06-29-2008, 04:32 PM
|
#1
|
|
Senior Member
Monaco Owners Club
Join Date: Jun 2005
Location: Was Fairbanks, AK now Somewhere, Lower 48
Posts: 796
|
Hi Guys and Gals,
Obviously I didn't learn enough about electricity while operating a power plant for a job for 31 years.
While dry camping at the FMCA Rally in Albany, OR. a couple weeks ago, it was cold enough to have to run two heatpumps. While doing this we used our microwave and the TV. Welllll....we noticed that our electrical management panel was wacking out and was going up and down between 30amps down to 20amps and couldn't make up it's mind where to stay before the 30amp breaker on the generator tripped. This happened 3 times before I decided to not run both heatpumps. It turns out that the heatpumps pull a LOT more juice than the air conditioners. I didn't even think of that before. I just thought that since they were in the same unit that they would pull the same amount of electricity.
I guess I figured that an 8KW generator would be enough to power a 50 amp coach but it turns out that's not the case. I was bugged that there was only a 30 amp breaker on the generator than a 50 amp breaker. Well duh...I guess that's because a 8kw generator can't carry a 50 amp load. Is this the case or am I wrong?
I ran this buy the Gauranty service rep at the rally and he just smirked and told me about how much the heatpumps took to run them. It turns out that everything was working just fine thank-you.
Now I just need a 10KW generator. The problem with that is I have to get a higher end coach. Well maybe not, but I don't feel like forking out more bucks.
Ta ta for now,
AKBrick
__________________
2007 Safari Cheetah 40SFD 350 CAT / Allison 3000 / RR8R chassis.
2007 Saturn Vue Auto/front wheel drive toad. Blue Ox Aladdin tow bar. Apollo brake system, Pressure Pro, Surge Guard. 2 Norwich Terriers. Dog shows, golf, RETIRED, fulltimer.
|
|
|
|
| |
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
06-29-2008, 04:32 PM
|
#2
|
|
Senior Member
Monaco Owners Club
Join Date: Jun 2005
Location: Was Fairbanks, AK now Somewhere, Lower 48
Posts: 796
|
Hi Guys and Gals,
Obviously I didn't learn enough about electricity while operating a power plant for a job for 31 years.
While dry camping at the FMCA Rally in Albany, OR. a couple weeks ago, it was cold enough to have to run two heatpumps. While doing this we used our microwave and the TV. Welllll....we noticed that our electrical management panel was wacking out and was going up and down between 30amps down to 20amps and couldn't make up it's mind where to stay before the 30amp breaker on the generator tripped. This happened 3 times before I decided to not run both heatpumps. It turns out that the heatpumps pull a LOT more juice than the air conditioners. I didn't even think of that before. I just thought that since they were in the same unit that they would pull the same amount of electricity.
I guess I figured that an 8KW generator would be enough to power a 50 amp coach but it turns out that's not the case. I was bugged that there was only a 30 amp breaker on the generator than a 50 amp breaker. Well duh...I guess that's because a 8kw generator can't carry a 50 amp load. Is this the case or am I wrong?
I ran this buy the Gauranty service rep at the rally and he just smirked and told me about how much the heatpumps took to run them. It turns out that everything was working just fine thank-you.
Now I just need a 10KW generator. The problem with that is I have to get a higher end coach. Well maybe not, but I don't feel like forking out more bucks.
Ta ta for now,
AKBrick
__________________
2007 Safari Cheetah 40SFD 350 CAT / Allison 3000 / RR8R chassis.
2007 Saturn Vue Auto/front wheel drive toad. Blue Ox Aladdin tow bar. Apollo brake system, Pressure Pro, Surge Guard. 2 Norwich Terriers. Dog shows, golf, RETIRED, fulltimer.
|
|
|
|
| |
|
06-29-2008, 05:18 PM
|
#3
|
|
Senior Member
Monaco Owners Club
Join Date: Feb 2008
Location: Western Montana on the Divide
Posts: 729
|
My Onan 8KW QD generator has a 35 amp breaker. I was exercising the generator today running both A/C's, the fridge and one TV and the EM panel indicated 39 amps. It ran for 1.5 hours with this load without tripping the generator breaker. Go figure.
__________________
Bob Retired Army Traveling alone now.
2008 Camelot 40 PDQ 4 slides ISL400
Western MT in summer, AZ, NV in winter
|
|
|
|
| |
|
06-30-2008, 03:02 AM
|
#4
|
|
Community Administrator
Newmar Owners Club
Join Date: May 2000
Location: Newark, DE
Posts: 13,894
|
You don't need a 10KW generator.
The 30 amp breaker is a ganged breaker with a 30 amp breaker on each leg.
I frequently run both AC/heatpumps on my 7.5KW Onan.
There should be one AC/heatpump on each leg.
It sounds like something is not wired correctly.
__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, '07 DSDP, '11 Virtual RV

|
|
|
|
| |
|
06-30-2008, 04:05 AM
|
#5
|
|
Senior Member
Workhorse Chassis Owner
Join Date: Sep 2007
Location: st.charles mo.
Posts: 564
|
These generators are not designed to run everything in the MH at the same time. That's why they call it an RV not a HOUSE!
__________________
|
|
|
|
| |
|
06-30-2008, 04:26 AM
|
#6
|
|
Community Administrator
Newmar Owners Club
Join Date: May 2000
Location: Newark, DE
Posts: 13,894
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">These generators are not designed to run everything in the MH at the same time. </div></BLOCKQUOTE>
That is correct.
I cannot run everything at the same time, but I can run 2, 3 or 4 things at once depending on their amperage requirements.
__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, '07 DSDP, '11 Virtual RV

