Genset when Plugged in to Shore Power?
Old 07-25-2011, 12:32 PM   #1
rpasetto is offline
Senior Member
Join Date: Dec 2008
Posts: 240
Doing my Genset maintenance this AM and, as always, after filling up the oil I disconnect from shore power before starting up the genset to test it.

I recall being told that it's "perfectly OK" to stay plugged in to shore power as the transfer switch will switch over to the genset. Of course I realize that, in the (unlikely?) event that shore power and genset were to "connect", lots of stuff would get blown away.

Opinions? Anyone ever run into a problem leaving shore power plugged in while starting the genset?

__________________
Rick P. '03 Dynasty
  Reply With Quote
   
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-25-2011, 05:18 PM   #2
Our Time is offline
Senior Member
Our Time's Avatar


Monaco Owners Club
Join Date: Aug 2006
Location: Ft Myers Fl / Omaha Ne
Posts: 572
When I run the generator while connected to shore power, I open the breaker on the generator so it does not apply power to the coach.

__________________
Chuck & Mary
2008 Monaco Diplomat 40 SKQ
2008 Enclave Toad
  Reply With Quote
   
Old 07-25-2011, 05:29 PM   #3
Bill Adams is offline
Registered User
Join Date: Dec 2006
Location: Traveling the lower 48
Posts: 2,450
There is no need to connect, disconnect, power up, power down, switch breakers or anything else when you start up or power down your generator "assuming" that you have an automatic transfer switch. The transfer switch will choose the generator as the primary connection when it comes on and will default back to shore power when the generator is powered down. If neither is available the inverter will kick in.
When powering a generator on I generally do nothing as the transfer is instantaneous. However, in my coach but not all coaches, the transfer from generator to shore power does cause a momentary power interruption. Because of this I will power off the A/C units (that's all) before shutting down the genset and then power them back on once I have good shore power. Otherwise, there is nothing that needs to be done.
__________________
  Reply With Quote
   
Old 07-25-2011, 05:33 PM   #4
rpasetto is offline
Senior Member
Join Date: Dec 2008
Posts: 240
Yeah, but what if the Xfer switch fails and locks in the genset before disconnecting shore power? ... even if only for a few milliseconds? What can happen?
__________________
Rick P. '03 Dynasty
  Reply With Quote
   
Old 07-25-2011, 06:15 PM   #5
Diplomat Don is offline
Senior Member
Diplomat Don's Avatar


Monaco Owners Club
Join Date: Apr 2005
Location: Moorpark, Ca.
Posts: 2,109
I did it once by accident when I was excercising the generator. It tripped a couple of citcuits. I decided it just wasn't worth taking a chance. I NEVER operate them together.
__________________
Don & Mary
2005 Monaco Diplomat 36SKT - 400 ISL
2010 Nissan Frontier - CrewCab - 4WD
  Reply With Quote
   
Old 07-25-2011, 06:21 PM   #6
fansill is offline
Senior Member
fansill's Avatar


Nor'easters Club
Fleetwood Owners Club
Join Date: Feb 2011
Location: Massachusetts
Posts: 316
Ditto to Bill Adams answer... I attended a seminar this weekend at an FMCA Rally and one of the RV Techs said the exact same thing. He said that on newer coachs with the automatic transfer system, the Gennie will override any shore power. But I also, shut off anything that I feel will be affected by the momentary lapse of power as the two systems pass off on one another.

Just reporting what a supposed expert said....

Faith
__________________
Faith and Bob, Bitsy the Papillon and Truffles the Sheltie
2005 Revolution LE - Sometimes the Goldwing Trike
Northern Massachusetts and the rest of the Country.
  Reply With Quote
   
Old 07-25-2011, 06:23 PM   #7
Mr_D is offline
Senior Member
Mr_D's Avatar


Join Date: May 2011
Location: Vancouver, WA
Posts: 4,282
Quote:
Originally Posted by Our Time View Post
When I run the generator while connected to shore power, I open the breaker on the generator so it does not apply power to the coach.
What does that accomplish? The gen set needs to have about ½ load applied while running to heat up the windings enough to burn off the moisture. If you're not doing that then no need to run the engine. You run the gen every month, the engine itself doesn't need it, the windings do.
__________________
2002 Newmar Dutch Star 4090 ISC 350/1050 with Banks Kit, now 435/1200
Charter Good Sam Lifetime Member, FMCA f47302s
RV'ing since 1957, NRA Benefactor Life Member
  Reply With Quote
   
Old 07-25-2011, 06:35 PM   #8
rpasetto is offline
Senior Member
Join Date: Dec 2008
Posts: 240
Quote:
Originally Posted by Mr_D View Post
What does that accomplish? The gen set needs to have about ½ load applied while running to heat up the windings enough to burn off the moisture. If you're not doing that then no need to run the engine. You run the gen every month, the engine itself doesn't need it, the windings do.
Yes Mr. D, that's why genset manuf. states to run "under load". I was talking about running genset after oil change, just to check for leaks. I don't know if that was what Our time was talking about.
__________________
Rick P. '03 Dynasty
  Reply With Quote
   
Old 07-25-2011, 07:13 PM   #9
LVJ58 is offline
Senior Member
LVJ58's Avatar


Join Date: Jul 2000
Location: Las Vegas, NV
Posts: 1,250
Hi Rick,

We also have an ATS on our coach and although it's designed to automatically switch to the priority power source input, there's always the potential for failure in any electromechanical device, therefore I always disconnect from shore power before firing up the generator when exercising it under load.

