Generator Problem

When I go on the road and start my generator to run everything during the trip it stops after the motor warms up. Usually about (15 min.) I can hit the start button and it restarts. let off the button and it dies. I changed the start button and it still stops. Any help would be appreciated.




1997 CC magna aspire Detroit 330 HP Turbo 6spd Allison Transmission
PowerTech 7000kw with Kubota motor
__________________

__________________
Jerry226 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-20-2016, 04:19 PM   #2
Senior Member
 
Country Coach Owners Club
Join Date: Jan 2006
Location: Redding
Posts: 3,412
Quote:
Originally Posted by Jerry226 View Post
When I go on the road and start my generator to run everything during the trip it stops after the motor warms up. Usually about (15 min.) I can hit the start button and it restarts. let off the button and it dies. I changed the start button and it still stops. Any help would be appreciated.
The Manual for my PowerTech generator provides trouble shooting steps in a rear section of the manual. (I got an electronic version from PowerTech web site.)

It would be helpful if you identified your rig model and vintage, and the manufacturer of the generator that you have.

You might have a broken fan belt, oil level too low, fuel starvation, coolant too low, heat too high all of which might trip a sensor.

The manual trouble shooting steps go into detail about how to test based on results of previous test. Too much to reprint here.
__________________

__________________
Dean
1995 CC Magna #5280
C8.3L 300hp Cummins, 31,000lbs
deandec is offline   Reply With Quote
Old 05-20-2016, 04:36 PM   #3
Member
 
Jerry226's Avatar
 
Join Date: May 2016
Location: Kokomo Indiana
Posts: 49
Thanks Dean I tried all the above. I can start the generator when the big motor is not running and it will run until I shut it off.
__________________
Jerry226 is offline   Reply With Quote
Old 05-20-2016, 05:26 PM   #4
Senior Member
 
Join Date: Jul 2014
Posts: 9,906
Do you have a generator auto start.

The generator may shut down due to the engine charging system bringing the batt voltage up to the set point.

Just a guess.
__________________
twinboat is online now   Reply With Quote
Old 05-20-2016, 07:20 PM   #5
Member
 
ltcolmac17's Avatar
 
Country Coach Owners Club
Join Date: Jul 2014
Location: Upstate SC
Posts: 81
Since it's not an immediate shutdown when you start the drive engine, it's likely not electrical interference or interruption from the alternator, AGS, or inverter. I'd look more to the fuel pump, cooling problem, or air starvation, or vapor lock due to too much vacuum in the main fuel tank.

If you google this issue there are numerous examples on this and other forums experienced across all types of diesel and gas rigs, and genny makes.

I've got the same genny as you and it has only shutdown while driving in 100+ degree F ambient temperature. I can usually restart it after 20 minutes of cooling after checking coolant level.


Sent from my iPhone using iRV2 - RV Forum
__________________
ltcolmac17
1998 Country Coach Allure 36' (CC# 30146), Cummins ISC 325
2012 Jeep Grand Cherokee Overland, Roadmaster Brakemaster & Blackhawk
Retired USAFR
ltcolmac17 is offline   Reply With Quote
Old 05-21-2016, 11:02 AM   #6
Senior Member
 
Jerry's Avatar
 
Country Coach Owners Club
Join Date: Feb 2000
Location: Fort Worth, TX
Posts: 118
I had a similar problem with my Onan diesel. It was the temperature sending unit. Onan has had a high failure rate on them.
__________________
2005 Country Coach Inspire Quad Slide w/C9-400 Kitty Kat, '08 Jeep Commander. "RVing since 1968"
Escapee #27953, FMCA #12697, Good Sam Life Mbr.
Jerry is offline   Reply With Quote
Old 05-21-2016, 04:46 PM   #7
Member
 
Jerry226's Avatar
 
Join Date: May 2016
Location: Kokomo Indiana
Posts: 49
My Generator has a Kubota diesel motor. It will start and run forever if there is fuel. when I start my coach and then the generator it will run until the motor on the generator get warmed up. it will stop running. I can push the switch up to start and it will restart. I then have to put the switch back in the middle to stop the starter motor. then it dies. it will re start every time but dies when put back in the middle. This has a new switch. up is start. middle is run. down is pre heat and stop.
__________________
Jerry226 is offline   Reply With Quote
Old 05-22-2016, 12:10 PM   #8
Senior Member
 
Country Coach Owners Club
Join Date: Jan 2006
Location: Redding
Posts: 3,412
Quote:
Originally Posted by Jerry226 View Post
My Generator has a Kubota diesel motor. It will start and run forever if there is fuel. when I start my coach and then the generator it will run until the motor on the generator get warmed up. it will stop running. I can push the switch up to start and it will restart. I then have to put the switch back in the middle to stop the starter motor. then it dies. it will re start every time but dies when put back in the middle. This has a new switch. up is start. middle is run. down is pre heat and stop.

