quote
   
Old 01-29-2012, 01:28 PM   #3
Sundancer268 is online now
Member
Gulf Streamers Club
Join Date: Jan 2009
Location: Charlevoix, Michigan
Posts: 53
Re the switch inside. If it is an Onan there is no switch inside that has to be operated Either switch will work with out the other switch being touched. If the engine is firing when you hold the start button on and quits when you stop pushing the button, you might have a failed voltage regulator or low oil pressure. Have you checked the oil level to verify it is where it belongs? I would also check the Onan WEB site and see if you can find any information on your generator. Good Luck.
__________________
GSMC(SW) U.S. Navy (RETIRED) 1967-10-03 to 1993-11-01
1995 Gulf Stream Scenic Cruiser, Cummins B5.9, Allison MD3060, Toad: 2005 Focus ZXW SES Wagon
  Reply With Quote
   
Old 01-30-2012, 04:42 AM   #4
baloo is offline
Junior Member
Join Date: Dec 2011
Posts: 28
MH still in the garage getting "serviced." (Now starting the 3rd week!) Am sitting here fretting and anxious to try out the recommendations.
__________________
  Reply With Quote
   
Old 02-01-2012, 12:41 PM   #5
GULFer is offline
Junior Member
Join Date: Jun 2010
Posts: 14
Is the motorhome new to you? If it is, I had the same problem until service manager explained how to prime generator from the dashboard switch. I don't remember if there is a primer on the outside panel. You prime it by pushing top portion of switch for 10 or 15 seconds and then push lower portion of rocker switch to start.. Good luck
__________________
  Reply With Quote
   
Old 02-02-2012, 03:46 AM   #6
baloo is offline
Junior Member
Join Date: Dec 2011
Posts: 28
Quote:
Originally Posted by GULFer View Post
You prime it by pushing top portion of switch for 10 or 15 seconds and then push lower portion of rocker switch to start.. Good luck
Yep, there was a little sign by the switch explaining the prime. I'm pretty sure it got to point, after numerous tries, that I was smelling gas.

I'm still stuck at the mercy of the whim of the service station, awaiting the MH's completion so that I can try all the suggestions!
__________________
  Reply With Quote
   
Old 03-30-2012, 10:42 PM   #7
BattChief7 is offline
Junior Member
BattChief7's Avatar
Join Date: Jan 2012
Location: College Station, Texas
Posts: 16
I went through a similar problem. Mechanic could not get any spark but coil showed good. He thought "trigger" on crankshaft had broken and took generator apart to replace. Turned out that the "pin" connectors on wiring harness were loose and corroded. replaced "pins" in connectors and genset ran fine. Just a thought.
__________________
  Reply With Quote
   
Old 03-31-2012, 07:06 AM   #8
George Schweikle is offline
Senior Member
George Schweikle's Avatar
Join Date: Apr 2004
Posts: 303
This may not suit everyone, but I went through two seasons of intermittent problems with my generator before taking a friend's advice and going to the nearest Cummins Onan service center. While there are probably many independent locations that can provide excellent generator service, and this forum also has excellent tips and advice, the Cummins Onan people had the test equipment and experience to correct my problem. They had one tech that did nothing but work on generators.

The generator is a Microlite 4000 that sometimes ran fine, but other times it wouldn't run under a load. I replaced the fuel line from the gas tank, changed the fuel filter, spark plug, and air filter, and verified the fuel pump was working. The Cummins Onan tech checked everything, and talked me through the process (did you know there is a reed valve inside the valve cover that must be cleaned?). It turned out that several things were slightly out of adjustment and combined to cause the problem. In this case, my money was well spent by "going to the source" where there was an expert.
__________________
George Schweikle
Lexington, KY
1999 Safari TREK 2830
  Reply With Quote
   
Old 03-31-2012, 09:59 AM   #9
baloo is offline
Junior Member
Join Date: Dec 2011
Posts: 28
George/BattChief,
As reluctant as I am to bringing the coach in (time, lack of faith in mechanics, difficulty in getting everything together to drive the monster out to a shop) -- I'm thinking that maybe the best thing to do is to just pay someone to figure out the problem.
I've gotten some good advice, including sending the control board to be checked, BUT I'm finding that there are a myriad of minute defects that could trip up the elephant, so to speak -- like those pins in a connector which Batt found. Incredible that it even was localized down to that!
__________________
  Reply With Quote
   
Old 03-31-2012, 10:12 AM   #10
DpDave is offline
Senior Member
DpDave's Avatar
Florida Cooters Club
Solo Rvers Club
Coastal Campers
KZ RV Club
Join Date: Jan 2012
Location: Travelling the East Coast
Posts: 113
Baloo, I have an Onan 5500 Elite in my 5er. When I bought the unit, I had know idea how long it had set up with out having run the genny. I went down to speak with the Onan/Cummins guys and got 2 suggestions.

Firstly, and easiest, was to take apart the carburetor and clean it. This was actually a simple job, involving a few hand tools and a can of carb cleaner. Fortunately my genny is very open for that job. The tech pointed out that if the carb was too crudded up for the carb cleaner to work, I could bring it in and hot tank it for a day. Anything more serious, they just replace the carb.

