No AC Power In Coach - Trouble Shooting Assistance Requested

Greetings all, Murphy bit us hard yesterday, we were just finishing up some food items to take to a friends home for Thanksgiving Dinner when all AC power in the coach died. I looked at the electrical control panel, the indicator showed 50 AMP power available, no circuit breakers were tripped and all were cool to the touch, but the inverter had shut off due to overload. I first thought we had lost power in the park, and that the indicator was lying but a check showed that we had power at the pedestal. I then did the following trouble shooting steps.

1, recycled the pedestal 50 amp breaker - no joy. Indicator showed AC power available after the 2+ minute delay for the surge protector and ATS to cycle.
2, disconnected shore power, turned on genset. Again the AC indicator showed 50 amp available but no AC power was available, i also noticed that the battery bank (4 large AGMs) was not charging.
3, next started engine, battery bank was charging at the normal level, 13.6/7 volts
4, did some research and suspicion focused on the surge protector and/or the transfer box. Opened bay door to gain access to both, on my 2005 Allure they are located side by side, cycled the shore power breakers and observed their operation. Every thing seemed normal, surge protector cycled as it should, transfer switch made no unusual sounds, both passed the nose test, no burnt electrical smell observed.
5, I pulled the cover off the circuit breaker panel inside the coach and checked the operation of the main 50 amp breaker,
it has power and supplied power to the sub breakers and when cycled off power was not observed at the sub breakers.

At this point I am out of ideas. Question:

1, does all of the AC power go through Inverter (Magnum 2812 installed by previous owner). After some research my DW suspects the inverter is the problem, my next step will be to go out to check its circuit breakers.
2,Given that I have power at the main 50 amp breaker does that eliminate the Surge Protector and ATS as the source of the problem?
3, as a stop gap does anyone see an issue with securing a large battery charger and keeping the house bank charged so we can run the hydro-hot heating system? We ran it all last night on our house batteries, they are now down to 12.2 volts, we are in N. VA and it will be below freezing tonight.


Howard
__________________

__________________
Guardsman
2005 Country Coach Allure 470
2001 BMW 330 CI
Guardsman is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-29-2019, 09:16 AM   #2
Senior Member


 
Join Date: Jul 2017
Location: Blue Springs, MO
Posts: 383
If you have 120 volts at your main 50 amp breakers and you have 120 volts at your sub breakers then you will have power at your outlets. Your outlets are directly wired to your breakers.

Are both green LED's on your surge protector on and you hear the transfer switch when it switches to pedestal power? (I've had to jiggle my plug at the pedestal to get both phases connected properly with a worn out receptical) The pedestal power goes directly to your breaker panel after going through the transfer switch so a failed inverter/converter won't stop your AC power from reaching your breaker panel.
__________________

__________________
2009 Country Coach Veranda 400
BonS is offline   Reply With Quote
Old 11-29-2019, 09:17 AM   #3
Senior Member
 
Join Date: Nov 2012
Posts: 734
How about the GFI'S?
__________________
Wally & Elta Mae
2007 Allure 470 Sunset Bay #31535
wfalch is offline   Reply With Quote
Old 11-29-2019, 09:21 AM   #4
Senior Member
 
Ljwt330's Avatar
 
Join Date: Jan 2018
Location: Capistrano Beach, California
Posts: 1,222
Quote:
Originally Posted by Guardsman View Post
Greetings all, Murphy bit us hard yesterday, we were just finishing up some food items to take to a friends home for Thanksgiving Dinner when all AC power in the coach died. I looked at the electrical control panel, the indicator showed 50 AMP power available, no circuit breakers were tripped and all were cool to the touch, but the inverter had shut off due to overload. I first thought we had lost power in the park, and that the indicator was lying but a check showed that we had power at the pedestal. I then did the following trouble shooting steps.

1, recycled the pedestal 50 amp breaker - no joy. Indicator showed AC power available after the 2+ minute delay for the surge protector and ATS to cycle.
2, disconnected shore power, turned on genset. Again the AC indicator showed 50 amp available but no AC power was available, i also noticed that the battery bank (4 large AGMs) was not charging.
3, next started engine, battery bank was charging at the normal level, 13.6/7 volts
4, did some research and suspicion focused on the surge protector and/or the transfer box. Opened bay door to gain access to both, on my 2005 Allure they are located side by side, cycled the shore power breakers and observed their operation. Every thing seemed normal, surge protector cycled as it should, transfer switch made no unusual sounds, both passed the nose test, no burnt electrical smell observed.
5, I pulled the cover off the circuit breaker panel inside the coach and checked the operation of the main 50 amp breaker,
it has power and supplied power to the sub breakers and when cycled off power was not observed at the sub breakers.

At this point I am out of ideas. Question:

1, does all of the AC power go through Inverter (Magnum 2812 installed by previous owner). After some research my DW suspects the inverter is the problem, my next step will be to go out to check its circuit breakers.
2,Given that I have power at the main 50 amp breaker does that eliminate the Surge Protector and ATS as the source of the problem?
3, as a stop gap does anyone see an issue with securing a large battery charger and keeping the house bank charged so we can run the hydro-hot heating system? We ran it all last night on our house batteries, they are now down to 12.2 volts, we are in N. VA and it will be below freezing tonight.


Howard

To answer your questions:


1. Yes. Check the inverter. From your description and the tests you've run, the inverter is the one common factor left that would account for your issue. Typically, AC from the post and generator go to the main panel (where you detect it), then to the inverter/converter and on to the sub panel. If you have no power at the sub panel main breaker, the interruption is at the inverter. There is likely a breaker in the sub panel labeled, "inverter." Be sure it has been cycled to ensure it is ON.