I also have the PT7000 generator but a different remote switch.

You can disconnect the remote switch, as the manual directs in the trouble shooting section, to remove any chance it is the problem. Just use the start switch on the generator.

If you have followed all the steps in the trouble shooting guide for "starts but won't run" and have assured yourself that the fan belt is good, then it would seem the next step is to take it to a generator specialist.

The only interaction I can imagine between the engine alternator and the generator is the recharging of the house battery when both power sources are running.

The chassis battery on my rig is not recharged by the generator and I have a dedicated generator start battery.

If you have gen auto/start installed that is set for recharging the house battery, I can imagine in a few minutes of charging by a 160A alternator and the generator combined could result in a battery full message and generator shutdown.
__________________
Dean
1995 CC Magna #5280
C8.3L 300hp Cummins, 31,000lbs
deandec is offline   Reply With Quote
Old 05-22-2016, 12:20 PM   #9
Senior Member
 
Freightliner Owners Club
Join Date: Apr 2004
Location: Apache Junction, Az
Posts: 703
First Check the fluid inside the radiator and not the overflow container. Look for a small cover on top. You may be surprise to find a radiator cap.
If you do have a separate radiator cap (Not The Overflow Container). Then take the cap to any auto parts store and get a new one. Please let us know if I was correct.
__________________
Dale&Susan, 08 Alfa Gold, DaGirlsRv Blog
2015 F-150XLT_1600W Solar_880 AmpHr
Magnum_MS2812
gatorcq is offline   Reply With Quote
Old 06-28-2016, 06:32 PM   #10
Member
 
Jerry226's Avatar
 
Join Date: May 2016
Location: Kokomo Indiana
Posts: 49
I bought a new radiator cap and it didn't help. changed oil filter, fuel filter, air filter. No change. I also bought a new transfer switch, no help.
__________________
Jerry226 is offline   Reply With Quote
Old 06-28-2016, 06:41 PM   #11
Senior Member
 
Country Coach Owners Club
Join Date: Jan 2006
Location: Redding
Posts: 3,412
Did you disconnect the remote switch?
__________________
Dean
1995 CC Magna #5280
C8.3L 300hp Cummins, 31,000lbs
deandec is offline   Reply With Quote
Old 06-28-2016, 07:07 PM   #12
Senior Member
 
Join Date: Sep 2012
Posts: 5,980
FWIW The only way it would be an electrical problem would be if something was shutting off the 12 VDC back to the generator controls. It really sounds like one of the protection sensors. The fact that it runs while you hold down the start position thus bypassing some of the sensors is part of what I am basing that on.
__________________
nothermark is offline   Reply With Quote
Old 06-29-2016, 03:32 PM   #13
Member
 
Jerry226's Avatar
 
Join Date: May 2016
Location: Kokomo Indiana
Posts: 49
Where are the sensors located???
__________________
Jerry226 is offline   Reply With Quote
Old 06-30-2016, 04:50 AM   #14
Senior Member
 
Join Date: Sep 2012
Posts: 5,980
FInd the manual for the generator to learn where things are. What you have for sensors and where they are depends on the generator you have. You at least have an oil pressure sensor and probably several more.
__________________

__________________
nothermark is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Automatic generator start system/Generator/shoreline automatic changeover switc Rac912 RV Systems & Appliances 14 01-12-2016 12:51 PM
Military Generator INSIDE prepped Generator Area WorkRVing 5th Wheel Discussion 21 11-18-2015 07:00 AM
Generator & Aux Power Problem BugSlayer Winnebago Industries Owner's Forum 27 03-01-2009 08:07 AM
Generator Problem Mr. Proto MH-General Discussions & Problems 1 01-27-2009 01:10 PM
Onan Generator Problem jadams RV Systems & Appliances 2 03-30-2007 03:52 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:21 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.