I have the same MH and I presume you have a 4 button thermostat.
If you have a 4 button Dometic thermostat try this reset procedure:
1. Turn the ON/OFF switch to ON. The display light with data should come on.
2. Depress mode to activate display light.
3. Depress the bottom two buttons (up & down) together.
4. While still holding the two buttons add the third from the bottom (mode) , hold all three for a few seconds.
5. Release the third (mode) button.
6. Release the bottom two (up & down) together.
7. Depress the mode button. The display light should be off. If not, repeat steps 2 through 6.
Unfortunately, these units are no longer made and you have 2 options.
1. You can have the unit repair:
william hendrix - Home
Frerichs Electronics
2. You can replace it which also requires replacing the PC boards in the AC unit.
We had ours replaced with a new Dometic CCC2 unit. When we did, we had another problem. The thermostat is mounted on an outside wall and there is a small cavity behind the thermostat where the wires are run. The high temp in the wall meeting the cool air inside, created condensation on the thermostat's PC board which caused it to short out. To solve this I used low expansion spray foam in the wall and sheet foam on the back of the PC board. So far, everything is fine. If not I will have to relocate thermostat to an interior wall.