Old 01-13-2017, 07:47 AM   #1
Junior Member
 
Spartan Chassis
Join Date: Jan 2017
Posts: 25
Smoked my 02 Gulf Stream Country Club

Hoping there is someone out there with the same rig to help in identifying the 110 volt circuits on my new to me rig.

Yesterday was the first time on shore power, and when I reset a couple of tripped breakers, looking to get microwave working, huge amount of smoke came out from under the bed.

Of course I killed all the breakers and pulled the cable, opened the windows and vents to get the smoke and smell out of her.
First look at ATS and breaker panel show no visible damage, but I know there is something burnt. Only pulled cover on ATS, not panel yet.

It was working ok, on generator but unsure if the tripped breakers were off at the time.

So as my 110 panel has lots of breakers and a limited circuit map, I am hoping there is someone who knows what each of the breakers are suppose to control. If I have to try and track/trace every wire in the rig, that would be a very long time.
__________________

TollerDP is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-13-2017, 08:13 AM   #2
Senior Member


 
Winnebago Owners Club
Freightliner Owners Club
Retired Fire Service RVer's
Join Date: Mar 2014
Location: SO CAL
Posts: 131
First things first. Do you have a 30 amp or a 50 amp MH?

Did you use a volt meter to check the outlet you are plugging into?

If you plugged your unit into 240 volt socket, there is the problem that produced the smoke. Now the problem becomes how much damage was done and how to repair it.
__________________

__________________
2007 Itasca Meridian 39K
350 HP Cat / Allison 6 Speed
1 Wife and 2 Dogs
960 watts of solar, 440 Amp hours AGM batteries
KCFDCapt is online now   Reply With Quote
Old 01-13-2017, 08:54 AM   #3
Junior Member
 
Spartan Chassis
Join Date: Jan 2017
Posts: 25
Sorry, it has the 50 amp shore power cord.
The outlet is my "old" 30 amp 220 plug, that I used with an adaptor to plug in the 50 amp.

Just to give an update. I went out pulled the panel cover, no signs of over heating in there or in the ATS. Started the main engine, to make sure I did not somehow fry the electronics, it started fine. Started the generator ( both are diesel ) with all breakers off. I could see a green light on the control board of the ATS, and pretty sure I heard a click about 20 seconds after startup. I shut everything down. Checked the bay where the convertor is, no sign of heat or smoke, the plug in "monitor" was showing a green light.

So as of right now, no "Smokin Gun ", but something made all that smoke.

Just checking is the 50 amp service not a 220 line split into two 110 circuits ?
TollerDP is offline   Reply With Quote
Old 01-13-2017, 09:23 AM   #4
Moderator Emeritus
 
smlranger's Avatar


 
Country Coach Owners Club
Freightliner Owners Club
Join Date: Sep 2004
Location: Glen Allen, VA
Posts: 7,669
Blog Entries: 1
[QUOTE=TollerDP;3414779]Sorry, it has the 50 amp shore power cord.
The outlet is my "old" 30 amp 220 plug, that I used with an adaptor to plug in the 50 amp.

[QUOTE]

The second sentence above is your likely issue. A 30 amp RV outlet is not the same as a 30 amp 220V outlet for a clothes dryer or maybe a welder. A properly wired 30 amp RV outlet is 30 amp 110V...a hot, a neutral and a ground. Your 30 amp 220V outlet is a hot, hot and a ground. Using your 50 amp plug to a 30 amp adaptor basically put 110 volts on both the hot and the neutral wire going to the coach.

A 50 amp RV set up is two hot 110v lines, a neutral and a ground.
__________________
'07 Country Coach Allure 470 Siskiyou Summit #31578, Cummins ISL 425; 2014 Ford F150 toad; Air Force One Toad Brake.
Glen Allen, VA
smlranger is online now   Reply With Quote
Old 01-13-2017, 10:22 AM   #5
Junior Member
 
Spartan Chassis
Join Date: Jan 2017
Posts: 25
Well, I feel completely like a fool. I pulled the panel off the shop panel to verify the wiring of the service plug. To my great surprise, my 30 amp 110 plug was wired to a 220 volt 20 amp breaker. Looks like I am off to Lowes to buy the proper setup for the new girl. Still no sign of what was actually doing the smoking, once I get the proper box and breaker installed I will go back to see what works and what does not.
THanks for making me stop, and look at the source power.
TollerDP is offline   Reply With Quote
Old 01-13-2017, 11:00 AM   #6
Senior Member
 
bdpreece's Avatar
 
Monaco Owners Club
Join Date: Mar 2000
Location: Woodburn Oregon USA
Posts: 2,719
If you plugged it into 220 the odds are you did a substantial amount of damage. any AC appliance that was plugged in has a good chance of being fried. Don't know where yours is located but possibly the smoke was from your inverter. This is probably not going to be cheap! Good luck.
__________________
Brian, Loretta & Daisy (Golden Retriever)
2008 Holiday Rambler Endeavor 40 PDQ , ISL 400
2014 Ford Explorer toad
bdpreece is offline   Reply With Quote
Old 01-13-2017, 03:07 PM   #7
Junior Member
 
