Old 03-22-2016, 09:57 PM   #15
Senior Member


 
Monaco Owners Club
Join Date: May 2014
Location: Satsop WA
Posts: 1,405
Thank you so much for this info.
We have the exact same meter as seen in the first post, and we are only running 30 amp on gen.
This explains alot!
Thank you again, very helpful.
__________________

__________________
2007 Alpine Limited SE
TMan59 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-22-2016, 10:57 PM   #16
Member
 
VinceB's Avatar
 
Join Date: Oct 2011
Location: La Verne, CA
Posts: 68
Quote:
Originally Posted by dmastroluca View Post
When I replaced mine last year, I marked each wire from the breakers and to the power sources, then took iPhone pictures of the labeled wires. I used a silver and a black sharpie to put the marks on the wires. Yanked out the old unit, and wired the new unit per the pictures. Everything fired right up.

1. Double check the dip switch settings to match your old unit.

2. Please remember to shut off ALL battery switches or disconnect battery cables so you don't get an accidental inverter/generator call while you are in there.
Thanks for the suggestions.
__________________

__________________
'01 Diplomat 36B usually towing '09 Rubicon or enclosed trailer
F&R Hughes Watts, Rear Hughes X-brace
Banks Turbo & ECU
VinceB is offline   Reply With Quote
Old 03-28-2016, 05:26 PM   #17
Member
 
VinceB's Avatar
 
Join Date: Oct 2011
Location: La Verne, CA
Posts: 68
Mission Complete.

The kit arrive last week. I 2x checked all the part numbers as is habit. The kit is very nicely done. There are new butt connectors already attached and the pin connectors are fully assembled. Included were a new transducer and a common wire already stripped and ready to go. I left the old transducer and old common wire in place – saw no reason to go through a lot of extra work in order to change them out. The 3-pin power supply and genset signal wire get re-used and just plug right in to the new main board.

Then I laid out the parts so I could have a good understanding of the modifications I was about to make to my system.

All you are doing with the kit is swapping out the 2 boards (main processor and monitor). The boards talk to each other via an original cable that has 4 wires. The new boards require only 3 wires so you are going to abandon one wire in place. The only trick here is to make sure you connect color to same color via the new pin connector harnesses that are provided. Except for red, the colors of the harnesses do not match one-for-one those in the cable so you need to pay attention what color you splice to and do the same on the other end. The attached pix will make this clearer.

I made sure all shore power and all batteries were disconnected and took an "as-is" pic. I include that because some may not know where to find the main board.

Then I labeled all the breaker wires starting with #1 on the processor board at the top and worked down to position #8. See pic. I spliced in the new pin connectors.

The bezel around the monitor panel just pops off so you can get to the insert that goes in front of the panel: behind the insert are the screws that hold the monitor panel in place. The insert is where all the text is printed.

I peeled the tape off the old monitor board that had the loads printed on it and stuck it on the new panel in the same position as the old. Now the new panel looks exactly like the original panel as pictured in post #1 of this thread. I did this assuming that the new board’s defaults will operate the same way as the old one did. I have no idea why the blank ones are at the top but assume that Monaco knew what they were doing when they installed it this way.

Speaking of defaults: the included manual says the DIP switches are set at the factory to the most common installation so I left them that way. As the old board had jumpers, you can’t use the old board as a reference to set your new switches. I suppose you could read all the documentation and figure it all out, but being that the defaults are the most common, I went with them. If in the future the settings do not work as I would like, I’ll dig deeper into the documentation and figure it out then.

After rewiring all the breaker wires and 2x checking everything I skipped past the system pre-check in the installation guide. All looked OK and it was either going to work or not work.

I powered up and ran it through its paces. It works the same as the day I bought it. Thanks everyone for your insights and suggestions.

All in all, it is a simple repair and went better than expected. Looking at all the wires and circuit boards can be intimidating. Once I got past that it took only about an hour.
Attached Thumbnails
Click image for larger version

Name:	IMG_0150.jpg
Views:	40
Size:	341.9 KB
ID:	122565   Click image for larger version

Name:	IMG_0154.jpg
Views:	39
Size:	279.8 KB
ID:	122566  

Click image for larger version

Name:	IMG_0155.jpg
Views:	38
Size:	363.4 KB
ID:	122567   Click image for larger version

Name:	IMG_0152.jpg
Views:	40
Size:	361.3 KB
ID:	122568  

__________________
'01 Diplomat 36B usually towing '09 Rubicon or enclosed trailer
F&R Hughes Watts, Rear Hughes X-brace
Banks Turbo & ECU
VinceB is offline   Reply With Quote
Old 03-28-2016, 07:00 PM   #18
Registered User
 
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
Great job!

How about a photo of your new display powered up?

Dr4Film ----- Richard
Dr4Film is offline   Reply With Quote
Old 03-28-2016, 07:45 PM   #19
Member
 
VinceB's Avatar
 
Join Date: Oct 2011
Location: La Verne, CA
Posts: 68
Quote:
Originally Posted by Dr4Film View Post
Great job!

How about a photo of your new display powered up?