It requires very little effort on my part to disconnect the shore power plug and I feel more comfortable doing so.
__________________
Jim & SherrySeward

2000 Residency 3790 v10 w/tags
  Reply With Quote
   
Old 07-25-2011, 07:20 PM   #10
Bill Adams is offline
Registered User
Join Date: Dec 2006
Location: Traveling the lower 48
Posts: 2,450
Some people like wearing a belt and suspenders. It's never necessary, but you can't argue with the folks that believe they need them!
If you live your life questioning what could happen "if", you would never leave your house! I did have a transfer switch fail a few years back. When it did, only the shore connection worked. If I powered up the genset (connected to shore power or not) nothing happened, it just didn't switch. No harm, no foul (and no power).
__________________
  Reply With Quote
   
Old 07-25-2011, 07:29 PM   #11
BigSkyBob is offline
Senior Member
BigSkyBob's Avatar


Monaco Owners Club
Join Date: Feb 2008
Location: Western Montana on the Divide
Posts: 729
I'm with Mr. Adams. I have never disconnected shore power when exercising the generator. The transfer switch is not a fail safe device but a failure is very uncommon and will usally fail on one side in the open position. The only thing I do is disconnect ALL loads so there is no arc at the contacts when the switch is made, then apply a 50% load for an hour.
__________________
Bob Retired Army Traveling alone now.
2008 Camelot 40 PDQ 4 slides ISL400
Western MT in summer, AZ, NV in winter
  Reply With Quote
   
Old 07-25-2011, 10:39 PM   #12
jablair is offline
Member
Join Date: Nov 2010
Posts: 89
The ATS uses "break before make" contacts. Meaning it is highly unlikely, even with a mechanical failure, that the two input sources would both be connected. Suppose anything is possible, but highly unlikely. Like Bill Adams said, some people will still want or need to take the extra precaution. It is certainly not going to hurt anything even if unnecessary.
__________________
  Reply With Quote
   
Old 07-26-2011, 05:07 AM   #13
Our Time is offline
Senior Member
Our Time's Avatar


Monaco Owners Club
Join Date: Aug 2006
Location: Ft Myers Fl / Omaha Ne
Posts: 572
When I run the generator for oil change, coolant change, etc while connected to shore power I open the breaker. I do load the generator up on a periodic basis, however I have popped the breakers for the energy management system when switching from shore to generator. Before I switch from one to the other, I turn off the generator or shore power. To me, it's not worth the chance of a major power flux.
__________________
Chuck & Mary
2008 Monaco Diplomat 40 SKQ
2008 Enclave Toad
  Reply With Quote
   
Old 07-26-2011, 02:07 PM   #14
azstork is offline
Member
azstork's Avatar
Monaco Owners Club
Join Date: May 2009
Location: Peoria, AZ
Posts: 45
I'm with Bill Adams on this one - I have taken apart the Transfer Switch on my HR and I think it would be impossible to have shore power and generator inputs connected together - The line to the coach is attached to the center contacts of a relay-energized switch - When the generator is "OFF" the contacts will by default go to the shore power input. If the generator is started, the transfer switch will sense the power in the generator input and after a time delay to allow the genset to get up to speed, it will energize the relay to pull the contacts to connect the coach line to the generator input - It will automatically and simultaneously disconnect the shore power input. If the transfer switch does not work correctly, the contacts will stay in the coach to shore power position, but will not and cannot connect both inputs together. Even if there is arcing that sticks (welds)the contacts in one position, it will still not connect the inputs together. Hope this makes sense.

__________________
Gary & Debi
2006 HR Ambassador 40DFD - 2008 Jeep Wrangler
US Gear Brake System - SafTte TPMS
  Reply With Quote
   
Reply

Tags
power


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
shore power problem cydonia-jacc Winnebago Industries Owner's Forum 8 12-30-2010 08:49 AM
Genset will not switch for internal power OpaRon Newmar Owner's Forum 8 05-17-2009 05:39 PM
Electrical - Shore Power 15A Old Rv'er Alpine Coach Forum 15 07-29-2008 07:04 PM
Appliances don't work with shore power wicked5ltr Travel Trailer Discussion 11 01-30-2007 02:47 PM
How To Keep Engine Battery Charged While on Shore Power FLYTYER Winnebago Industries Owner's Forum 15 06-18-2006 05:09 AM

Download our Mobile App






1% for the Planet
» Upcoming Rallies
No events scheduled in
the next 365 days.
» iRV2 on facebook

Our Communities

Our communities encompass many different hobbies and interests, but each one is built on friendly, intelligent membership.

» More about our Communities

Automotive Communities

Our Automotive communities encompass many different makes and models. From U.S. domestics to European Saloons.

» More about our Automotive Communities

RV & Travel Trailer Communities

Our RV & Travel Trailer sites encompasses virtually all types of Recreational Vehicles, from brand-specific to general RV communities.

» More about our RV Communities

Marine Communities

Our Marine websites focus on Cruising and Sailing Vessels, including forums and the largest cruising Wiki project on the web today.

» More about our Marine Communities


Copyright 2002-2012 Social Knowledge, LLC All Rights Reserved.
All times are GMT -6. The time now is 01:49 AM.