Originally Posted by vito.a
If you have two Zone 1's then your dip switches have been incorrectly set somewhere along the line.
|
I don't think so in this case. Here is the 2007 Signature Owner Manual Description which should be the same as the OP:
Wall Thermostat
The living room Comfort Control operates the front roof air conditioner functions and the Aqua-Hot living room heat exchangers. The bedroom Comfort Control operates the rear roof air conditioner, mid-roof air conditioner and Aqua-Hot bathroom and bedroom heat exchangers.
The motorhome is divided into three operating zones: front, middle and rear. The selected Zone will flash. Control individual zone temperatures using the UP or DOWN buttons.
Living Room = Zone One
Hallway/Bathroom = Zone Two
Bedroom = Zone Three
NOTE:
The bedroom (Zone Three) will display as Zone One at the Bedroom Comfort
Control.
NOTE:
The Comfort Control must be ON to operate any HVAC function. DO NOT select conflicting modes of operation.
One zone cannot be on Cool while another zone is set to Furnace.
The Bedroom comfort control will operate rear roof air conditioner functions and the center roof air conditioner.
Press the MODE button repeatedly until Cool is displayed.
Press the ZONE button to alternate between Zone One and Zone Two.
Zone One controls the bedroom roof air conditioner and Zone Two controls the
center roof air conditioner.
The remote temperature sensor is connected to Zone 2 and is located in the center bath
Aux Heat Mode:
If the Heat Pump mode is selected at or below
30° F, or if operating in Heat Pump mode and
temperature drops to 30º F, the air conditioner
will stop Heat Pump operation and Aux Heat
will be displayed. The furnace will be selected
as the auxiliary heat source and will begin
operation. The furnace will remain the primary
heat source until ambient temperature rises
above 42º F.
When ambient temperature is between 30 and
42º F, a defrost cycle is initiated approximately
every 40 minutes of compressor operation. The
blower motor will stop for five minutes and
Defrost will be displayed. After the defrost cycle
the heat pump operation will resume.
NOTE:
The Aqua-Hot needs to be on for Aux
Heat to function. Turn on the Aqua-Hot
diesel burner or electric element. The
exchanger blowers automatically begin
operation in Auxiliary Heat mode.