Spartan Chassis
Join Date: Jan 2017
Posts: 25
Nobody had the correct plug or breaker to put in my shop for the 50 amp service, but I did get the right 30 amp breaker to fit my panel.
With the proper wiring this time, I put the power onto the cord then went in and tried the breakers. None of the breakers tripped into a reset, a quick once around showed correct power, with my little plug in tester, at all the plugs I could reach.
The fridge responded to the power button, the micro wave did not.
Turned off shore power started the generator. All breakers held, and the green light came on at the ATS, which did not show while on shore power. PLugs all tested good again, fridge responded, micro did not.

So it looks like my little adventure put the micro wave out of comission and perhaps the auto switch. TO check that though I guess I have to be on shore power then start the genny and see if it switches.

The invertor seems to be working as while on generator I checked the coach batteries and they showed higher than with the generator off.

I still can not find anything burnt.
TollerDP is offline   Reply With Quote
Old 01-13-2017, 03:24 PM   #8
Senior Member
 
kustom's Avatar
 
Ford Super Duty Owner
Join Date: Aug 2012
Location: costa rica / river ranch fl.
Posts: 909
microwaves have a fuse inside you might get lucky we had a microwave failed 1 year
and a 1 day
but they checked it and it was the fuse
__________________
99 coachman catalina mbs-334
5.9 275hp dp
kustom is offline   Reply With Quote
Old 01-13-2017, 04:54 PM   #9
Moderator Emeritus
 
smlranger's Avatar


 
Country Coach Owners Club
Freightliner Owners Club
Join Date: Sep 2004
Location: Glen Allen, VA
Posts: 7,669
Blog Entries: 1
I would take the cover off the auto transfer switch and inspect the contacts and wires carefully. If all you fried was the ATS and maybe a fuse in the microwave, you got lucky.

Lowes sells a Swan 50 amp weather proof box with breakers and receptacle. You also need a 50 amp double pole breaker for the circuit panel feeding the box and the appropriate size wire.
__________________
'07 Country Coach Allure 470 Siskiyou Summit #31578, Cummins ISL 425; 2014 Ford F150 toad; Air Force One Toad Brake.
Glen Allen, VA
smlranger is online now   Reply With Quote
Old 01-14-2017, 03:42 AM   #10
Community Moderator
 
RV Wizard's Avatar


 
Country Coach Owners Club
Appalachian Campers
Gulf Streamers Club
Join Date: Mar 2000
Location: Chattanooga, Tn.
Posts: 12,062
The 50 amp receptacle you need is the same as a 50 amp four wire range receptacle. You will need to install a neutral conductor to the receptacle from the distribution panel that will go to the flat blade terminal opposite side of the round equipment ground terminal.
Once you get power restored into the coach you should be able to better trouble shoot all the items killed. I have not seen any electrical conductors damaged from this mistake only all the components and appliances.
Good luck and keep us posted.
__________________
Mike, RVIA & RVSA Certified Master RV Technician
Amy, Dr. Assistant - Roxie & Mei Ling, four legs each
2000 Gulf Stream Scenic Cruiser 450 hp & 1330# torque
06 Saturn Vue, 06 Chevy Z71 4x4 & 2014 Corvette Z51 M7
RV Wizard is offline   Reply With Quote
Old 01-14-2017, 04:47 AM   #11
Senior Member
 
Sweetbriar's Avatar


 
Thor Owners Club
Ford Super Duty Owner
Join Date: Jul 2011
Posts: 2,324
I suspect the transfer switch is OK. Most, not all, will only become active when power is available from the generator. In other words the default de-energized state is closed contacts supplying shore power to the coach while power for the controller and the relay coils is taken from a hot leg coming from the generator.

Check the AC to DC converter/charger a bit deeper. Some generators have a DC charging output voltage to keep the starting battery charged which I think you might have been measuring. If the converter is working properly, with the generator off and on shore power, you should have in excess of 13VDC at the batteries which will indicate the converter is attempting to charge the batteries. Anything less and you will have problems maintaining a full battery charge. If the converter is under the bed near the AC breaker panel high probability the smoke you had came from it.

