Briefly, we have a 2008 Holiday Rambler Admiral with dual Brisk Air heat pumps and a gas furnace run through a SINGLE Duo-therm 5 button CCC 3109228.019. We were at a campground hooked to 30 amp service, we left for a few hours with only front A/C running and more than likely had several voltage drops from to many units, but upon our return the front A/C was not working. Service guy came and replaced fan motor and control box.
Since that time, HVAC will not cycle on and off properly.
FRONT UNIT: In A/C mode, unit will turn on when thermostat is turned below 70 deg, will run and cool properly BUT not turn off until you manually raise the CCC to 72 degrees, even when temperature setting has been reached or bypassed! Then unit shuts off almost immediately. In Heat mode, basically just the opposite happens, you must set the CCC to 72 or above to turn on, unit will run and heat normally, but never turn off until the setting on CCC is manually changed to 70 degrees, even if tempature reached 85 degrees! Same thing happens with furnace, with one exception…the furnace burner will cycle on and off, but fan will never stop until you manually reduce thermostat setting to 70 deg. Then fan runs in proper cool down mode for a minute or so and then shuts off.
REAR UNIT: The rear Heat and A/C operates semi-normally! By-the-way, it was turned off during the low voltage incident! The unit seems to function normally, except that it also has a “temperature number that it likes!” What I mean is, it will function in HEAT MODE if you set the thermostat to 73 degrees or warmer. It will run, heat and cut-off properly! BUT, if you set the CCC to 71 degrees, it will never turn on! ALSO, if the front HEAT is running and you then set the rear unit to run, it will not turn on until you raise the setting to 80 degrees or more!
Please understand that while I am not a HVAC person (although I have now learned way more than I ever cared to know!), I am a mechanical engineer. We have used temp probes to verify that requested temp is either less or more than ask for. Our rear remote sensor has always been about 2 degrees warmer than front.
This is a list of what has been tried:
Two new thermostats have been tried…with no change to problem!
12 DC current is correct to thermostat (12.50v) and CCC (11.41v)
Run capacitors exchanged, front to rear…no change to operation
Original control board was tried…functioned same as new one. Rear control board was moved to front unit…no correction to problem
Wiring traced…appears correct
Replacement fan is correct part number
Control boards are correct numbers 3109226.005
No shorts appear in 12 volt wiring to thermostat
CCC reset each time disconnected or dip switches changed
Did not replace start capacitor or PTCR…was not sure if they might affect fan operation
The initial service tech never came back. The local dealer where we were contacted Dometic and they said it was a CCC issue, hence first new CCC! We have since had to come to Texas and I contacted two local mobile repairmen and BOTH said it had to be thermostat, so I went to local dealer and talked to Service Manager. He confirmed it had to be thermostat! Hence second CCC. Needless to say, it don’t work!
Anyone have a fix? Suggestion?
Thanks!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! !!!!