Dr4Film ----- Richard
Proudly... and a vid as well showing what happens as it comes online. Don't blame me for the ad. I think IRV2 did it which is OK by me for the service they provide us.
Attached Thumbnails
Click image for larger version

Name:	IMG_0160.jpg
Views:	37
Size:	350.2 KB
ID:	122594  
Attached Files
__________________
'01 Diplomat 36B usually towing '09 Rubicon or enclosed trailer
F&R Hughes Watts, Rear Hughes X-brace
Banks Turbo & ECU
VinceB is offline   Reply With Quote
Old 03-28-2016, 07:52 PM   #20
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 4,835
Life is good
__________________
Jim J
2002 Monaco Windsor 38 PKD
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 03-29-2016, 09:05 AM   #21
Senior Member
 
dmastroluca's Avatar
 
Monaco Owners Club
Join Date: Jul 2015
Location: Henderson, Nevada
Posts: 309
Quote:
Originally Posted by VinceB View Post
Speaking of defaults: the included manual says the DIP switches are set at the factory to the most common installation so I left them that way.
If you look on page 5 of the manual it says:

"Dip-switch S4 determines if energy management is enabled when 120 VACGen-Set service is available. If S4 is in the “on” position, energy management will be disabled, but the Display Panel will still display total system current. If S4 is in the “OFF” position, energy management will be enabled and the current rating of the Gen-Set needs to be selected using dip-switch S5. With S5 set to the “ON” position, system current drawn from the generator will be limited to 45Amps. With S5 set to the “OFF” position, system current drawn from the generator will be limited to 60Amps."

If you leave S4 and S5 in the default ON position, you will not get any energy management while on generator, and only get 45 amps from your generator. Not sure what generator you have, but mine is a 7.5 KW with an output of 60 amps. I had to set dip switch 4 and 5 to OFF so I would get all the amps from my generator.

A good test would be to run your generator and fire up both HVAC units, electric water heater, inverter with loads, and run the microwave (with a bowl of water). If your EMS starts shedding loads at 45 amps, you have it set up wrong.
__________________
Dan & April Mastroluca-2001 Monaco Diplomat 36PBD Cummins ISC330HP 8.3L Diesel 6-Speed Allison Transmission-Towing 2011 Cadillac SRX w/ Blue Ox Aventa BX7445 & Roadmaster Invisibrake FMCA# F452291 https://www.facebook.com/dmastroluca GO DODGER BLUE!!!
dmastroluca is offline   Reply With Quote
Old 03-29-2016, 10:11 AM   #22
Senior Member


 
Monaco Owners Club
Join Date: May 2014
Location: Satsop WA
Posts: 1,405
Ok, I have to ask, where is dp switch 4 located?
I would like to check mine also.
Thank you, we have been on 30 amps a long time.
__________________
2007 Alpine Limited SE
TMan59 is offline   Reply With Quote
Old 03-29-2016, 10:40 AM   #23
Senior Member
 
dmastroluca's Avatar
 
Monaco Owners Club
Join Date: Jul 2015
Location: Henderson, Nevada
Posts: 309
Quote:
Originally Posted by TMan59 View Post
where is dp switch 4 located?
On the EMS board in your breaker panel.
Attached Thumbnails
Click image for larger version

Name:	dip.jpg
Views:	27
Size:	155.7 KB
ID:	122639  
__________________
Dan & April Mastroluca-2001 Monaco Diplomat 36PBD Cummins ISC330HP 8.3L Diesel 6-Speed Allison Transmission-Towing 2011 Cadillac SRX w/ Blue Ox Aventa BX7445 & Roadmaster Invisibrake FMCA# F452291 https://www.facebook.com/dmastroluca GO DODGER BLUE!!!
dmastroluca is offline   Reply With Quote
Old 03-29-2016, 12:53 PM   #24
Member
 
VinceB's Avatar
 
Join Date: Oct 2011
Location: La Verne, CA
Posts: 68
Quote:
Originally Posted by dmastroluca View Post
If you look on page 5 of the manual it says:

"Dip-switch S4 determines if energy management is enabled when 120 VACGen-Set service is available. If S4 is in the “on” position, energy management will be disabled, but the Display Panel will still display total system current. If S4 is in the “OFF” position, energy management will be enabled and the current rating of the Gen-Set needs to be selected using dip-switch S5. With S5 set to the “ON” position, system current drawn from the generator will be limited to 45Amps. With S5 set to the “OFF” position, system current drawn from the generator will be limited to 60Amps."

Good catch - thanks.
.
.
__________________
'01 Diplomat 36B usually towing '09 Rubicon or enclosed trailer
F&R Hughes Watts, Rear Hughes X-brace
Banks Turbo & ECU
VinceB is offline   Reply With Quote
Old 03-29-2016, 09:23 PM   #25
Senior Member


 
Monaco Owners Club
Join Date: May 2014
Location: Satsop WA
Posts: 1,405
Quote:
Originally Posted by dmastroluca View Post
On the EMS board in your breaker panel.

Thank you very much!
__________________
2007 Alpine Limited SE
TMan59 is offline   Reply With Quote
Old 04-03-2016, 05:32 PM   #26
Member
 
VinceB's Avatar
 
Join Date: Oct 2011
Location: La Verne, CA
Posts: 68
Quote:
Originally Posted by dmastroluca View Post
On the EMS board in your breaker panel.
I found that a dental pick worked great with which to move the switches.
__________________

__________________
'01 Diplomat 36B usually towing '09 Rubicon or enclosed trailer
F&R Hughes Watts, Rear Hughes X-brace
Banks Turbo & ECU
VinceB is offline   Reply With Quote
Reply

Tags
service



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gen set service neilnoff MH-General Discussions & Problems 12 06-03-2015 01:34 PM
Engine Gen warning lite on when running gen set Gumby Monaco Owner's Forum 11 06-01-2012 08:15 AM
MPG w/Gen set & Coach AC or Dash AC Field Trip Newmar Owner's Forum 8 07-11-2011 01:48 PM
auto start gen/set & air cond chris cross Alpine Coach Owner's Forum 2 06-11-2010 07:27 AM
MH battery set up...: Anyone plug this set up in? fkloster Class A Motorhome Discussions 6 04-30-2010 08:58 AM

» Featured Campgrounds

Reviews provided by


Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 02:37 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, vBulletin Solutions, Inc.