2. Yes.



3. Possibly. It's generally ok to use a separate charger to maintain the battery bank. Just be sure it provides enough charging amps to charge the bank and run the device drawing the amps. You are basically replacing your converter, which is part of the inverter combination, because the in-house one is not functioning. In addition, be sure the charger has a float or monitoring function so the batteries do not overcharge.


Before attempting the above, check out the inverter and look for tripped breakers on it.


You also have high amp 12v fuses/breakers from the battery bank. If one of those has tripped, the batteries will not charge from the inverter/converter but could still charge from the alternator. However, since you have no AC from shore or generator, the inverter is still the main suspect, IMO.
__________________
Larry, Eileen, and Finley
2004 Alpine 36FDDS
Third motor home, first Alpine, no need for another.
Ljwt330 is online now   Reply With Quote
Old 11-29-2019, 09:34 AM   #5
Community Moderator
 
CountryFit's Avatar


 
Join Date: Sep 2011
Location: Between the Oceans
Posts: 5,970
Blog Entries: 4
Quote:
Originally Posted by wfalch View Post
How about the GFI'S?
x 2. Our GFCI will trip when the induction cooktop is turned off from 425 deg or higher cooking. We now work around by going from 425+ to 275 first, then shut it down.

Funny though, microwave has an equal max wattage but never trip it.
__________________
Steven & Polly
2000 Country Coach Intrigue 40'
2014 Ford C-Max Energi
CountryFit is online now   Reply With Quote
Old 11-29-2019, 09:49 AM   #6
Senior Member
 
Country Coach Owners Club
Join Date: Oct 2016
Location: Branson, MO
Posts: 178
You mentioned its cold. Did you happen to have a small electrical heater running? That and the microwave and some lighter draws will kick the inverter on some rigs. On mine it will. Check both the main button reset and the paddle breakers on the inverter. Best of luck
Kodiakan is offline   Reply With Quote
Old 11-29-2019, 10:37 AM   #7
Senior Member
 
Join Date: Jul 2014
Posts: 19,662
Look for tripped breakers on the inverter. That's where you problem is.

Look hard on every side, they are lever type or push button type. They will be there.
twinboat is online now   Reply With Quote
Old 11-29-2019, 12:04 PM   #8
Member
 
Join Date: Nov 2017
Posts: 63
Thanks to all who responded so quickly to our request for trouble shooting assistance.

The inverter did have a tripped AC Input Circuit breaker. I reset it and life is good. My battery bank is recharging and the heat is on.

Reflecting on the event we realized that we had two 1KW Vornado heaters running, a 300 watt dehumidifier, a 300 watt air cleaner, and the convection oven all running at the same time, I believe the refrigerator kicked on and it was just too much for it to handle. The Magnum remote panel said " AC overload".

So once again the IRV2 Community saves the day or in our case the night as we will be warm this evening.


Howard
__________________
Guardsman
2005 Country Coach Allure 470
2001 BMW 330 CI
Guardsman is offline   Reply With Quote
Old 11-29-2019, 02:33 PM   #9
Community Moderator
 
CountryFit's Avatar


 
Join Date: Sep 2011
Location: Between the Oceans
Posts: 5,970
Blog Entries: 4
On our Magnim 2800w inverter, when "AC Overload" happens, I have to do a master reset by pressing and holding down the little push button switch at the back for 15 seconds.
__________________
Steven & Polly
2000 Country Coach Intrigue 40'
2014 Ford C-Max Energi
CountryFit is online now   Reply With Quote
Old 11-29-2019, 04:15 PM   #10
Senior Member
 
Smitty77's Avatar
 
Join Date: Aug 2010
Location: Over the next hill, around the next curve...
Posts: 4,478
Howard - Thanks for posting what you found out. Never know when a thread like this via search - will help another...

Best,
Smitty
__________________
Roo II is our 04 Country Coach Allure 40'
OnDRoad for The JRNY! Enjoy life...
Smitty77 is offline   Reply With Quote
Old 11-30-2019, 11:45 AM   #11
Senior Member
 
Mainecoons's Avatar
 
Join Date: Apr 2017
Location: New Mexico
Posts: 144
When we have this problem it is either the GFCI in the bedroom or the circuit breakers located on the inverter behind that steel panel in the battery compartment.
__________________
2002 Country Coach Allure 36, Double Slide
Mainecoons is offline   Reply With Quote
Old 11-30-2019, 11:59 AM   #12
Senior Member
 
cavie's Avatar
 
Join Date: Jul 2018
Posts: 1,975
Quote:
Originally Posted by Guardsman View Post
Thanks to all who responded so quickly to our request for trouble shooting assistance.

The inverter did have a tripped AC Input Circuit breaker. I reset it and life is good. My battery bank is recharging and the heat is on.

Reflecting on the event we realized that we had two 1KW Vornado heaters running, a 300 watt dehumidifier, a 300 watt air cleaner, and the convection oven all running at the same time, I believe the refrigerator kicked on and it was just too much for it to handle. The Magnum remote panel said " AC overload".

So once again the IRV2 Community saves the day or in our case the night as we will be warm this evening.


Howard
Electric management 101
__________________

__________________
2011 Keystone Sprinter BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
cavie is online now   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Trouble shooting Bedroom Slide power outlets Herkdriver Newmar Owner's Forum 4 04-01-2019 07:55 PM
Assistance requested, Goldwing on a lift. Mrchips Class A Motorhome Discussions 15 06-30-2015 10:23 PM
Power Gear Electric Jacks Trouble Shooting. CLIFFTALL Fleetwood Owner's Forum 5 02-07-2013 07:33 PM
Need help trouble shooting bedroom slide out problem? rrob48 Winnebago Industries Owner's Forum 5 03-25-2008 01:18 PM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 06:02 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
×