|
|
|
|
| |
|
06-30-2008, 04:50 AM
|
#7
|
|
Moderator Emeritus
Join Date: Jan 2000
Location: Greenwell Springs, LA EBR
Posts: 2,258
|
Something to check would be how the loads are distributed on each buss.
The loads were not distributed properly on the two busses in my fiver from the factory. It would actually trip the shore power breaker at some campgrounds.
Well after a check of the loads on each buss I found out why. After re-distributing the loads on the two busses I have had no further problems.
Of course I should have checked this from the start as I have seen this situation before. Even in high end coaches by well respected manufacturers. So I should have checked this before I even made the first trip.......
But like most, I did not until the problem showed up.....
__________________
Don Fauntleroy (W5IT) 99 F-350 Cab and Chassis with a Herrin Hauler bed now towing a 2006 3612 DS Raptor Toyhauler. 2002 and 2006 National Rally Wagonmaster.
"Words of Wisdom"
|
|
|
|
| |
|
06-30-2008, 05:00 AM
|
#8
|
|
Senior Member
Join Date: Apr 2002
Location: Waynesville Missouri
Posts: 107
|
If I am doing this right:
WATTS = AMPS * VOLTS
AMPS = WATTS / VOLTS
8000 WATTS = 66 AMPS TOTAL
(8000/120 =66.66)
33 AMPS PER LEG
THUS THE 30 AMP BREAKER(S)
Jack
__________________
2003 CHEV 2500HD EXT CAB, DMAX Allison SB 4X4
2001 Dutchmen Classic 27RK 5W
|
|
|
|
| |
|
06-30-2008, 05:04 AM
|
#9
|
|
Community Administrator
Newmar Owners Club
Join Date: May 2000
Location: Newark, DE
Posts: 13,894
|
You got it right.
__________________
Adios, Dirk - '84 Real Lite Truck Camper, '86 Wilderness Cimarron TT, '07 DSDP, '11 Virtual RV

|
|
|
|
| |
|
06-30-2008, 05:15 AM
|
#10
|
|
Senior Member
Monaco Owners Club
Join Date: Jun 2005
Location: Was Fairbanks, AK now Somewhere, Lower 48
Posts: 796
|
Thanks guys,
I woke up this morning trying to remember OHM's Law and then I couldn't go back to sleep. You've solved it for me.
I'll also have to check what's on each leg for general knowledge of my coach.
Thanks again all,
AKBrick
__________________
2007 Safari Cheetah 40SFD 350 CAT / Allison 3000 / RR8R chassis.
2007 Saturn Vue Auto/front wheel drive toad. Blue Ox Aladdin tow bar. Apollo brake system, Pressure Pro, Surge Guard. 2 Norwich Terriers. Dog shows, golf, RETIRED, fulltimer.
|
|
|
|
| |
|
06-30-2008, 01:55 PM
|
#11
|
|
Senior Member
Join Date: Dec 2007
Location: Blairsville,GA
Posts: 257
|
Are you sure it's a heat pump? Heat pumps generally draw the same whether heating or cooling, It may be electric strip heat, or the emergency heat may have kicked in, which is electric strips, which draw considerably more power. Could be the antishort cycle timer not working though, judging from the amp surge, this could be it. If power is interupted to the compressor, it locks the compressor out for a predetermined time, allowing gas pressures to drop, allowing the compressor to restart normally. Just a few things to ponder.
__________________
|
|
|
|
| |
|
06-30-2008, 01:57 PM
|
#12
|
|
Senior Member
Join Date: Dec 2007
Location: Blairsville,GA
Posts: 257
|
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by MO _ Jack:
If I am doing this right:
WATTS = AMPS * VOLTS
AMPS = WATTS / VOLTS
8000 WATTS = 66 AMPS TOTAL
(8000/120 =66.66)
33 AMPS PER LEG
THUS THE 30 AMP BREAKER(S)
Jack </div></BLOCKQUOTE>
You are correct sir!
__________________
|
|
|
|
| |
|
06-30-2008, 08:03 PM
|
#13
|
|
Member
Join Date: Feb 2007
Posts: 53
|
If it is a true heat pump, the system just reverses and extracts heat from the outside air. They don't work very well below 35 degrees as a rule, and then some other type of heat must be used. In RV's it is a heatstrip (resistance coil) mounted in the A/C unit. There are regular RV A/C's that are not heat pumps, but they have a heat strip installed.
On either system the compressor is not supposed to run when the heat strip is energized because the amount of wattage drawn would be prohibitive. You may have a unit that is mis-wired internally or has a relay or electronic control stuck allowing both compressor and heat strip to be energized at the same time in one of your 2 units. Check the actual amperage draw of each unit, separately. You may find one that pulls a bit more load than it should.
Happy travels,
Sparetire
__________________
|
|
|
|
| |
|
06-30-2008, 08:12 PM
|
#14
|
|
Senior Member
Monaco Owners Club
Join Date: Jun 2005
Location: Was Fairbanks, AK now Somewhere, Lower 48
Posts: 796
|
Thanks for the info guys. Some of it may be a little over my head but not too bad. I think I'll let Gauranty RV Service look into it in August. I never checked the amperage of each heatpump. I should, but with the 100 degree outside temps here in Deer Park, WA. I think I'll pass on running the heatpumps for awhile.
AKBrick
__________________
2007 Safari Cheetah 40SFD 350 CAT / Allison 3000 / RR8R chassis.
2007 Saturn Vue Auto/front wheel drive toad. Blue Ox Aladdin tow bar. Apollo brake system, Pressure Pro, Surge Guard. 2 Norwich Terriers. Dog shows, golf, RETIRED, fulltimer.
|
|
|
|
| |
|
 |
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

»
Recent Discussions

»
Upcoming Rallies
No events scheduled in the next 365 days.
|
»
iRV2 on facebook
|