Old 01-23-2016, 07:39 PM   #1
Senior Member
 
Tobias7000's Avatar


 
Country Coach Owners Club
Newmar Owners Club
Freightliner Owners Club
Join Date: Apr 2013
Location: Portland
Posts: 278
Onan 8000 Randomly Starts?

We went to visit our coach in winter storage this weekend. I found the generator running! When we arrived there was diesel exhaust odor in the covered parking area. Seems like it had been running for awhile. But, it may be that it was not on very long because the genset housing was cool to the touch and my fuel level did not go down very much from what I recall when we parked it. So I cannot be sure if it was on for days or just randomly started today.

I have never used the auto-start feature. I double checked and it was still in manual mode and the shore power detection circuit was working. (I leave the coach plugged in to draw a few amps to trickle charge the batteries.)

In theory, the genset should have never turned on. So why was it on?

Any ideas appreciated - even a way to disconnect the control module that might be initiating the auto start.
__________________

__________________
2015 Newmar Dutch Star 4366 pulling a 2014 Dodge Ram Truck
Tobias7000 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-23-2016, 07:53 PM   #2
Senior Member
 
Clayobx's Avatar


 
Fleetwood Owners Club
Join Date: Dec 2011
Location: Willow Lakes RV & Golf Resort, FL
Posts: 3,116
It, the generator may automatically default and start due to low voltage? Just a guess.
__________________

__________________
Clay & Pebble.. Miss Butter our sweet Goldie (Jan. 2005-Jan. 2015) Sissy our Border Collie
2012 Providence 42 M. Spartan Chassis, 450 ISL
Ford Edge toad, RM All Terrane, TST TPMS, SMI Air Force One, RVM95....
Clayobx is offline   Reply With Quote
Old 01-23-2016, 08:04 PM   #3
Member
 
Join Date: May 2013
Location: Tucson, AZ
Posts: 50
Check your control panel. Your AGS, auto generator start, is enabled. It can be configured to auto start when batteries get to a selected voltage or temperature on some models. Ours is configured to auto start when the voltage drops to 11.8 and set to run for 2 hours, which is enough time to get back to float charging.
__________________
tgdameron is offline   Reply With Quote
Old 01-23-2016, 08:26 PM   #4
Senior Member
 
Steve Ownby's Avatar
 
Join Date: Nov 2008
Location: Cosby, Tn
Posts: 6,394
Quote:
Originally Posted by Tobias7000 View Post
We went to visit our coach in winter storage this weekend. I found the generator running! When we arrived there was diesel exhaust odor in the covered parking area. Seems like it had been running for awhile. But, it may be that it was not on very long because the genset housing was cool to the touch and my fuel level did not go down very much from what I recall when we parked it. So I cannot be sure if it was on for days or just randomly started today.



I have never used the auto-start feature. I double checked and it was still in manual mode and the shore power detection circuit was working. (I leave the coach plugged in to draw a few amps to trickle charge the batteries.)



In theory, the genset should have never turned on. So why was it on?



Any ideas appreciated - even a way to disconnect the control module that might be initiating the auto start.

For years there have been reports of phantom starts with the Onan 7500 and by extension the 8000. This is even on units with out an auto gen start installed. It seems to be caused by moisture intrusion into a connector in the control wiring going into the generator. The fix is to open the connector and dry it out & use a dielectric grease on the connector.
__________________
Steve Ownby
Full time since 2007
2003 Monaco Signature
Steve Ownby is offline   Reply With Quote
Old 01-23-2016, 08:38 PM   #5
Senior Member
 
Tobias7000's Avatar


 
Country Coach Owners Club
Newmar Owners Club
Freightliner Owners Club
Join Date: Apr 2013
Location: Portland
Posts: 278
Quote:
Originally Posted by Steve Ownby View Post
For years there have been reports of phantom starts with the Onan 7500 and by extension the 8000. This is even on units with out an auto gen start installed. It seems to be caused by moisture intrusion into a connector in the control wiring going into the generator. The fix is to open the connector and dry it out & use a dielectric grease on the connector.
This makes a lot of sense. It has been raining heavily recently. Thanks for sharing!
__________________
2015 Newmar Dutch Star 4366 pulling a 2014 Dodge Ram Truck
Tobias7000 is offline   Reply With Quote
Old 01-24-2016, 10:14 PM   #6
Senior Member
 
