WRT the "propane-fired heater" situation...
If the gas-line (tubing) to your p-f-heater heater had been inactive for a long time (in storage, say), then you may be aware that the heater will try to ignite, but fail and will wait about 10 seconds and then try to ignite again, etc. etc. You can hear these "multiple ignition attempts" if you get your ear near the heater's location.
So my suggestion is to perform the following experiment:
Leave the genset off and turn the heater on. Do you hear these multiple ignition attempts?
Here's what I'm thinking:
Your p-f-heater fires up the gas (propane) via a high-voltage spark produced by an electronics pack. This "electronics pack" uses 12vdc (which BTW, might answer your question if there is a common "run capacitor" with this unit and your a/c unit....and the answer is "no"). If the input voltage to the heater (12vdc) is sagging (to say, 11vdc), the spark could be weak or non-existent. The electronics module will try the "multiple attempts" starting, but these attempts result in a failure to light the gas. No spark, no fire. After several attempts to ignite, the electronic module stops trying.
But....
When you start your genset, there is a charge being replaced into your house batteries, so your "sagging" 11vdc (at the heater) becomes a healthy 13vdc....and the heater's electronic module has no problem in creating the high-voltage spark. Hence: you get heat!!. As you stated, you now can turn-off the genset .... and the heater continues to work.
Suggest trying this "experiment" and let this forum know your findings.