The second option he had mentioned, was that they had been seeing a problem with mice climbing up into the rotor space. When you hit the start button, the rotor spins, whacks the mouse, makes a mess, and breaks an arm off. With an arm off the rotor, no start.

Fortunately, the carb cleaner fixed me up. I now run mine on a load on a regular basis.
__________________
05 Ford F-350
05 KZ 42' Escalade Toy Hauler
00 Harley Road King
  Reply With Quote
   
Old 03-31-2012, 03:12 PM   #11
baloo is offline
Junior Member
Join Date: Dec 2011
Posts: 28
Well, I finally got the MH back and finally got to trying some troubleshooting things out.
Once again, this is an Onan 7KW gas Gold Marquis, carbuerated (HGJAB).

I removed the air filter, and it was soaked with gas.
I then tried turning over the generator, and gas was squirting out of the carb.
I let the generator sit about 10 minutes, moved the "altitude" dial way over, and then tried starting it without priming it. It started and ran for about 1 minute! This is the very first time it has started and run.
Heavy black smoke came out, I'm assuming due to a very rich mix.
Then, the genset cut off and would not start all over again.

If I drained the carb bowl, it would start for 2 seconds and then immediately stop. Subsequent attempts to start would fail. It's only when allowed to sit, would it seem to try to catch for a second or two.

I pulled off the fuel solenoid switch which is on the bottom of the carb, and I tested it with an ohmmeter. I got a high reading across the leads regardless if the plunger was pushed down or not. I take it that the solenoid is not doing its job of turning off the fuel pump when the float reaches a certain level??

1) Would this be correct thinking??

I'm thinking that the fuel pump keeps pumping because the cutoff solenoid is not kicking in, so it is flooding.

2) I cannot get to the carb mounting bolts because they are on the backside of the genset. The gen cover is preventing me from even getting a contorted angle at the bolts.

Anyone have ideas how to remove the carb without taking the generator totally out of the MH??
__________________
  Reply With Quote
   
Old 04-01-2012, 02:46 AM   #12
RV Wizard is offline
Community Moderator
RV Wizard's Avatar


Gulf Streamers Club
Country Coach Owners Club
Appalachian Campers
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 8,250
It is flooding because the float in the carburetor is sticking not shutting off the fuel and sticking again not allowing the proper amount into the bowl. You may try removing the bowl and cleaning the float and valve assembly with the carburetor still on the engine.
__________________

Mike, Certified Master RV Technician
Amy, RV Merchandiser; Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser w/ Banks & 2 toads
  Reply With Quote
   
Old 04-04-2012, 11:56 AM   #13
Jim2668 is offline
Junior Member
Join Date: Aug 2010
Posts: 3
Same problem, mouse had chewed the supply line.
__________________
  Reply With Quote
   
Old 04-04-2012, 12:14 PM   #14
ga traveler is offline
Senior Member


Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 1,387
Quote:
Originally Posted by baloo View Post
Well, I finally got the MH back and finally got to trying some troubleshooting things out.
Once again, this is an Onan 7KW gas Gold Marquis, carbuerated (HGJAB).

I removed the air filter, and it was soaked with gas.
I then tried turning over the generator, and gas was squirting out of the carb.
I let the generator sit about 10 minutes, moved the "altitude" dial way over, and then tried starting it without priming it. It started and ran for about 1 minute! This is the very first time it has started and run.
Heavy black smoke came out, I'm assuming due to a very rich mix.
Then, the genset cut off and would not start all over again.

If I drained the carb bowl, it would start for 2 seconds and then immediately stop. Subsequent attempts to start would fail. It's only when allowed to sit, would it seem to try to catch for a second or two.

I pulled off the fuel solenoid switch which is on the bottom of the carb, and I tested it with an ohmmeter. I got a high reading across the leads regardless if the plunger was pushed down or not. I take it that the solenoid is not doing its job of turning off the fuel pump when the float reaches a certain level??

1) Would this be correct thinking??

I'm thinking that the fuel pump keeps pumping because the cutoff solenoid is not kicking in, so it is flooding.

2) I cannot get to the carb mounting bolts because they are on the backside of the genset. The gen cover is preventing me from even getting a contorted angle at the bolts.

Anyone have ideas how to remove the carb without taking the generator totally out of the MH??
#1 the solenoid does not cut off the fuel pump. The fuel pump runs all the time. The fuel is shut off by a needle valve, when the fuel is at the correct level. The purpose of the solenoid is to shut off fuel flow into the carb. when you shut down the generator. It sounds like the needle valve is stuck, allowing the carb to flood.

__________________
15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
  Reply With Quote
   
Reply

Tags
generator, onan


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan 5500 generater won't start fanctil Class A Motorhome Discussions 10 09-02-2011 01:42 PM
Onan Kubota Start Problem noladiver Monaco Owner's Forum 12 10-31-2009 07:40 AM
Onan LP Generator hard to start Darryl RV Systems & Appliances 2 10-27-2009 09:26 PM
Onan won't start racer0624 MH-General Discussions & Problems 12 10-28-2006 10:13 AM
Gas Onan 5500 shuts down after start antec7 Winnebago Industries Owner's Forum 10 07-04-2006 03:28 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 09:45 PM.