Tobias7000's Avatar


 
Country Coach Owners Club
Newmar Owners Club
Freightliner Owners Club
Join Date: Apr 2013
Location: Portland
Posts: 278
Quote:
Originally Posted by Tobias7000 View Post
This makes a lot of sense. It has been raining heavily recently. Thanks for sharing!
Update for all: the molex-like connector to the genset is triple sealed and was completely dry. I sprayed with a moisture replacing electrical contact cleaner anyway. Next, I think I'll replace the head end unit (display and buttons mounted in the control center) as the backlight light flickers frequently and makes me wonder how the rest of the electronics are doing.
__________________
2015 Newmar Dutch Star 4366 pulling a 2014 Dodge Ram Truck
Tobias7000 is offline   Reply With Quote
Old 01-25-2016, 07:37 AM   #7
Senior Member
 
Clayobx's Avatar


 
Fleetwood Owners Club
Join Date: Dec 2011
Location: Willow Lakes RV & Golf Resort, FL
Posts: 3,116
Quote:
Originally Posted by Tobias7000 View Post
Update for all: the molex-like connector to the genset is triple sealed and was completely dry. I sprayed with a moisture replacing electrical contact cleaner anyway. Next, I think I'll replace the head end unit (display and buttons mounted in the control center) as the backlight light flickers frequently and makes me wonder how the rest of the electronics are doing.
Please keep us posted and if possible some pics to help with your diagnoses. I have the 8000 KW no issues yet, knock on wood, but your trouble shooting will help those with like Onan products should the need arise.
__________________
Clay & Pebble.. Miss Butter our sweet Goldie (Jan. 2005-Jan. 2015) Sissy our Border Collie
2012 Providence 42 M. Spartan Chassis, 450 ISL
Ford Edge toad, RM All Terrane, TST TPMS, SMI Air Force One, RVM95....
Clayobx is offline   Reply With Quote
Old 02-26-2016, 04:23 PM   #8
Senior Member
 
Rsponsford's Avatar


 
Country Coach Owners Club
Join Date: Aug 2015
Location: Santa Rosa, CA
Posts: 375
There is also a setting in the AGS which tells it to cycle the generator every x number of days for x number of hours if the genset hasn't been operated during that time interval. I have mine set to run for two hours every 21 days if it hasn't been run during that period. I think it will activate this feature even if the AGS is set to the manual mode.
__________________

Russ
1990 Country Coach Concept 36' Anteres
1997 Jeep Wrangler, Blue Ox
Rsponsford is offline   Reply With Quote
Old 02-26-2016, 06:41 PM   #9
Senior Member
 
Join Date: Jul 2007
Posts: 678
To OP.
I had an Onan 7500 on a previous coach that auto started and there wasn't an auto start feature on that coach.

I pulled the control wire connector (near the upper passenger side of the generator) to the generator apart, cleaned it, used a small amount of dielectric grease on the contacts and re-assembled the connector.

Didn't have the problem again but never really trusted the generator and if I was going to be away from the coach for several days I would disconnect the house batteries to prevent any accidental start of the generator.
__________________

__________________
Pete - Full Timing
2000 Country Coach Magna 40', CAT C10, #5892
2006 Jeep Liberty
phays is offline   Reply With Quote
Reply

Tags
onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Another Onan 8000 question courtjester RV Systems & Appliances 7 10-14-2015 11:38 PM
Onan 8000 Stops After a few Minutes When Freezing Outside FFaust RV Systems & Appliances 12 10-13-2015 06:53 PM
Onan Quiet Diesel starts, then shuts off dave freitas RV Systems & Appliances 6 03-12-2015 05:52 PM
Onan 8000 stops on it own!!! Larry Geese RV Systems & Appliances 9 06-17-2014 05:34 PM
Onan 8000 ticking noise rescue595 National RV Owner's Forum 7 03-09-2014 11:53 AM

» Virginia Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 05:48 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.