Other items that were not mentioned is the coach entertainment equipment. TV's, DVD players, satellite receiver and such. If any of these items were plugged in they may now be dead. With the situation you encountered, 120VAC on the AC neutral line, anything that was plugged in, microwave, converter, tv's and other electric/electronic devices, even if the device was turned off, might have sustained damaged. Many times beyond economic repair.

Next RV shopping trip pick up a surge suppressor that also checks for correct voltage, neutral and ground connections. If it doesn't like what it senses it will not apply power to the coach. They come in two general types, power cord end or hard wired.

What is also a concern is replacing the shop panel breaker and outlet but no mention of the wire between the two. Going from a 20 amp service to 50 you will need to also change the wire from the normal 12 gage for 20 amps to 8 or maybe 6 gage depending on the distance. If the day comes that you load up the circuit with a high amp demand there is some risk of overheating the wiring and the hazards associated with such.
Sweetbriar is offline   Reply With Quote
Old 01-14-2017, 05:07 AM   #12
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 4,903
Both Lowes and Home Depot offer a 50 amp box with RV receptacle, some stores stock them or you can order and pick them up.

Sounds like you got lucky if you old fried your microwave. Good Luck
__________________
Jim J
2002 Monaco Windsor 38 PKD
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is online now   Reply With Quote
Old 01-14-2017, 05:56 AM   #13
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Quote:
Originally Posted by TollerDP View Post

Sorry, it has the 50 amp shore power cord.

The outlet is my "old" 30 amp 220 plug, that I used with an adapter to plug in the 50 amp.

Just checking is the 50 amp service not a 220 line split into two 110 circuits ?
Quote:
Originally Posted by TollerDP View Post

Well, I feel completely like a fool. I pulled the panel off the shop panel to verify the wiring of the service plug. To my great surprise, my 30 amp 110 plug was wired to a 220 volt 20 amp breaker.
The two posts above that you made are confusing, conflicting and make NO sense to me.



Can your or someone on this thread explain exactly what has happened?

The top posts states that the outlet you had plugged into was a 220 VAC supply (which you wanted) and by using an adapter you were able to plug in your 50 amp shore cord.

The second posts states that after removing the panel, "To my great surprise, my 30 amp 110 plug was wired to a 220 volt 20 amp breaker.

Also, I don't think your microwave is located under your bed where ALL of the smoke was coming from so I'd be looking for some other damage besides the microwave not working.

Dr4Film ----- Richard

Dr4Film is offline   Reply With Quote
Old 01-14-2017, 06:41 AM   #14
Senior Member
 
Sweetbriar's Avatar


 
Thor Owners Club
Ford Super Duty Owner
Join Date: Jul 2011
Posts: 2,324
Quote:
Originally Posted by Dr4Film View Post
The two posts above that you made are confusing, conflicting and make NO sense to me.



Can your or someone on this thread explain exactly what has happened?

The top posts states that the outlet you had plugged into was a 220 VAC supply (which you wanted) and by using an adapter you were able to plug in your 50 amp shore cord.

The second posts states that after removing the panel, "To my great surprise, my 30 amp 110 plug was wired to a 220 volt 20 amp breaker.

Also, I don't think your microwave is located under your bed where ALL of the smoke was coming from so I'd be looking for some other damage besides the microwave not working.

Dr4Film ----- Richard

The OP's description was a bit confusing on first read but basically what occurred was the original setup might have looked like a standard camp site 30 amp outlet but unfortunately rather than a hot-neutral-ground configuration it had a hot-hot-ground which basically changed all the outlets from 120VAC to 220VAC. What isn't mentioned was the breaker is probably a double pole common trip which is the more common distribution setup 220VAC from standard USA residential utility service such as this example -



With an industrial application it is certainly possible to have a 220VAC single phase configuration but that will require really big transformer that will provide 220 single phase power such as this portable one -



Had a bunch of them when I was living in Australia which has 220VAC single phase residential power that I need to step down to 120VAC for all my USA made stuff. Regardless of the breaker size, 20 or 30 amp, the outcome would not have changed if the circuit was wired as I suspect, hot-hot-neutral. I am making a couple of presumptions based on filling in the blanks but it sure reads like an over volt situation.
__________________

Sweetbriar is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
2002 Gulf Stream Country Club Yellowstone TollerDP iRV2 Owners Registry 0 01-06-2017 03:09 PM
1990 Gulf Stream Sun Stream 2000 rebirth theartist Vintage RV's 5 07-30-2015 04:16 PM
2008 Gulf Stream Gulf Breeze smonagle New Rig Show-Off! 6 08-07-2013 12:15 AM
2006 Gulf Stream Gulf Breeze TT -- New To Me!! YodaRules Gulf Stream Owner's Forum 5 03-06-2013 05:43 AM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:28 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.