You can manually select 30 Amps on your intellitic remote. Press the 20/30 amp button on the bottom of the panel. See if it remains on your selected input. You might still have a problem but by selecting 30 Amps your system should shed loads as needed. Once the generator kicks on it should go to 50 Amps. Maybe when the generator was turn on it caused a problem. I would unhook the shore power, start the generator; see if it shows 50 Amps. Let it run the A/C's for a few minutes then shut them down and turn off the generator. Wait 2 minutes, then plug into shore power again and see if it shows the correct amps.